Combustion Air Covers

A Coal stoker furnace or stove controls most operations including automatically feeding the coal. They are quite similar to any conventional oil and gas units and easily operated for extended periods of time. They commonly use rice coal but may use larger sizes like buckwheat. They can be used as primary heat, supplementary heat or have a dual set up with your existing oil/gas furnace.
ssmilloy36
New Member
Posts: 12
Joined: Tue. Jan. 10, 2017 8:04 pm
Hot Air Coal Stoker Furnace: ak 220
Coal Size/Type: rice

Post Tue. Jan. 10, 2017 8:18 pm

It's my third year with the ak 220 (only use one side) and I just realized there is an adjustable air intake cover. After searching I've found nothing, maybe I don't know what I am searching for.

Is it ok to open shield all the way. It clearly increases flame. This year I'm having a hard time reaching set temp. Its 20 outside and I set indoors to 68. I'm at 62 and not rising F99. I've adjusted max and still not getting anything. Im assuming the combustion air increase will be the answer.

Any advice?


User avatar
CoalisCoolxWarm
Member
Posts: 1401
Joined: Wed. Jan. 19, 2011 11:41 am
Stoker Coal Boiler: Keystoker KA-6
Hand Fed Coal Furnace: old Sears rebuilt, bituminous- offline as of winter 2014
Coal Size/Type: Anthracite Buckwheat
Other Heating: Oil Boiler
Location: Western PA

Post Tue. Jan. 10, 2017 9:15 pm

What is your draft reading (do you have a manometer)?
Keystoker KA-6 online January 2015

ssmilloy36
New Member
Posts: 12
Joined: Tue. Jan. 10, 2017 8:04 pm
Hot Air Coal Stoker Furnace: ak 220
Coal Size/Type: rice

Post Wed. Jan. 11, 2017 6:54 am

no I do not. professional used my old oil furnace one. that furnace is still connected and used in the warmer days.
I went through 4.5 tons last year and we all know that was a warm winter. it doesn't seem right. currently 3 bags a day and always have pebbles in the bucket never hot ones though. @f99 I am one inch from end.
not sure where metal shield was I kinda felt in the dark. got overly warm by morning. worried about too big a flame

ssmilloy36
New Member
Posts: 12
Joined: Tue. Jan. 10, 2017 8:04 pm
Hot Air Coal Stoker Furnace: ak 220
Coal Size/Type: rice

Post Wed. Jan. 11, 2017 6:59 am

let's say I get a manometer and research how to use one. this blow dryer looking combustion fan would adjust the flu's draft?

User avatar
McGiever
Member
Posts: 5997
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Coal Size/Type: PEA / ANTHRACITE
Other Heating: Ground Source Heat Pump
Stove/Furnace Make: Hydro Heat /Mega Tek
Location: Junction of PA-OH-WV

Post Wed. Jan. 11, 2017 7:04 am

yes, but using only 1 of 2 burners makes it tricky.
SLOW AND STEADY WINS THE RACE

ssmilloy36
New Member
Posts: 12
Joined: Tue. Jan. 10, 2017 8:04 pm
Hot Air Coal Stoker Furnace: ak 220
Coal Size/Type: rice

Post Wed. Jan. 11, 2017 7:53 am


User avatar
titleist1
Member
Posts: 4404
Joined: Wed. Nov. 14, 2007 4:06 pm
Hot Air Coal Stoker Stove: Harman Mag Stoker (old style) one in basement, one in workshop
Hand Fed Coal Stove: Harman Mark III on standby for long power outages
Coal Size/Type: Rice/Anthracite; Nut/Anthracite
Location: Cecil County, MD

Post Wed. Jan. 11, 2017 8:12 am

You need something that can accurately measure 0 - 0.1" h2O that is the range you will be running. These two are widely used here.

https://www.amazon.com/Dwyer-25-Manometer-Inclined-Vertical- ... i+model+25

or this

https://www.amazon.com/Dwyer-Magnehelic-Differential-Pressur ... elic+gauge
I drive a VW TDI, heat my home & workshop with two coal stokers and have two vintage JD diesel tractors....
The EPA just loves me!!

User avatar
Rob R.
Site Moderator
Posts: 11343
Joined: Fri. Dec. 28, 2007 4:26 pm
Stoker Coal Boiler: EFM DF520
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Lehigh Rice
Other Heating: Dad's 1953 EFM Highboy
Location: Chazy, NY

Post Wed. Jan. 11, 2017 9:02 am

If you can't heat the house properly, why are you only using one stoker? I can't imagine that makes good use of the heat exchanger...Plus it may be sucking air through the unused stoker.

Light the 2nd stoker, set the max feed to whatever LL recommends, and adjust the air so you get a full stoker of fire. The burning coal should be blturner to ash just before the last set of air holes on the grate.

