Power Usage

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Thu. Apr. 06, 2017 10:47 am

Generally I believe that an induction motor can briefly peak at up to about 5 - 7 times its running (under load) amp draw. This could very briefly exceed the required wire and fuse capacity of the circuit. That is why fuses have time delay ratings.

Don't quote me, but I think the general rule is to assume 250% of full load current and size your motor circuits wires and breakers somewhat above this value.

For the example of a 1/2 HP motor (single phase, 120V) I would take this to mean:

373 Watts/110 Volts = 3.39 amps (allowing for a bit of commonly seen voltage drop)

3.39 x 2.5 = 8.5 Amps

The wiring and breaker for this motor must be selected to allow for some margin of safety above 8.5 amps, so 10 amp capable wiring (at a minimum) and a 10 amp breaker (maximum) are the choices here.

I need McGiever to review my logic here and correct it as needed.

EDIT: If your motors spec plate indicates its LRA (locked rotor amps) this value (I presume) should be fairly representative of its peak draw. At the moment the circuit closes, and just before the rotor breaks free and the motor spins, it is effectively (and very briefly) in the state of "locked".

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Thu. Apr. 06, 2017 11:13 am

They generally draw about 3X the nameplate at startup. But that is a very brief event. The average motor should draw about half its rating in actual service, at least that is my experience with them. Running over 80% of its nameplate will pretty much assure a limited lifespan.

 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Thu. Apr. 06, 2017 2:25 pm

Wow, I'll need to get one of those meters that wraps around the wire. I just assumed they used what they were stamped. Now I'm curious to see what they really draw.


 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Thu. Apr. 06, 2017 3:18 pm

If you know their rated HP, you know what Watts they draw. If they are conventional fixed speed motors, and they are not running at their rated HP, then you were sold a bill of goods when you bought them. Variable speed is another matter.

1 HP = 746 Watts

 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Thu. Apr. 06, 2017 3:27 pm

Yeah, they are fixed speed and stamped 2.8 amps each.

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Thu. Apr. 06, 2017 3:28 pm

Kill A Watt easy meter, $20 @ Home Depot.

http://m.homedepot.com/p/P3-International-Kill-A-Watt-EZ-Meter-P4460/202196388

Current (amps) goes up as the load increases, has nothing to do with HP rating, they only make enough HP to perform the task.


 
User avatar
oliver power
Member
Posts: 2970
Joined: Sun. Apr. 16, 2006 9:28 am
Location: Near Dansville, NY
Stoker Coal Boiler: KEYSTOKER Kaa-2
Hand Fed Coal Stove: Hitzer 50-93 & 30-95, Vigilant (pre-2310), D.S. 1600 Circulator, Hitzer 254

Post by oliver power » Thu. Apr. 06, 2017 7:36 pm

Lightning wrote:I thought they would draw what they are rated since it seems to work that way with light bulbs and heating elements lol.
Hi Lightning. I'm no electrical engineer. However, I've always been told an electric motor draws the rated amps at start up. Once up to speed, it draws about half.

I've been around some big electric motors, with amp gauges on them. And when turned on, the gauge shows exactly that. .....and every time, I think about what I've been told. Some things just get etched in ones brains for life. :)

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Thu. Apr. 06, 2017 8:22 pm

Inrush AMPS (Single Phase) = ((Locked Rotor value per code letter) X HP X 1000)/VAC
(where inrush amps are the motors peak start-up current)

Locked Rotor Code Letters and their values
(low-high and midrange)
A 0.00 - 3.14 1.6
B 3.15 - 3.54 3.3
C 3.55 - 3.99 3.8
D 4.00 - 4.49 4.3
E 4.50 - 4.99 4.7
F 5.00 - 5.59 5.3
G 5.60 - 6.29 5.9
H 6.30 - 7.09 6.7
J 7.10 - 7.99 7.5
K 8.00 - 8.99 8.5
L 9.00 - 9.99 9.5
M 10.00 - 11.19 10.6
N 11.20 - 12.49 11.8
0 12.50 - 13.99 13.2
R 14.00 - 15.99 15.0

The motors locked rotor code letter should be on its spec plate.