Chimneys Caps: Cap or No Cap?

 
User avatar
deepwoods
Member
Posts: 616
Joined: Fri. Aug. 29, 2008 10:21 am
Location: north central pa.
Hand Fed Coal Stove: Hitzer 50-93 & DS Machine Newstyle Champion
Coal Size/Type: nut (so far)
Other Heating: Ruud propane forced air system

Post by deepwoods » Mon. Feb. 06, 2017 9:42 pm

2 flue masonry chimney. Both flues have ss caps. No reduction in drafting at least according to my manometers. Upper 1/2 of chimney rebuilt this past summer and the caps are new also.


 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Tue. Feb. 07, 2017 8:31 am

'google' wind directional chimney cap ;)

 
User avatar
oliver power
Member
Posts: 2970
Joined: Sun. Apr. 16, 2006 9:28 am
Location: Near Dansville, NY
Stoker Coal Boiler: KEYSTOKER Kaa-2
Hand Fed Coal Stove: Hitzer 50-93 & 30-95, Vigilant (pre-2310), D.S. 1600 Circulator, Hitzer 254

Post by oliver power » Tue. Feb. 07, 2017 7:58 pm

I've been slow to reply on this subject. Personally, I like to keep the water from running down my chimney (not that it's a big concern when burning). For that reason, I like a simple hat over my chimney. The hat also helps draft during low pressure atmosphere. That being said, I see chimneys all over the place. Some with caps, and some without caps. Some in great shape, others not so..... I think it all boils down to maintenance (cap or no cap).

We're up close to chimneys all the time. From the ground, most chimneys look good. Up close; many need attention.

 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Tue. Feb. 07, 2017 8:33 pm

oliver power wrote:The hat also helps draft during low pressure atmosphere
Low pressure atmosphere?

 
User avatar
2001Sierra
Member
Posts: 2211
Joined: Wed. May. 20, 2009 8:09 am
Location: Wynantskill NY, 10 miles from Albany
Hot Air Coal Stoker Stove: Keystoker 90 Chimney vent
Coal Size/Type: Rice
Other Heating: Buderus Oil Boiler 3115-34

Post by 2001Sierra » Tue. Feb. 07, 2017 9:59 pm

oliver power wrote:I've been slow to reply on this subject. Personally, I like to keep the water from running down my chimney (not that it's a big concern when burning). For that reason, I like a simple hat over my chimney. The hat also helps draft during low pressure atmosphere. That being said, I see chimneys all over the place. Some with caps, and some without caps. Some in great shape, others not so..... I think it all boils down to maintenance (cap or no cap).
I too agree with Oliver Power, and have held back on contributing.

Before burning this year I have been speaking with friends about removing my stainless chimney cap to see if the sulfur smell from time to time would dissapate more. Still have not acted on it, and curious what others here may say. Also hoping to add pictures of my install.
Last edited by 2001Sierra on Sat. Apr. 01, 2017 12:20 pm, edited 2 times in total.
Reason: Quote box

 
User avatar
oliver power
Member
Posts: 2970
Joined: Sun. Apr. 16, 2006 9:28 am
Location: Near Dansville, NY
Stoker Coal Boiler: KEYSTOKER Kaa-2
Hand Fed Coal Stove: Hitzer 50-93 & 30-95, Vigilant (pre-2310), D.S. 1600 Circulator, Hitzer 254

Post by oliver power » Tue. Feb. 07, 2017 10:01 pm

Lightning wrote:
oliver power wrote:The hat also helps draft during low pressure atmosphere
Low pressure atmosphere?
Yes, or maybe I should say low atmospheric pressure. What ever the terminology, chimneys don't seam to draw as well. The hat over the chimney helps.

 
User avatar
mozz
Member
Posts: 1351
Joined: Mon. Sep. 17, 2007 5:27 pm
Location: Wayne county PA.
Stoker Coal Boiler: Axeman Anderson 1982 AA-130 Steam

Post by mozz » Sat. Apr. 01, 2023 6:51 pm

Back from the dead thread. Me almost, CO beeper was going off today, windy, making my draft go positive. I don't know if the cap screen is blocked, hard to tell from the picture from my phone. It is blocked some as i shot it with the BB gun and i can see a puff of soot. Opened all the basement windows. Fire is now almost out after 6 hours. I have cleaning rods and a 8" brush but from the cellar i can't get all the way to the top, going to tractor supply tomorrow and getting 18' more ft. Could also be after a new roof a few years back maybe the guys didn't tighten the screws and the cap dropped?
IMG_20230401_172159258.jpg
.JPG | 296.7KB | IMG_20230401_172159258.jpg
IMG_20230401_172203928.jpg
.JPG | 301.9KB | IMG_20230401_172203928.jpg
IMG_20230401_172212691.jpg
.JPG | 325.3KB | IMG_20230401_172212691.jpg
IMG_20230401_172214113.jpg
.JPG | 322.4KB | IMG_20230401_172214113.jpg
IMG_20230401_172228772.jpg
.JPG | 148.8KB | IMG_20230401_172228772.jpg
IMG_20230401_172230786.jpg
.JPG | 156.7KB | IMG_20230401_172230786.jpg
IMG_20230401_172246825.jpg
.JPG | 148.9KB | IMG_20230401_172246825.jpg