Excess combustion air reduces efficiency.


ssmilloy36
New Member
Posts: 12
Joined: Tue. Jan. 10, 2017 8:04 pm
Hot Air Coal Stoker Furnace: ak 220
Coal Size/Type: rice

Post Wed. Jan. 11, 2017 9:43 am

second burner for 5000 sq ft house. I have 1800 but got the ak 220 cheaper than a 110.
had no issue last year getting set point temp. think while cleaning might have bumped the cover. just figured wasting coal burning two and when parts go in the future bad I'll then use side two.

User avatar
McGiever
Member
Posts: 5997
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Coal Size/Type: PEA / ANTHRACITE
Other Heating: Ground Source Heat Pump
Stove/Furnace Make: Hydro Heat /Mega Tek
Location: Junction of PA-OH-WV

Post Wed. Jan. 11, 2017 10:07 am

Enjoy your saved money getting more than twice what you needed. :)

No sense arguing w/ success. 8-)
SLOW AND STEADY WINS THE RACE

ssmilloy36
New Member
Posts: 12
Joined: Tue. Jan. 10, 2017 8:04 pm
Hot Air Coal Stoker Furnace: ak 220
Coal Size/Type: rice

Post Wed. Jan. 11, 2017 10:21 am

but this is a clear air issue. if my air is wrong and I enable side two my air is still wrong. next day airing the meter. thanks for the quick replies!

not sure if it's coming with detailed instructions. what should my meter read? do I put it before or after the barometer in the flue? isn't outside temp a major factor in the reading?

User avatar
titleist1
Member
Posts: 4404
Joined: Wed. Nov. 14, 2007 4:06 pm
Hot Air Coal Stoker Stove: Harman Mag Stoker (old style) one in basement, one in workshop
Hand Fed Coal Stove: Harman Mark III on standby for long power outages
Coal Size/Type: Rice/Anthracite; Nut/Anthracite
Location: Cecil County, MD

Post Wed. Jan. 11, 2017 10:43 am

You should get readings on the manometer from two places to compare, one in the firebox itself and one in the flue pipe before the baro. Do you have a chimney or direct / power vent?

If you don't have a chimney there will be instructions in the manual for setting the direct / power vent up based on the measured draft.

LL manuals have the recommended draft numbers but should be in the ballpark of 0.02 over fire and 0.05 in the flue pipe....check the manual or call LL for the exact numbers.

Adjusting the amount of fan intake the baffle plate covers is part of setting up and the manometer gives you the actual numbers to do it accurately.

Do you have a couple CO monitors?

forgot to ask, which mano did you get?
Last edited by titleist1 on Wed. Jan. 11, 2017 10:54 am, edited 1 time in total.
I drive a VW TDI, heat my home & workshop with two coal stokers and have two vintage JD diesel tractors....
The EPA just loves me!!

Olllotj
Member
Posts: 410
Joined: Thu. Sep. 04, 2014 10:01 am
Stoker Coal Boiler: Keystoker KB-8
Coal Size/Type: Buckwheat
Other Heating: Utica Propane Hot Water Baseboard
Location: Western NY

Post Wed. Jan. 11, 2017 10:50 am

I don't see how having both burners lit would a sacrifice in efficiency?

Wouldn't the burners just have shorter cycles?

I hope you're making your domestic hot water with that bad boy as well.

It may be because I don't have one and have never used one, but It seems like the coal trol really complicates everything.

ssmilloy36
New Member
Posts: 12
Joined: Tue. Jan. 10, 2017 8:04 pm
Hot Air Coal Stoker Furnace: ak 220
Coal Size/Type: rice

Post Wed. Jan. 11, 2017 11:24 am

yes I have two different brand co monitors. I have a chimney. how would you use in fire box. I'm gathering you drill holes in flue so again how check fire box

got the dwyer mano

User avatar
titleist1
Member
Posts: 4404
Joined: Wed. Nov. 14, 2007 4:06 pm
Hot Air Coal Stoker Stove: Harman Mag Stoker (old style) one in basement, one in workshop
Hand Fed Coal Stove: Harman Mark III on standby for long power outages
Coal Size/Type: Rice/Anthracite; Nut/Anthracite
Location: Cecil County, MD

Post Wed. Jan. 11, 2017 11:53 am

From Page 10 of the manual found on their website.....

All stoves must utilize a Barometric Draft Control such as the Field Controls Type RC Barometric Damper, the weights should be adjusted to obtain a -.03” to -.05” water column negative pressure in the flue pipe at the stove outlet. Draft should be checked using a draft meter or manometer. Over fire pressure can be checked by drilling a small ¼” hole in front of furnace usually below the top door and just above the bottom door. It should be -.02 to -.03 water column no lower than -.01. Combustion air is pre-determined by blower size and should be correct from the factory, if it is necessary combustion air can be reduced by adjusting the block off plate covering part of the intake side of the combustion blower. Caution!! Do not increase blower size for increased firing for any reason

Near the stove I used copper tubing left over from a refrigerator water line, others use brake line to handle the temps. Then you transition to the tubing that comes with the manometer. After the initial set up mine stays in the flue pipe all the time. I can tell when to cover my baro in the warmer weather by watching the manometer.
I drive a VW TDI, heat my home & workshop with two coal stokers and have two vintage JD diesel tractors....
The EPA just loves me!!