Koker Losing Manometer Reading When Blower Turns on

 
jkush
New Member
Posts: 8
Joined: Sat. Jan. 19, 2013 6:19 pm
Location: Pottsville
Hot Air Coal Stoker Furnace: KeyStoker Koker
Coal Size/Type: Rice

Post by jkush » Sat. Jan. 19, 2013 6:38 pm

I just picked up a one year old keystone koker 160. (Looked like it was brand new) I attached to a recently built chimney. When I fired it up I started getting a lot of fumes and had to turn it off. I received and hooked up a dwyer 25 manometer and it read between .02 and .03. I have it ducting into about 15 feet of 8 inch diamater metal duct pipe. I put a thermoter in the duct pipe about 5 feet from furnace. As it started heating up I noticed the duct thermometer went up 210 degrees then the stove turned on. The duct thermoter dropped to about 140 while fan was on. The big problem that I see is that when the blower turned on the manometer went to + .05 (Positive pressure) and I could feel and smell the air comming out of the barametric damper which was being forced closed due to pressure. Any information would be creatly apprecieated.


 
User avatar
Scottscoaled
Member
Posts: 2812
Joined: Tue. Jan. 08, 2008 9:51 pm
Location: Malta N.Y.
Stoker Coal Boiler: EFM 520, 700, Van Wert 800 GJ 61,53
Baseburners & Antiques: Magic Stewart 16, times 2!
Coal Size/Type: Lots of buck
Other Heating: Slant Fin electric boiler backup

Post by Scottscoaled » Sat. Jan. 19, 2013 6:45 pm

Chimney is plugged?

 
User avatar
LsFarm
Member
Posts: 7383
Joined: Sun. Nov. 20, 2005 8:02 pm
Location: Michigan
Stoker Coal Boiler: Axeman Anderson 260
Hand Fed Coal Boiler: Self-built 'Big Bertha' SS Boiler
Baseburners & Antiques: Keystone 11, Art Garland

Post by LsFarm » Sat. Jan. 19, 2013 6:48 pm

Describe your chimney, it sounds like it is clogged. the combustion fan in the stove should not be able to create a positive pressure in the chimney
UNLESS it is blocked or clogged..
Do you have a source of fresh 'make=up' air to replace the air going up the chimney and down the ducts?? Sometimes a room is too tight for a
chimney t be able to draw enough air .

But it sure sounds like the chimney is at least partially blocked.

Greg L

 
User avatar
Wiz
Member
Posts: 926
Joined: Sun. Nov. 27, 2011 8:45 pm
Location: Tannersville Pa
Stoker Coal Boiler: Keystoker Ka 6
Coal Size/Type: Casey Junk Coal :(

Post by Wiz » Sat. Jan. 19, 2013 8:51 pm

Check your stove pipes for flyash build up

 
Rigar
Member
Posts: 856
Joined: Tue. Dec. 04, 2012 6:30 am
Location: central new york (syracuse area)
Hot Air Coal Stoker Furnace: Keystoker A 150
Coal Size/Type: anthracite rice

Post by Rigar » Sat. Jan. 19, 2013 9:57 pm

sorry but I am unclear about 1 thing..
you said when the " blower" comes on... draft will go positive

... do you mean the combustion blower (i would assume)
... or do you mean convection blower... that sends the heated air through your duct..??

... positive pressure in the chimney from the combustion blower would definitely indicate restriction in the flu... you said you have a baro installed... any chance you have a manual damper also?
... but if you mean the convection blower ( when that comes on) is creating positive pressure in the chimney... that's an entirely different story.
... my first bet would be chimney is restricted.
... but my confusion lies here:
you're getting a good draft when you started up... and you are getting 210 degree duct temperatures
... so I'm assuming your combustion blower is already running?

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sat. Jan. 19, 2013 10:05 pm

Noticed you said it was a newly built chimney, still check it for no obstructions. Do not burn without Carbon Monoxide Detectors installed.

