dennis8483
New Member
Posts: 17
Joined: Thu. Apr. 24, 2014 9:13 pm
Other Heating: Propane

Post by dennis8483 » Tue. Dec. 20, 2016 6:35 pm

Bought a 4 year old stove and been running for 2 years now. Primarily run on stove temp around 2 or 3. Now the feed motor doesn't want to kick on sometimes. Fire dies down randomly, occaisionally going out. When it does go out, coal is completely burned on grates and as far back as possible. Feed motor is not engaging at all, no light, no motion, no indication of it working at all.

Most times, the feed motor works no problem, and when it is not feeding properly, I turn to test mode and feed motor pushes coal no problem. Wondering if it's a board issue. Any suggestions?

 
coalnewbie
Member
Posts: 8601
Joined: Sat. May. 24, 2008 4:26 pm
Location: Chester, NY
Hot Air Coal Stoker Stove: LL AnthraKing 180K, Pocono110K,KStokr 90K, DVC
Hand Fed Coal Stove: Invader 2
Baseburners & Antiques: Wings Best, Glenwood #8(x2) Herald 116x
Coal Size/Type: Rice,
Other Heating: Heating Oil CH, Toyotomi OM 22

Post by coalnewbie » Tue. Dec. 20, 2016 8:15 pm

Have you cleaned out the fines drawer? How about that little filter?


 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Tue. Dec. 20, 2016 9:34 pm

Dirty probes???