Might as well bite the bullet and replace the entire length. You can probably hire a backhoe pretty cheap this time of year.
- SWPaDon
- Member
- Posts: 9857
- Joined: Sun. Nov. 24, 2013 12:05 pm
- Location: Southwest Pa.
- Hand Fed Coal Furnace: Clayton 1600M
- Coal Size/Type: Bituminous
- Other Heating: Oil furnace
Maybe I'm off base here, but, if the Pex is already inside the black sewer pipe, can't you just slide new Pex thru the sewer pipe?
-
- Member
- Posts: 180
- Joined: Sun. Oct. 26, 2008 5:19 pm
- Location: catskills, New York State
- Stoker Coal Boiler: KA6 Keystoker
- Hand Fed Coal Stove: Harmon TLC 2000
- Coal Size/Type: Rice, Nut
- Other Heating: oil
they are kinda tied together and the sewer pipe crushes from being buries so I don't think it will pull through but If it did it would be a nice solutionSWPaDon wrote:Maybe I'm off base here, but, if the Pex is already inside the black sewer pipe, can't you just slide new Pex thru the sewer pipe?
- Lightning
- Site Moderator
- Posts: 14669
- Joined: Wed. Nov. 16, 2011 9:51 am
- Location: Olean, NY
- Stoker Coal Boiler: Modified AA 130
- Coal Size/Type: Pea Size - Anthracite
"kinda tied" doesn't compute.. Can you slide it thru? Why not just try it...GaryFerg wrote:they are kinda tied together and the sewer pipe crushes from being buries so I don't think it will pull through but If it did it would be a nice solution
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
I did something similar once...this did the trick for me...
Splice new onto old w/ apiece of solid rod push half inside both tubes (internal splice coupling) drill 2 holes, 1 thru both halves and tap shear pin in drilled holes. (need not be brass) And file or grind flush.
Lube it up w/ some cable pulling lube and tug/winch her in...lubeing it the whole time while it's being tugged is highly advised.
Yeah, what do you have to lose?
Splice new onto old w/ apiece of solid rod push half inside both tubes (internal splice coupling) drill 2 holes, 1 thru both halves and tap shear pin in drilled holes. (need not be brass) And file or grind flush.
Lube it up w/ some cable pulling lube and tug/winch her in...lubeing it the whole time while it's being tugged is highly advised.
Yeah, what do you have to lose?
-
- Member
- Posts: 286
- Joined: Wed. Jan. 29, 2014 1:42 pm
- Location: N/W Pa. Meadville, Pa.
- Hand Fed Coal Stove: Sears circulator air tight stove.
- Other Heating: Crown 115,000 BTU oil fired boiler(house) Weil Mclain 150,000BTU oil fired boiler(Shop)
Another thing to add to the the system is a low boiler water cut-off switch.
Low Water Cutoff Switch (Low Voltage)
http://www.pexsupply.com/Taco-LTA0243S-2-Electron ... 7AodJkcA2g
Low Water Cutoff Switch (120VAC)
http://www.pexsupply.com/Taco-LTA1203S-2-Electron ... -Off-Water
You can add the 120VAC switch into the stoker system to shut off the stoker if the water level drops to a certain point.
The switch can be installed in the supply side piping 12" above the boiler jacket.
It will open and shut the system down to prevent the stoker from feeding once the water level reaches that point.
If you wire it to the stoker, I would run the stoker through a relay to keep the electrical load down on the switch itself.
I have one on my oil boiler for the shop, as it runs in a room outside the main shop. I had it active once when the Pressure Relief tripped and drained my feed tank. and system.
It saved the boiler from boiling out.
If I remember the wiring right a beacon can be added to notify you that the boiler is down.
Dan.
Low Water Cutoff Switch (Low Voltage)
http://www.pexsupply.com/Taco-LTA0243S-2-Electron ... 7AodJkcA2g
Low Water Cutoff Switch (120VAC)
http://www.pexsupply.com/Taco-LTA1203S-2-Electron ... -Off-Water
You can add the 120VAC switch into the stoker system to shut off the stoker if the water level drops to a certain point.
The switch can be installed in the supply side piping 12" above the boiler jacket.
It will open and shut the system down to prevent the stoker from feeding once the water level reaches that point.
If you wire it to the stoker, I would run the stoker through a relay to keep the electrical load down on the switch itself.
I have one on my oil boiler for the shop, as it runs in a room outside the main shop. I had it active once when the Pressure Relief tripped and drained my feed tank. and system.
It saved the boiler from boiling out.
If I remember the wiring right a beacon can be added to notify you that the boiler is down.
Dan.
-
- Member
- Posts: 180
- Joined: Sun. Oct. 26, 2008 5:19 pm
- Location: catskills, New York State
- Stoker Coal Boiler: KA6 Keystoker
- Hand Fed Coal Stove: Harmon TLC 2000
- Coal Size/Type: Rice, Nut
- Other Heating: oil
while in place?McGiever wrote:I did something similar once...this did the trick for me...
Splice new onto old w/ apiece of solid rod push half inside both tubes (internal splice coupling) drill 2 holes, 1 thru both halves and tap shear pin in drilled holes. (need not be brass) And file or grind flush.
Lube it up w/ some cable pulling lube and tug/winch her in...lubeing it the whole time while it's being tugged is highly advised.
Yeah, what do you have to lose?
