Keystoker koker direct vent.

Post Reply
 
2004blackwrx
Member
Posts: 48
Joined: Tue. Apr. 29, 2014 7:39 pm
Hot Air Coal Stoker Furnace: Looking to buy one

Post by 2004blackwrx » Mon. Oct. 02, 2017 10:29 am

I HAVE THE KEYSTOKER KOKER DIRECT VENT. I Installed it 2 to 3 years ago and it has worked great. Based on what I read I used a stainless steel stove pipe. http://m.go2marine.com/controller?f=932 ... Stove+pipe
The link shows the pipe I used but after only a few seasons it looks like swiss cheese. I need recommendations for a quality pipe that will last or something dirt cheap i can easily replace each year. I prefer the quality long lasting option. I see some people use the duravent pellet pro vent but it doesnt appear to be rated for coal. Thanks

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Mon. Oct. 02, 2017 11:25 am

You need a very expensive stainless or take it apart and clean it when not in use. It will last forever as long as you're burning, when you shut it down, they start to rot.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Mon. Oct. 02, 2017 11:55 am

316T stainless should meet code, but will still erode. It will hold up better and erode more slowly than any other stainless that meets code. It must state 316T, and not merely 316 or 316_ (where _ is anything other than T).

 
gravely800
Member
Posts: 24
Joined: Thu. Aug. 13, 2015 2:29 pm
Location: south central pa
Hot Air Coal Stoker Stove: Keystoker 105

Post by gravely800 » Mon. Oct. 02, 2017 7:51 pm

Olympia Chimney Supply out of Scranton makes a Class A pipe with a lifetime warranty. They sell all kinds of pipe, I'm not sure if they have a product that will meet your needs. Check out their website and see what you can find. I don't think that they sell direct to the public.

Gravely


 
2004blackwrx
Member
Posts: 48
Joined: Tue. Apr. 29, 2014 7:39 pm
Hot Air Coal Stoker Furnace: Looking to buy one

Post by 2004blackwrx » Mon. Oct. 02, 2017 9:49 pm

lsayre wrote:
Mon. Oct. 02, 2017 11:55 am
316T stainless should meet code, but will still erode. It will hold up better and erode more slowly than any other stainless that meets code. It must state 316T, and not merely 316 or 316_ (where _ is anything other than T).
Is 316Ti the same as 316T

 
2004blackwrx
Member
Posts: 48
Joined: Tue. Apr. 29, 2014 7:39 pm
Hot Air Coal Stoker Furnace: Looking to buy one

Post by 2004blackwrx » Mon. Oct. 02, 2017 11:53 pm

any thoughts on something like this? https://www.firesidechimneysupply.com/f ... liner.html\

I am also reading nothing last with coal an may be cheaper to just get a disposable chimney system

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Tue. Oct. 03, 2017 6:20 am

As was already said above,
By just disconnecting, removing and storing in a dryer location during the off season will save one all this aggravation.and expense.Pay now or pay later, the choice is yours.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Tue. Oct. 03, 2017 10:58 am

2004blackwrx wrote:
Mon. Oct. 02, 2017 9:49 pm
Is 316Ti the same as 316T
Yes


 
claridon coal burner
Member
Posts: 34
Joined: Mon. Oct. 03, 2011 8:33 pm
Hot Air Coal Stoker Furnace: Keystoker Koker
Coal Size/Type: rice
Other Heating: oil

Post by claridon coal burner » Tue. Nov. 07, 2017 7:47 pm

My original exhaust pipe lasted 6 heating seasons (I would patch it up with silicone when I saw issues) ended up replacing the majority of it with sch. 10 stainless steel pipe, 304L I believe, I'm pretty sure it will outlast me.

 
kimberlyS
New Member
Posts: 7
Joined: Tue. Jan. 16, 2018 11:05 am
Hand Fed Coal Furnace: US Stove 1500 Series
Other Heating: Heat pump

Post by kimberlyS » Wed. Jan. 24, 2018 2:09 pm

I am torn between a direct vent or chimney vent Keystoker warm air furnace. Since the we will put the furnace in the storage room in the basement are away from chimney, I think the only option we have is the direct vent one. If venting through the chimney, we would need to run the pipe above the basement ceiling, and drill a hole through the brick wall of the chimney, which I am not sure if this can be done. The direct vent furnace is selling at $6,800 for a 120,000 BTU installed, the chimney vent is significant cheaper.

I am not sure what are the pros and cons of the 2 venting options. Any advice would be greatly appreciated. Thank you!!

 
titleist1
Member
Posts: 5226
Joined: Wed. Nov. 14, 2007 4:06 pm

Post by titleist1 » Wed. Jan. 24, 2018 2:28 pm

Chimney, Chimney, Chimney!! :D

Look at any and all ways of possibly using a chimney for your install, either an existing chimney or new. I do not recommend a long run of pipe from the stoker to the chimney. You will need access to any horizontal runs to inspect/clean out the fly ash probably more than once per heating season.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Wed. Jan. 24, 2018 6:05 pm

The bitterness of a having a Direct Vent/Power Vent remains long after the sweet taste of low price is forgotten.

Why pay forever for electric blower 24/7, when hot air already rises forever for FREE.
Need I mention mechanical things running 24/7 in a hot dirty environment have a very short trouble free lifetime. 8-)

 
User avatar
swyman
Member
Posts: 2355
Joined: Mon. Apr. 13, 2015 9:50 pm
Location: Blissfield, MI
Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
Coal Size/Type: Lehigh Pea

Post by swyman » Thu. Jan. 25, 2018 10:21 am

McGiever wrote:
Wed. Jan. 24, 2018 6:05 pm
The bitterness of a having a Direct Vent/Power Vent remains long after the sweet taste of low price is forgotten.

Why pay forever for electric blower 24/7, when hot air already rises forever for FREE.
Need I mention mechanical things running 24/7 in a hot dirty environment have a very short trouble free lifetime. 8-)
They are pretty noisy also if installed in a house..... mine is anyway. I am looking to install a chimney in the off season for all the above stated reasons.