Low draft at idle on keystoker 90-105

Post Reply
 
arcticcatmatt
Member
Posts: 320
Joined: Wed. Sep. 10, 2008 10:22 pm
Location: Montour Falls NY

Post by arcticcatmatt » Tue. Nov. 21, 2017 9:02 am

At full burn I am getting .03. At idle I'm getting .01. Manual says idle should be .02 and if draft is low, I close the circle metal piece on the combustion blower. Even if I close that all the way, draft doesn't move. If you close that all the way, no air is getting in to burn your coal. Stove is in basement, chimney goes up to roof of 1.5 story cape cod.


 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Tue. Nov. 21, 2017 10:15 am

Draft gets set at full burn only....idle is not to be counter adjusted away from your full burn draft setting.

Tightening up ALL stove body holes, replacing wore out gaskets, sealing hopper air cracks near stoker etc will make it run perfect as it possiblly can run.