-
- Member
- Posts: 180
- Joined: Sun. Oct. 26, 2008 5:19 pm
- Location: catskills, New York State
- Stoker Coal Boiler: KA6 Keystoker
- Hand Fed Coal Stove: Harmon TLC 2000
- Coal Size/Type: Rice, Nut
- Other Heating: oil
its a hand feed boiler don't see how that would help other then the warning lightLu47Dan wrote:Another thing to add to the the system is a low boiler water cut-off switch.
Low Water Cutoff Switch (Low Voltage)
http://www.pexsupply.com/Taco-LTA0243S-2-Electron ... 7AodJkcA2g
Low Water Cutoff Switch (120VAC)
http://www.pexsupply.com/Taco-LTA1203S-2-Electron ... -Off-Water
You can add the 120VAC switch into the stoker system to shut off the stoker if the water level drops to a certain point.
The switch can be installed in the supply side piping 12" above the boiler jacket.
It will open and shut the system down to prevent the stoker from feeding once the water level reaches that point.
If you wire it to the stoker, I would run the stoker through a relay to keep the electrical load down on the switch itself.
I have one on my oil boiler for the shop, as it runs in a room outside the main shop. I had it active once when the Pressure Relief tripped and drained my feed tank. and system.
It saved the boiler from boiling out.
If I remember the wiring right a beacon can be added to notify you that the boiler is down.
Dan.
-
- Member
- Posts: 180
- Joined: Sun. Oct. 26, 2008 5:19 pm
- Location: catskills, New York State
- Stoker Coal Boiler: KA6 Keystoker
- Hand Fed Coal Stove: Harmon TLC 2000
- Coal Size/Type: Rice, Nut
- Other Heating: oil
home depot doesn't have 1 inch pex pipe in stock here locally by me so I cant even do a patch job! I will have to order it and wait.
-
- Member
- Posts: 286
- Joined: Wed. Jan. 29, 2014 1:42 pm
- Location: N/W Pa. Meadville, Pa.
- Hand Fed Coal Stove: Sears circulator air tight stove.
- Other Heating: Crown 115,000 BTU oil fired boiler(house) Weil Mclain 150,000BTU oil fired boiler(Shop)
Missed that.GaryFerg wrote:its a hand feed boiler don't see how that would help other then the warning lightLu47Dan wrote:Another thing to add to the the system is a low boiler water cut-off switch.
Low Water Cutoff Switch (Low Voltage)
http://www.pexsupply.com/Taco-LTA0243S-2-Electron ... 7AodJkcA2g
Low Water Cutoff Switch (120VAC)
http://www.pexsupply.com/Taco-LTA1203S-2-Electron ... -Off-Water
You can add the 120VAC switch into the stoker system to shut off the stoker if the water level drops to a certain point.
The switch can be installed in the supply side piping 12" above the boiler jacket.
It will open and shut the system down to prevent the stoker from feeding once the water level reaches that point.
If you wire it to the stoker, I would run the stoker through a relay to keep the electrical load down on the switch itself.
I have one on my oil boiler for the shop, as it runs in a room outside the main shop. I had it active once when the Pressure Relief tripped and drained my feed tank. and system.
It saved the boiler from boiling out.
If I remember the wiring right a beacon can be added to notify you that the boiler is down.
Dan.
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
Yes, pull the new in while using the old to pull on...all while still buried underground.GaryFerg wrote:while in place?McGiever wrote:I did something similar once...this did the trick for me...
Splice new onto old w/ apiece of solid rod push half inside both tubes (internal splice coupling) drill 2 holes, 1 thru both halves and tap shear pin in drilled holes. (need not be brass) And file or grind flush.
Lube it up w/ some cable pulling lube and tug/winch her in...lubeing it the whole time while it's being tugged is highly advised.
Yeah, what do you have to lose?
Obviously you need to attach to good sound pipe for the connection.
I'm only saying this for replacing the same size tube...not to install larger.
Other than what might of been used for tying, this will slide right in during the old being removed.
Several rope hitches and a cable winch may be required on the pulling/tugging end.
And leave some extra PEX coiled for a service loop at each end..
-
- Member
- Posts: 637
- Joined: Tue. Jan. 18, 2011 6:41 am
- Location: New Britain, PA
- Stoker Coal Boiler: WL 110
PEX life expectancy:
http://www.vesbo.com/en/pex_2.asp#1
http://www.vesbo.com/en/pex_2.asp#1
Products - PE-X PIPES
Permissible Operating Pressure
Projected Service Life
The following table provides more detailed information with regards to the permissible pressure of various temperatures. These values are derived from the hoop stress chart and formula. Under normal working pressures and conditions, the average service life of Vesbo PE-X pipes is projected to be 50 years or more. A PN 20 hot water pipe, transporting water at a temperature of 95oC can last for more than 50 years under normal conditions with an operating pressure of 8.2 Bars.
-
- Member
- Posts: 180
- Joined: Sun. Oct. 26, 2008 5:19 pm
- Location: catskills, New York State
- Stoker Coal Boiler: KA6 Keystoker
- Hand Fed Coal Stove: Harmon TLC 2000
- Coal Size/Type: Rice, Nut
- Other Heating: oil
Ok this is what was explained to me . I lost all water because boiler overheated. The water in the pipe was gone so atmospheric pressure collapsed the pipe because of the vacuum much like when you heat a tin can and it collapses. I need to add a water supply to my boiler to prevent this and also a dump zone.