Koker 160 Will Not Idle

 
User avatar
Cuzz01
Member
Posts: 29
Joined: Sun. Feb. 15, 2015 10:30 am
Location: NEPA
Hot Air Coal Stoker Furnace: Koker 160
Coal Size/Type: Anthracite Rice
Other Heating: Ele. HVAC

Post by Cuzz01 » Thu. Nov. 23, 2017 9:38 am

I'll take that back, Ventor and combustion B and W wires are tied together and run continuously. Gear motor runs when timer switches are activated. (R-W) wires. No connections with the limit switches except for a common. Wiring as per diagram and like I said it has opperated like that for 2 winters. BUT...

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Thu. Nov. 23, 2017 9:51 am

Cuzz01 wrote:
Thu. Nov. 23, 2017 9:38 am
I'll take that back, Ventor and combustion B and W wires are tied together and run continuously. Gear motor runs when timer switches are activated. (R-W) wires. No connections with the limit switches except for a common. Wiring as per diagram and like I said it has opperated like that for 2 winters. BUT...
I'll take a look at diagram in manual...sum ting wong???
Did you buy this Koker new?

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Thu. Nov. 23, 2017 2:11 pm

That is NOT matching the factory wiring...yes it worked for 2 winters...but, lucky you are both alive and still have a standing home. :hangover:

Better correct it ASAP.

Page 16 is wiring diagram:
Koker-Thermostat.pdf
.PDF | 1.4MB | Koker-Thermostat.pdf


 
User avatar
Cuzz01
Member
Posts: 29
Joined: Sun. Feb. 15, 2015 10:30 am
Location: NEPA
Hot Air Coal Stoker Furnace: Koker 160
Coal Size/Type: Anthracite Rice
Other Heating: Ele. HVAC

Post by Cuzz01 » Thu. Nov. 23, 2017 7:04 pm

Woah, Yes purchased new. My diagram is a bit different, diagram on pg. 21 on mine, also have a ventor on mine.

Following both diagrams, wiring is identical however your pictorial layout is different, but wires and colors match up as to where they are going.

My diagram is attached.

Attachments

Koker 160 with Thermostat 3-2015.jpg
.JPG | 277KB | Koker 160 with Thermostat 3-2015.jpg

 
User avatar
Cuzz01
Member
Posts: 29
Joined: Sun. Feb. 15, 2015 10:30 am
Location: NEPA
Hot Air Coal Stoker Furnace: Koker 160
Coal Size/Type: Anthracite Rice
Other Heating: Ele. HVAC

Post by Cuzz01 » Thu. Nov. 23, 2017 7:08 pm

BTW, I just installed a new thermostat and re-started. Burned hot for 1/2-45 min at 575 on front, convection cooled bonnet down. Convection turned off and bonnet now reads 225 and is going into idle mode. Will be watching it for some time!

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Thu. Nov. 23, 2017 10:18 pm

Direct vent is a different animal...wondered what the h3ll a "ventor" was.

I'm not your guy..."ventors" are not for your average coal burner.

Wish ya Luck :)


 
User avatar
WNY
Member
Posts: 6307
Joined: Mon. Nov. 14, 2005 8:40 am
Location: Cuba, NY
Hot Air Coal Stoker Stove: Keystoker 90K, Leisure Line Hyfire I
Coal Size/Type: Rice
Contact:

Post by WNY » Fri. Nov. 24, 2017 6:58 am

Thermostat is only for calling for heat. has nothing to do with idle mode. you can disconnect your thermostat and the stove should still continuously run on Idle if set correctly.

IDLE is control by your timer box and feed screw. once the thermostat is satisfied, the stoker turns off and it should only come on/off from the timer box and only feed where you pins are set.

 
User avatar
Cuzz01
Member
Posts: 29
Joined: Sun. Feb. 15, 2015 10:30 am
Location: NEPA
Hot Air Coal Stoker Furnace: Koker 160
Coal Size/Type: Anthracite Rice
Other Heating: Ele. HVAC

Post by Cuzz01 » Fri. Nov. 24, 2017 3:13 pm

UPDATE ***
My thanks to; Hyfire1, McGiever, Don and Brian @ Keystoker, Paul at Agel Coal (now using Reading coal-hard anthracite - HOT, dusty and ashy) for their time and patience...

I am at a point of sitting and waiting for a cold front to move in to see what the 160 will do. As of right now we are good, off to a 3rd. winter!

Tested; Thermostat and wire - Should the wire had become pinched or the relay in the thermostat stuck closed the gear motor would be on continuous run, relay in RA89A closes and opens with thermo, contacts clean. all good.

adjustments made; Fan limit - 100, 160, 220 - from 165,200,240
stoker screw - 6 turns CCW - from 4
Timer pins - 2 X 3 - from 4
Used; 10 self made "Rats"(definite fire starters, first time every time), #15 wasted coal, well maybe not!
Cuzz

Post Reply