Leisure Line Econo With Powervent Question

Post Reply
 
User avatar
ElCamMan515
Member
Posts: 306
Joined: Sat. May. 17, 2014 9:48 am
Location: North Norwich, NY
Hot Air Coal Stoker Furnace: Keystoker K-Lite
Hand Fed Coal Stove: Surdiac Gotha 513
Coal Size/Type: Rice and Pea Anthracite

Post by ElCamMan515 » Sat. Feb. 11, 2017 9:13 pm

Good evening all,

My brother in law just picked up an older LL Econo with a powervent. My questions are does he need to have a barometric damper with the powervent and can we run the stove pipe right out the back of stove into powervent.

Tim

 
User avatar
ElCamMan515
Member
Posts: 306
Joined: Sat. May. 17, 2014 9:48 am
Location: North Norwich, NY
Hot Air Coal Stoker Furnace: Keystoker K-Lite
Hand Fed Coal Stove: Surdiac Gotha 513
Coal Size/Type: Rice and Pea Anthracite

Post by ElCamMan515 » Sun. Feb. 12, 2017 7:37 am

Any suggestions on powervent install? This stove was bought used with no paperwork. I have no idea how to hook up powervent. Would like to just run rear vent on stove to powervent with horizontal piece of stove pipe.

Thanks everyone

Tim

 
User avatar
philthy
Member
Posts: 163
Joined: Sat. Nov. 09, 2013 9:15 pm
Location: Newville PA
Hot Air Coal Stoker Stove: Keystoke Koker Lite, Alaska Kast Konsole
Baseburners & Antiques: Glenwood #6, Glenwood #116 x 2, Crawford 40

Post by philthy » Sun. Feb. 12, 2017 8:34 am

I would recommend the baro. A powervent is a consistent draw that is adjusted with a rheostat or similar device if yours came with one. With that being said, changes in operating temp of the stove or wind gust across the face of the powervent will affect the draft. The baro helps control this in my opinion. I've found with the powervent that a mano is crucial to set the correct draft for your stove. In my particular situation my powervent draws very little.

As far as install, what you are suggesting should be fine. Powervent goes thru the wall and then just pipe the stove into it.

 
User avatar
ElCamMan515
Member
Posts: 306
Joined: Sat. May. 17, 2014 9:48 am
Location: North Norwich, NY
Hot Air Coal Stoker Furnace: Keystoker K-Lite
Hand Fed Coal Stove: Surdiac Gotha 513
Coal Size/Type: Rice and Pea Anthracite

Post by ElCamMan515 » Sun. Feb. 12, 2017 8:45 am

Thanks philthy.

I hope to install it today for my brother in law.

Tin

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sun. Feb. 12, 2017 9:01 am

First things first...Carbon Monoxide detectors to protect loved ones and pets.

Don't forget to install and wire-in the separate 'fume switch' to stop/shut-down the pv if it were blocked, failed or of reduced capacity. :idea:


 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Sun. Feb. 12, 2017 9:08 am

You will need a draft gauge or manometer to set the baro damper properly. If you don't use one, you could be wasting a lot of heat to the outside or have operational problems with the stove. Draft is the critical component to safe and efficient operation.

 
User avatar
coalvet
Member
Posts: 254
Joined: Tue. Feb. 27, 2007 12:48 pm
Location: Rhode Island
Hand Fed Coal Stove: Crane Model 404, Harman MK I
Coal Size/Type: Nut
Other Heating: NG Boiler

Post by coalvet » Sun. Feb. 12, 2017 9:24 am

Here are the instructions from LL.

Attachments

Power Vent Instructions.pdf
.PDF | 2.9MB | Power Vent Instructions.pdf

 
User avatar
philthy
Member
Posts: 163
Joined: Sat. Nov. 09, 2013 9:15 pm
Location: Newville PA
Hot Air Coal Stoker Stove: Keystoke Koker Lite, Alaska Kast Konsole
Baseburners & Antiques: Glenwood #6, Glenwood #116 x 2, Crawford 40

Post by philthy » Sun. Feb. 12, 2017 9:32 am

McGiever wrote:First things first...Carbon Monoxide detectors to protect loved ones and pets.

Don't forget to install and wire-in the separate 'fume switch' to stop/shut-down the pv if it were blocked, failed or of reduced capacity. :idea:
This is a big one! Look on the inside where the fume switch comes into the stove body. Make sure it isn't plugged up with gunk. I've had this issue before and didn't know it.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sun. Feb. 12, 2017 2:25 pm

From the archives>>>>>>>>> Fume Switch

 
User avatar
ElCamMan515
Member
Posts: 306
Joined: Sat. May. 17, 2014 9:48 am
Location: North Norwich, NY
Hot Air Coal Stoker Furnace: Keystoker K-Lite
Hand Fed Coal Stove: Surdiac Gotha 513
Coal Size/Type: Rice and Pea Anthracite

Post by ElCamMan515 » Sun. Feb. 12, 2017 7:17 pm

Thank you all for your help. Stove wasn't installed today as we noticed the grate wasn't sealed. Hope to have it up and running by the weekend.

Tin


 
User avatar
ElCamMan515
Member
Posts: 306
Joined: Sat. May. 17, 2014 9:48 am
Location: North Norwich, NY
Hot Air Coal Stoker Furnace: Keystoker K-Lite
Hand Fed Coal Stove: Surdiac Gotha 513
Coal Size/Type: Rice and Pea Anthracite

Post by ElCamMan515 » Thu. Mar. 02, 2017 10:06 pm

Good evening all,

With a cold snap coming this weekend and my brother in law hating paying for pro-pain to heat his 1500 Sq ft house, I finally finished his Econo install and fired it up tonight. In 1 hour living room went from 66 to 71. Very impressed with this little stove. I didn't get any pics as it was late when I left. Converted another to coal.

Tim

 
titleist1
Member
Posts: 5226
Joined: Wed. Nov. 14, 2007 4:06 pm

Post by titleist1 » Fri. Mar. 03, 2017 11:21 am

Good Job spreading the love of black rocks!!! :clap:

 
User avatar
Flyer5
Member
Posts: 10376
Joined: Sun. Oct. 21, 2007 4:23 pm
Location: Montrose PA
Stoker Coal Boiler: Leisure Line WL110
Hot Air Coal Stoker Stove: Leisure Line Pioneer
Contact:

Post by Flyer5 » Sat. Mar. 04, 2017 6:48 am

If you do not use a Baro that is properly adjusted when running a PV you could end up with a hopper fire as well. The other hint for the econo when lighting plug the hopper fan in direct for the first hr so it runs full speed till the stove levels out.

 
User avatar
ElCamMan515
Member
Posts: 306
Joined: Sat. May. 17, 2014 9:48 am
Location: North Norwich, NY
Hot Air Coal Stoker Furnace: Keystoker K-Lite
Hand Fed Coal Stove: Surdiac Gotha 513
Coal Size/Type: Rice and Pea Anthracite

Post by ElCamMan515 » Sat. Mar. 04, 2017 7:43 am

Hello all,

We installed a barometric damper and got it set to where draft is -.04. Stove has been running good. Brother in law and his family are very happy coal burners.

Tim