Great Fire, No Heat!

A Coal stoker furnace or stove controls most operations including automatically feeding the coal. They are quite similar to any conventional oil and gas units and easily operated for extended periods of time. They commonly use rice coal but may use larger sizes like buckwheat. They can be used as primary heat, supplementary heat or have a dual set up with your existing oil/gas furnace.
coalmark
New Member
Posts: 17
Joined: Tue. Feb. 05, 2008 8:18 pm
Stove/Furnace Make: Newmac

Post Tue. Feb. 12, 2008 9:28 pm

I think I need someone familiar with both coal and HVAC for some advice. I finally seem to have a good fire going, nice orange glow and abundant blue flame. My house is still cold. I have a Newmac combination furnace. It burns oil, wood or coal. I have it set up for coal, shaker grates and cast iron liner plates. It has a thermostatically controlled fan whose flow can be restricted with a sliding gate, as well as a manual damper in the ash door for use in case of power failure. Currently I am running it with the fan partially (about 50%) open and the manual damper fully closed. The stove pipe going to the chimney is very hot to the touch, the plenum is not, very warm at best. I am experimenting with different combinations of opening for the fan and manual damper in the ash door. Any suggestions or advice would be greatly appreciated.

I am not experiencing these problems when burning oil.


User avatar
Flyer5
Verified Business Rep.
Posts: 10382
Joined: Sun. Oct. 21, 2007 4:23 pm
Stoker Coal Boiler: Leisure Line WL110
Hot Air Coal Stoker Stove: Leisure Line Pioneer
Location: Montrose PA
Contact:

Post Tue. Feb. 12, 2008 9:34 pm

coalmark wrote:I think I need someone familiar with both coal and HVAC for some advice. I finally seem to have a good fire going, nice orange glow and abundant blue flame. My house is still cold. I have a Newmac combination furnace. It burns oil, wood or coal. I have it set up for coal, shaker grates and cast iron liner plates. It has a thermostatically controlled fan whose flow can be restricted with a sliding gate, as well as a manual damper in the ash door for use in case of power failure. Currently I am running it with the fan partially (about 50%) open and the manual damper fully closed. The stove pipe going to the chimney is very hot to the touch, the plenum is not, very warm at best. I am experimenting with different combinations of opening for the fan and manual damper in the ash door. Any suggestions or advice would be greatly appreciated.

I am not experiencing these problems when burning oil.
Do you have a barometric damper installed . With the oil the flame shooting into the end of the furnace causes a better transfer of heat . Where as the coal heat is just being carried out the pipe ,
http://www.leisurelinestove.com


You know when people say it was "better back in my day"?

They were right.

User avatar
coaledsweat
Site Moderator
Posts: 9826
Joined: Fri. Oct. 27, 2006 2:05 pm
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea
Location: Guilford, Connecticut

Post Tue. Feb. 12, 2008 9:55 pm

Your going to need a baro, your heat is going up the chimney. Another thing is to make sure your firebox is completely full of coal, right to the top.
Nothing is impossible for people who don't have to do it themselves.

coalmark
New Member
Posts: 17
Joined: Tue. Feb. 05, 2008 8:18 pm
Stove/Furnace Make: Newmac

Post Tue. Feb. 12, 2008 9:57 pm

Baro?

User avatar
coaledsweat
Site Moderator
Posts: 9826
Joined: Fri. Oct. 27, 2006 2:05 pm
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea
Location: Guilford, Connecticut

Post Tue. Feb. 12, 2008 10:01 pm

coalmark wrote:Baro?
http://www.fieldcontrols.com/draftcontrol.php#draftwork

Poke around there, it will describe how it works and why. Most of us here run an R/C model from Field Controls. A barometric damper is pretty much required on most installs.
Nothing is impossible for people who don't have to do it themselves.

coalmark
New Member
Posts: 17
Joined: Tue. Feb. 05, 2008 8:18 pm
Stove/Furnace Make: Newmac

Post Tue. Feb. 12, 2008 10:05 pm

Got one

User avatar
coaledsweat
Site Moderator
Posts: 9826
Joined: Fri. Oct. 27, 2006 2:05 pm
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea
Location: Guilford, Connecticut

Post Tue. Feb. 12, 2008 10:35 pm

Was it tuned with a manometer? Does it move freely? Crack the baro flapper about half way with a chunk of coal, within a few minutes, does the stovepipe cool and the heat exchanger warm up?

Have you burned wood? The back of the baro could be coated with creosote and not in proper tune (out of balance).

Firebox full?
Last edited by coaledsweat on Tue. Feb. 12, 2008 11:01 pm, edited 1 time in total.
Nothing is impossible for people who don't have to do it themselves.

GreenAcres
New Member
Posts: 4
Joined: Mon. Feb. 11, 2008 8:59 pm
Stove/Furnace Make: Alaska Channing III

Post Tue. Feb. 12, 2008 10:43 pm

Coal stoves are pretty simple, but they've been engineered and tested for efficient operation. Different fuels behave differently and furnaces are designed with specific chamber size and shape to get the most out of the a specific fuel it's burning. I'm skeptical of multi fuel units. They may work fine with one fuel and less efficiently with another's. It's a trade off for versatility. My coal stoves surface will boil water, but you can rest your hand on the vent pipe. The one reply I read may have something about having enough coal on the grates. Oil and wood burns fast and the hot gases expand so quickly that it can't escape through the vent easily as slow burning goal. Adding more coal could increase the hot gases and slow down the escape through the vent.