Also, you might try restricting the air inlet of the fan...less air in = less air out. The manometer will read the changes as you adjust the restrictor at air inlet.

 
jkush
New Member
Posts: 8
Joined: Sat. Jan. 19, 2013 6:19 pm
Location: Pottsville
Hot Air Coal Stoker Furnace: KeyStoker Koker
Coal Size/Type: Rice

Post by jkush » Sat. Jan. 19, 2013 10:38 pm

Thank you for such a quick response. I apologize for the confusion on which blower. The blower that causes the manometer to jump is the one that come on to blow the hot air through the ductwork. I was just speaking to a freind who works on coal stoves every day and he believes I have a crack or a hole somewhere in the firebox or heat exchanger. That would account for the high temps in my ductwork (Hot gasses leaking into duct) and for the pressure when the fan turns on. I plan on removing blower and top plate to inspect for something obvious. I probably will also contact Keystoker but I am not sure if they will be able to assist for I am not the original purchaser. I am going to try to attach 2 pics to give you a visual. Again that you for all you help.

Attachments

photo.JPG

Pic1

.JPG | 98KB | photo.JPG
photo (1).JPG

Pic 2

.JPG | 93.3KB | photo (1).JPG


 
User avatar
Rick 386
Member
Posts: 2508
Joined: Mon. Jan. 28, 2008 4:26 pm
Location: Royersford, Pa
Stoker Coal Boiler: AA 260 heating both sides of twin farmhouse
Hot Air Coal Stoker Stove: LL Hyfire II w/ coaltrol in garage
Coal Size/Type: Pea in AA 260, Rice in LL Hyfire II
Other Heating: Gas fired infared at work
Contact:

Post by Rick 386 » Sat. Jan. 19, 2013 10:48 pm

As Greg LS Farm indicated, your house may be too tight,

Crack a window in the room where the stove is located and see if the manometer changes.

If your house is too tight, when that big old convection fan comes on, it is sucking air from wherever it can. If the room is too tight, it is actually pulling or creating a backflow in the flue pipe. This used to happen at my old shop when I had all the doors and windows closed and turned on my spraybooth exhaust fan. It would actually cause a back flow from the oil burner. Cracking a window would solve the problem. This is usually called "make up air."

Rick

 
Rigar
Member
Posts: 856
Joined: Tue. Dec. 04, 2012 6:30 am
Location: central new york (syracuse area)
Hot Air Coal Stoker Furnace: Keystoker A 150
Coal Size/Type: anthracite rice

Post by Rigar » Sat. Jan. 19, 2013 11:06 pm

;) hmm
Last edited by Rigar on Sat. Jan. 19, 2013 11:19 pm, edited 1 time in total.

 
Rigar
Member
Posts: 856
Joined: Tue. Dec. 04, 2012 6:30 am
Location: central new york (syracuse area)
Hot Air Coal Stoker Furnace: Keystoker A 150
Coal Size/Type: anthracite rice

Post by Rigar » Sat. Jan. 19, 2013 11:16 pm

I didnt want to jump to conclusions...but it def sounds like the fire box is compromised. That would explain positive pressure when it comes on
:(

The simplest way to check this would be to DISCONNECT the duct from the top of the stove
...this would allow the air in the room to "free wheel"...as you wont be evacuating it.
"spillage" should then be prevented...if that is the problem.
...unfortunately this would entail you firing it up again
Last edited by Rigar on Sat. Jan. 19, 2013 11:21 pm, edited 1 time in total.

 
User avatar
VigIIPeaBurner
Member
Posts: 2579
Joined: Fri. Jan. 11, 2008 10:49 am
Location: Pequest River Valley, Warren Co NJ
Hot Air Coal Stoker Furnace: Keystoker Koker(down)
Hand Fed Coal Stove: Vermont Casting Vigilant II 2310
Other Heating: #2 Oil Furnace

Post by VigIIPeaBurner » Sat. Jan. 19, 2013 11:20 pm

Rick is onto the problem.

