Room Blower Hesitation

Post Reply
 
Dash_Martino
New Member
Posts: 1
Joined: Fri. Feb. 16, 2018 6:33 pm
Hot Air Coal Stoker Furnace: Koker Lite
Coal Size/Type: Anthracite Rice

Post by Dash_Martino » Fri. Feb. 16, 2018 6:38 pm

Hey all,
I've had my Keystoker Koker Lite for 1 year now. I've been noticing some hesitation with the room blower going to turn on. It sounds like the blower tries to turn on and stutters, then re-tries again. When I push the button for continuous, the blower runs. If I fiddle with the fan limit switch dial, the furnace seems to run normally for awhile, but then it goes back to the stuttering symptoms. Tried changing the filters on the blower to no avail. Any help is appreciated!

-John


 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Fri. Feb. 16, 2018 10:40 pm

It is most likely the fan switch electrical contacts doing that.

Since you can run it w/ over ride button the contacts may be dirty.

Only other thing is maybe your set points are too close together, but I doubt that it is possible to get them so close together to do what you describe.