Post by Joe » Tue. Apr. 26, 2011 8:50 pm

This is my first year with the AHS-130. I would like to try to burn through the summer for DHW, we have a pretty large demand. But ... My dump zone has been turning on more frequently, and heating the garage beyond comfortable. Do any of you guys with AHS-130's burn through the summer, and if so, what adjustments do you make to the asher temperature settings? I also heard the about 12lbs/day is a min for this boiler at no-load.


 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Tue. Apr. 26, 2011 9:02 pm

Joe wrote:This is my first year with the AHS-130. I would like to try to burn through the summer for DHW, we have a pretty large demand. But ... My dump zone has been turning on more frequently, and heating the garage beyond comfortable. Do any of you guys with AHS-130's burn through the summer, and if so, what adjustments do you make to the asher temperature settings? I also heard the about 12lbs/day is a min for this boiler at no-load.
**Broken Link(s) Removed**

 
User avatar
mozz
Member
Posts: 1363
Joined: Mon. Sep. 17, 2007 5:27 pm
Location: Wayne county PA.
Stoker Coal Boiler: Axeman Anderson 1982 AA-130 Steam

Post by mozz » Tue. Apr. 26, 2011 9:12 pm

I burn year round and in the summer it doesn't save me anything, unless you count boiler life in the equation. I think I measured, in 5 gallon pails worth, how much coal I burned a week. My electric hot water heater would be cheaper to run. It is not a PITA to clean a boiler, it is part of owning it, if you neglect that, well, you will find out the hard way. The first year I had the AA130 I turned down the aquastat from 190-230 to 160-200 or something, ran the water up a little bit in the sight glass because when running steam, only about 1/2 the coil is actually under water, correct me if I am wrong on that one. Last year and this year I just leave it at the winter settings, helps dry out the basement, snakes like it too.

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Tue. Apr. 26, 2011 9:15 pm

Joe wrote:This is my first year with the AHS-130. I would like to try to burn through the summer for DHW, we have a pretty large demand. But ... My dump zone has been turning on more frequently, and heating the garage beyond comfortable. Do any of you guys with AHS-130's burn through the summer, and if so, what adjustments do you make to the asher temperature settings? I also heard the about 12lbs/day is a min for this boiler at no-load.
Joe, please post all of your settings. Are you using a tankless coil in the AHS?

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Tue. Apr. 26, 2011 9:36 pm

Wood'nCoal wrote:
Are you happy with the hot water production with 3 teeth and 150 for the low limit? Also, do you have a bypass installed between the supply and return on the boiler?
So far, so good, but I just made the change yesterday. I'm just happy I was able to figure out why I lost the fire. The incoming cold water tends to warm up some in the Summer as opposed to the dead of Winter. Yesterday after relighting the boiler the water temperature hit 210° :shock: , it was running on the timer, I guess that second little shovel full of coal I placed on top of the wood fire was a tad too much!
Yes, there is a bypass, ball valve is open about 1/4.
I would run the bypass wide open for DHW duty...natural convection should keep the temperature more uniform in the boiler. I did not install a bypass on mine, and that was a mistake. It does thermosiphon a little through the oil boiler, but not much.

 
User avatar
steevesj
Member
Posts: 106
Joined: Thu. Apr. 24, 2008 7:31 pm
Location: Willsboro, Upstate New York

Post by steevesj » Tue. Apr. 26, 2011 9:40 pm

markviii wrote: How tall is the chimney compared to the roof? What size is the flue? Are you using the recommended 8" pipe? How many elbows and tee's are installed between the boiler and the thimble?
The chimney stands about 6-8 feet high from the edge of the roof. There is 1 90 from the boiler then 1 90 that connects into the horizontal pipe that leads to the chimney. There is 8" pipe to the thimble but the chimney is 6" clay.

 
User avatar
CoalHeat
Member
Posts: 8862
Joined: Sat. Feb. 10, 2007 9:48 pm
Location: Stillwater, New Jersey
Stoker Coal Boiler: 1959 EFM 350
Hand Fed Coal Stove: Harman Magnafire Mark I
Baseburners & Antiques: Sears Signal Oak 15 & Andes Kitchen Range
Coal Size/Type: Rice and Chestnut
Other Heating: Fisher Fireplace Insert

Post by CoalHeat » Tue. Apr. 26, 2011 9:46 pm

I would run the bypass wide open for DHW duty...natural convection should keep the temperature more uniform in the boiler
Good idea.

Also covering the baro with foil isn't a bad idea either in the warm weather. Even when the baro is closed there is space between the flap and the housing, especially on a larger baro like mine (8").


 
Pacowy
Member
Posts: 3555
Joined: Tue. Sep. 04, 2007 10:14 pm
Location: Dalton, MA
Stoker Coal Boiler: H.B. Smith 350 Mills boiler/EFM 85R stoker
Coal Size/Type: Buckwheat/anthracite

Post by Pacowy » Wed. Apr. 27, 2011 12:58 am

mozz wrote: It is not a PITA to clean a boiler, it is part of owning it, if you neglect that, well, you will find out the hard way.
You seem to be misquoting my earlier post, which stated that cleaning my boiler "for a summer shutdown would be a PITA". The boiler is a 350 Mills (not an EFM 350), a 7-section water tube boiler that has a large heat exchange area comprised of irregular surfaces. It is not neglected, and gets cleaned as it is supposed to be for a boiler in use. My point was that cleaning it to the extent that would be required to prevent corrosion if it were idled in the summer would be a PITA, and for that boiler I think that's a pretty fair summary.