Is yor cold air return drawing off the basement floor? From the pictures you posted it looks like that is the case. If so and your basement is tight, it could pull on the chimney for a source of air to make up for the vacuum created when the circulating blower pulls air out of the basement. If this is the case, hook up a cold air duct work line to the first floor. You should also consider running a 4" combustion air supply from the outside to the combustion air shutter/motor. Both of these systems, a cold air return and outside combustion air, should stop the back flow thru the chimney. There ar several threads on this forum regarding running combustion air lines to a Koker.

 
Rigar
Member
Posts: 856
Joined: Tue. Dec. 04, 2012 6:30 am
Location: central new york (syracuse area)
Hot Air Coal Stoker Furnace: Keystoker A 150
Coal Size/Type: anthracite rice

Post by Rigar » Sat. Jan. 19, 2013 11:53 pm

Im gonna lean the other way on this one a bit...
koker 160 has a 1500 cfm convection blower
..thats a TON of air !
Not that a single 8 " duct will allow that much through it...but alot of air just the same.
.again- remove the supply duct or restrict inlet
...if the basement is even fairly tight...that size blower could create neg. pressure in the basement..(reading positive on your guage)

...but fumes immediately on start up (with adequate draft ) indicates something else (imo)

...

 
User avatar
blrman07
Member
Posts: 2383
Joined: Mon. Sep. 27, 2010 3:39 pm
Location: Tupelo Mississippi

Post by blrman07 » Sun. Jan. 20, 2013 7:05 am

I am tending to agree with rick36 on this one.

Lets keep the checking simple. Coal stove operation and coal burning is not an exotic action. Do not assume anything. Verify it visually.

1. I didn't see anything in the photo's showing where the return air is coming from. If that big distribution fan is sucking from the same room the stove is in chances are excellent that it is just pulling the fumes right out of the stove and into the fan ducting. If that is the case then when the blower starts and sucks all that air, it's going to get it from somewhere. What better place than back-drafting down a wide open chimney? Open a window WIDE OPEN in the stove area and try it again. If the firebox pressure stays negative you found the problem. Not enough makeup air in the stove area.

The Koker needs to be tied in to the return air system and it needs lots of makeup air. See the threads in this forum for cold air return for Koker or Koker return air.

2. Verify visually that the chimney is COMPLETELY open from top to bottom.

3. Verify visually that the flue pipe is COMPLETELY open from stove to chimney.

IMHO start with the most obvious and work to the obscure.

Rev. Larry

 
CoaLen
Member
Posts: 601
Joined: Wed. Apr. 09, 2008 7:05 am
Location: Geauga County, NE Ohio
Hot Air Coal Stoker Furnace: Keystoker Koker
Coal Size/Type: rice

Post by CoaLen » Sun. Jan. 20, 2013 7:28 am

The Koker is a furnace, not a stove. The 1536 CFM blower is a big part of that difference. It needs to be drawing air from your return duct, not your basement. Rick, Rev Larry, Greg and VigII are right, you are currently pulling air down your chimney through your damper.
You also need to get a much larger hot air connection to your duct work to get all the heat the blower is trying to wash off the furnace. That single small line is going to offer too much resistance to good hot air flow.
The Koker will keep you very warm when you get it hooked up right. :)

 
User avatar
Dennis
Member
Posts: 1082
Joined: Sun. Oct. 30, 2011 5:44 pm
Location: Pottstown,Pa
Hand Fed Coal Boiler: AHS/WOC55-multi-fuel/wood,oil,coal
Coal Size/Type: Anthracite/stove size

Post by Dennis » Sun. Jan. 20, 2013 7:45 am

CoaLen wrote:The Koker is a furnace, not a stove. The 1536 CFM blower is a big part of that difference. It needs to be drawing air from your return duct, not your basement. Rick, Rev Larry, Greg and VigII are right, you are currently pulling air down your chimney through your damper.
You also need to get a much larger hot air connection to your duct work to get all the heat the blower is trying to wash off the furnace. That single small line is going to offer too much resistance to good hot air flow.
The Koker will keep you very warm when you get it hooked up right. :)
I agree with the above. Not quite sure ,but when the combustion blower is running without the convection blower look to see witch way the baro flap is going then turn the convection blower on and see if the baro flap changes direction.Or put a candle in front of the baro to see any changes in air flow.


Post Reply