If you're thinking about restricting the vent, be sure your CO alarm is operational.


coalmark
New Member
Posts: 17
Joined: Tue. Feb. 05, 2008 8:18 pm
Stove/Furnace Make: Newmac

Post Tue. Feb. 12, 2008 11:29 pm

coaledsweat wrote:Was it tuned with a manometer? Does it move freely? Crack the baro flapper about half way with a chunk of coal, within a few minutes, does the stovepipe cool and the heat exchanger warm up?

Have you burned wood? The back of the baro could be coated with creosote and not in proper tune (out of balance).

Firebox full?
Yes it has been tuned, the damper door moves freely, no creosote. By heat exchanger, you mean in the furnace itself? I will check the plenum. The coal box has been fairly full for the last three days. Thanks for all the input I will look into these and post soon

User avatar
beatle78
Member
Posts: 1026
Joined: Wed. Oct. 03, 2007 1:46 pm
Stove/Furnace Make: Keystoker KA-4
Location: Rhode Island

Post Wed. Feb. 13, 2008 4:48 pm

coalmark wrote:
coaledsweat wrote:Was it tuned with a manometer? Does it move freely? Crack the baro flapper about half way with a chunk of coal, within a few minutes, does the stovepipe cool and the heat exchanger warm up?

Have you burned wood? The back of the baro could be coated with creosote and not in proper tune (out of balance).

Firebox full?
Yes it has been tuned, the damper door moves freely, no creosote. By heat exchanger, you mean in the furnace itself? I will check the plenum. The coal box has been fairly full for the last three days. Thanks for all the input I will look into these and post soon
correct me if I'm wrong, but with a properly tuned baro, the stove pipe after the baro should be cool enough to put your hand on for a second or 2 (the not so scientific expression). Not sure was the actual stack temp should be.

User avatar
WNY
Member
Posts: 5849
Joined: Mon. Nov. 14, 2005 8:40 am
Hot Air Coal Stoker Stove: Keystoker 90K, Leisure Line Hyfire I
Coal Size/Type: Rice
Stove/Furnace Make: Keystoker, LL & CoalTrol
Stove/Furnace Model: 90K, Hyfire I, VF3000 Soon
Location: Cuba, NY
Contact:

Post Wed. Feb. 13, 2008 6:05 pm

It depends on how hot the stove is running, the baro will cool the downstrem part of the pipe quite a bit, maybe 50-150 degrees. My exhaust temp just before going into the chimney about 6 feet of pipe after the baro runs 160-250 degrees depends on how hot the fire is burning. It averages around 200 degrees most of the time. That is measuring INSIDE the pipe with a digital thermometer and probe.
- Dave
Hyfire I & Keystoker 90K heating an 1890 Victorian
- Amsoil Authorized T1 Certified Dealer

User avatar
coalstoves
Member
Posts: 399
Joined: Fri. Feb. 23, 2007 7:37 pm
Stove/Furnace Make: Harman and Liberty
Stove/Furnace Model: Magnum and Victory 700
Location: Mt.Carmel Pa. Located on The Western Middle Anthracite Field

Post Wed. Feb. 13, 2008 8:06 pm

beatle78 wrote:
correct me if I'm wrong, but with a properly tuned baro, the stove pipe after the baro should be cool enough to put your hand on for a second or 2 (the not so scientific expression)

I like it like that before the Baro and even a little cooler after it, remember the baro does not just cool the exhaust gas but rather the big hole in the chimney reduces draft overall to slow the draw

. Not sure was the actual stack temp should be.
"No Fuel Like An Old Fuel"

User avatar
North Candlewood
Member
Posts: 239
Joined: Sun. Dec. 09, 2007 9:00 pm
Stoker Coal Boiler: Eshland S-130
Hot Air Coal Stoker Furnace: Keystoker A 120
Hand Fed Coal Stove: Chubby
Hand Fed Coal Furnace: Clayton 1602
Baseburners & Antiques: Princess Atlantic Cookstove
Coal Size/Type: Nut Rice
Location: Ct

Post Wed. Feb. 13, 2008 8:21 pm

Question is was the baro setup for the oil end of this unit or coal. Most oil setups are not done as accurate as we coal burners need.

coalmark
New Member
Posts: 17
Joined: Tue. Feb. 05, 2008 8:18 pm
Stove/Furnace Make: Newmac

Post Wed. Feb. 13, 2008 9:27 pm

Damper is tuned for oil. My heating guy told me the fire was not high enough. I loaded the stove to just shy of the very top of the firebox. House is 70 degrees, fire is burning great and the wife is warm and happy. So far so good.

User avatar
coalstoves
Member
Posts: 399
Joined: Fri. Feb. 23, 2007 7:37 pm
Stove/Furnace Make: Harman and Liberty
Stove/Furnace Model: Magnum and Victory 700
Location: Mt.Carmel Pa. Located on The Western Middle Anthracite Field

Post Wed. Feb. 13, 2008 10:27 pm

North Candlewood wrote:Most oil setups are not done as accurate as we coal burners need.

Okay :dancing:
"No Fuel Like An Old Fuel"


Post Reply