Mike

 
User avatar
blrman07
Member
Posts: 2383
Joined: Mon. Sep. 27, 2010 3:39 pm
Location: Tupelo Mississippi

Post by blrman07 » Wed. Apr. 27, 2011 6:57 am

6th year burning my Yellow flame boiler year round. It took a while to figure out but I found setting the pins to make shorter runs more often did the trick on those hot hot hot summer days when the chimney looses draft. For four years now I reset the pins to "summer" mode on Easter Sunday and have had not a single out fire due to losing draft since I started doing that.

Coal usage is 1/4 ton a month or 15-16 lbs a day. Current price for Lenig's coal is $140 ton bulk. My DHW costs me $1.16 a day during the summer.

This summer that will be even less because I will supplement the DHW coil in the boiler by running the preheated solar DHW through it. The only way to get less now is to cut the boiler off and go with 100% solar and circulate the DHW through the coil and use the boiler as a heat sink. Hmmmmmm....gave myself an idea to tinker with!

 
ben
Member
Posts: 178
Joined: Thu. Aug. 06, 2009 9:06 pm
Location: n central PA
Stoker Coal Boiler: EFM 350 with an S-20 pot (1966)
Coal Size/Type: Rice

Post by ben » Wed. Apr. 27, 2011 11:15 am

Efm 350 here. I run this unit all summer long with my timer every 30 min for about 1 minute. Never a problem. Set my limits at 130 - 170. This keeps the temp about 145. Also by running the boiler thru the summer I do not have to use my de-humidifier, which saves on my electric.
Seem to be around 5 ton a year with a traditional Cape Cod.

 
User avatar
CoalHeat
Member
Posts: 8862
Joined: Sat. Feb. 10, 2007 9:48 pm
Location: Stillwater, New Jersey
Stoker Coal Boiler: 1959 EFM 350
Hand Fed Coal Stove: Harman Magnafire Mark I
Baseburners & Antiques: Sears Signal Oak 15 & Andes Kitchen Range
Coal Size/Type: Rice and Chestnut
Other Heating: Fisher Fireplace Insert

Post by CoalHeat » Wed. Apr. 27, 2011 6:27 pm

Also by running the boiler thru the summer I do not have to use my de-humidifier, which saves on my electric.
:D :) :D

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Wed. Apr. 27, 2011 6:54 pm

steevesj wrote:
markviii wrote: How tall is the chimney compared to the roof? What size is the flue? Are you using the recommended 8" pipe? How many elbows and tee's are installed between the boiler and the thimble?
The chimney stands about 6-8 feet high from the edge of the roof. There is 1 90 from the boiler then 1 90 that connects into the horizontal pipe that leads to the chimney. There is 8" pipe to the thimble but the chimney is 6" clay.
I think a 6" flue is marginal for your application. Have you adjusted the inlet damper according to Keystoker's instructions? You could be pressurizing the firebox with excessive combustion air.

How tall is the chimney compared to the roof peak?

 
User avatar
tsb
Member
Posts: 2621
Joined: Wed. Jul. 30, 2008 8:38 pm
Location: Douglassville, Pa
Stoker Coal Boiler: Binford 2000
Hot Air Coal Stoker Stove: LL Pioneer top vent
Hand Fed Coal Stove: Saey Hanover II
Baseburners & Antiques: Grander Golden Oak , Glenwood # 6
Coal Size/Type: All of them

Post by tsb » Wed. Apr. 27, 2011 9:22 pm

I didn't run last summer because I was just getting acquainted with the
contraption that I built. This summer I'm going to let it run on low fire
all summer. During high water demand the boiler may run a little cold,
but it will have all night and day to recover. Hope to burn no more than
15 pounds a day.

 
User avatar
whistlenut
Member
Posts: 3548
Joined: Sat. Mar. 17, 2007 6:29 pm
Location: Central NH, Concord area
Stoker Coal Boiler: AA130's,260's, AHS130&260's,EFM900,GJ & V-Wert
Hand Fed Coal Boiler: Franks,Itasca 415,Jensen, NYer 130,Van Wert
Hot Air Coal Stoker Furnace: Alaska, EFM, Keystoker, Yellow Flame
Hot Air Coal Stoker Stove: Alaska, Keystoker-2,Leisure Line
Hand Fed Coal Stove: Alaska, Gibraltar, Keystone,Vc Vigilant 2
Hand Fed Coal Furnace: Ford, Jensen, NYer, Van Wert,
Baseburners & Antiques: Glenwoods
Coal Size/Type: Barley, Buck, Rice ,Nut, Stove
Other Heating: Oil HWBB

Post by whistlenut » Wed. Apr. 27, 2011 9:31 pm

It's not chilly in the boiler rooms anywhere tonight! Made 75 here at 3pm, still 68 at 9:30. Spring? One day of it.....

 
User avatar
CoalHeat
Member
Posts: 8862
Joined: Sat. Feb. 10, 2007 9:48 pm
Location: Stillwater, New Jersey
Stoker Coal Boiler: 1959 EFM 350
Hand Fed Coal Stove: Harman Magnafire Mark I
Baseburners & Antiques: Sears Signal Oak 15 & Andes Kitchen Range
Coal Size/Type: Rice and Chestnut
Other Heating: Fisher Fireplace Insert

Post by CoalHeat » Wed. Apr. 27, 2011 9:57 pm

When I had the Alaska stove burning for DHW all summer the cellar stayed 85° to 90°, I expect lower temperatures this year.