 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Sat. Apr. 01, 2023 7:11 pm

Yeah, that doesn't look like there is much clearance for exhaust to exit. The screens do get brittle and decay. It appears that the cap has sunk. I'd recommend that somebody go up there and check it out. Personally, I think rain caps are a good idea since they will help keep the chimney dry.

 
stokerstove
Member
Posts: 179
Joined: Wed. Jan. 25, 2006 4:05 pm
Location: NE PA
Hot Air Coal Stoker Stove: Alaska Kodiak Stokerstove 1

Post by stokerstove » Sat. Apr. 01, 2023 10:05 pm

Always have a cap on my 2 story masonry chimney while burning the stove. No problem with draft and keeps the rain and critters out. I remove the cap at the end of the season and replace it with a cover I fabricated from an old cap. Always wash the ash off it, anti-seize the threads and store it in a dry spot. By doing this, I'm only on my 3rd cap in 35 or more years of burning the stove. Current cap is stainless and is showing its age, might break down and get a new one for next season.

 
User avatar
davidmcbeth3
Member
Posts: 8505
Joined: Sun. Jun. 14, 2009 2:31 pm
Coal Size/Type: nut/pea/anthra

Post by davidmcbeth3 » Mon. Apr. 03, 2023 1:23 am

Have animals nearby ? Then cap it. Pretty sure you have animals nearby.

 
k-2
Member
Posts: 1744
Joined: Thu. Sep. 28, 2017 10:57 am
Location: Coal Township Pa
Stoker Coal Boiler: K2- Keystoker
Hot Air Coal Stoker Stove: Alaska Stoker Stove
Coal Size/Type: Rice

Post by k-2 » Mon. Apr. 03, 2023 4:27 am

I put in a brand new masonry chimney and very soon after noticed water wicking through the clay liner and concrete block around the clay liner thimble in the living room after a rainstorm. I installed a good SS cap,problem solved.

 
User avatar
mozz
Member
Posts: 1351
Joined: Mon. Sep. 17, 2007 5:27 pm
Location: Wayne county PA.
Stoker Coal Boiler: Axeman Anderson 1982 AA-130 Steam

Post by mozz » Mon. Apr. 03, 2023 6:18 am

Ran a brush up from the bottom, a got a lot of ash and crud, which i don't see how that built up. Brush went all the way until it hit the cap and i hit it a bunch of times to loosen what i could. Relit and after a while brought the house back up to 70 from 63 overnight. Draft is -.030 which is good, wind causes it to shift but i am not getting below zero, wind has also died down. I still can see some of the screen partially blocked so i will try to blast it with the gas powered pressure washer during the week. Climbing the roof is not for me so if i have to pay someone to do it i will.

 
Hoytman
Member
Posts: 6019
Joined: Wed. Jan. 18, 2017 11:30 pm
Location: swOH near a little town where the homes are mobile and the cars aren’t
Hand Fed Coal Stove: Hitzer 354
Coal Size/Type: nut coal
Other Heating: electric, wood, oil

Post by Hoytman » Mon. Apr. 10, 2023 9:02 pm

Next year will mark the 70th anniversary of this home with two chimneys and neither have chimney caps.

Never had/have a problem, coal or wood.

I’m not saying it’s right or wrong. Just giving you the facts of this house…family home.

If I were to cap it, then it would be when it isn’t in use. When the chimney’s are in use the caps would come off.

Taking caps on and off would be a pain, so then a cap of an open design would be my choice if I were to cap any chimney. That means animals can still get in the chimney, which just means you check them before putting the chimney in use…seasonal checking if a chimney is basic common sense anyway…means checking a couple times a year is a good practice.

 
nut
Member
Posts: 1397
Joined: Wed. Aug. 28, 2019 1:54 pm
Location: NEPA
Hand Fed Coal Stove: Glacier Bay
Coal Size/Type: nut
Other Heating: electric

Post by nut » Mon. Apr. 10, 2023 9:50 pm

Me too, no cap. Had one once but it rotted out and I can't reach the chimney so no cap for many years now. I have never seen signs of rain getting in. I'm sure it does but it must evaporate fast. I burn the stove all winter so the chimney stays warm and prevents water expansion damage.

 
User avatar
SMITTY
Member
Posts: 12520
Joined: Sun. Dec. 11, 2005 12:43 pm
Location: West-Central Mass
Stoker Coal Boiler: EFM 520 Highboy
Coal Size/Type: Rice / Blaschak anthracite
Other Heating: Oil fired Burnham boiler

Post by SMITTY » Thu. May. 04, 2023 10:55 am

I needed a cap on mine. 100+ year old chimney that you can scoop out the mortar with a fingernail. It's ROUGH. There's also 2 jogs in the run going 2 different directions! So, whenever it rains, water leaks through the crappy mortar.

A cap fixed it, and since it's an internal chimney with none of the 4 sides exposed to the outdoors, draft is still very good.

The cap does have to be high enough up above the flue, obviously. I'd wager that cap rotted out and sunk.


Post Reply