Help on Plumbing for Thermosiphon

 
User avatar
Richard S.
Mayor
Posts: 15242
Joined: Fri. Oct. 01, 2004 8:35 pm
Location: NEPA
Stoker Coal Boiler: Van Wert VA1200
Coal Size/Type: Buckwheat/Anthracite

Post by Richard S. » Mon. Sep. 15, 2008 8:14 pm

This is how ours was set up BIG BEAM, plumbing wasn't exactly the same because our coil has two pipe same height on the back of the furnace.
BIG BEAM wrote:No need for any check valves.But that's just me.
I can understand your point about the check valve on the cold water inlet. As far as the one in the loop if you have a large coil in boiler it's most practical to send it through the coil first since it can heat the water quickly.


 
User avatar
Freddy
Member
Posts: 7301
Joined: Fri. Apr. 11, 2008 2:54 pm
Location: Orrington, Maine
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Coal Size/Type: Pea size, Superior, deep mined

Post by Freddy » Mon. Sep. 15, 2008 8:33 pm

BIG BEAM wrote:if you hook the hot from the coil to the hot on the tank when a tap is opened the hot from the coil will go right into the hot water line bypassing the tank.
No it won't. Water takes the path of least resistence.
Take a look here. They show a diagram of how to hook the one they sell up.

http://www.therma-coil.com/plumbing.htm

Richard makes a point. The heat picked up during a quick pass might not be much, but any is more than none! Maybe it should be done similar to his idea.

 
BIG BEAM
Member
Posts: 712
Joined: Fri. Jan. 25, 2008 9:34 am
Location: upstate NY

Post by BIG BEAM » Mon. Sep. 15, 2008 9:18 pm

Freddy look at the pics
What will make the water go into the tank if the hot coming out of the coil is connected to the hot on the tank and a tap (hot water) is open?
DON

Freddy I just looked at you link and that is just what I said to ceccll on how I would do it.

 
BIG BEAM
Member
Posts: 712
Joined: Fri. Jan. 25, 2008 9:34 am
Location: upstate NY

Post by BIG BEAM » Mon. Sep. 15, 2008 9:43 pm

That pic freddy linked to should be the "standard" we use here.One more thing some water weaters have their PRV on the top of the tank that is where you should connect the hot from the coil.Either location will work fine.

The reason I think that link should be the standard is because must of us on this forum are here to build systems that work at as low a cost as posible and still work well. KISS
After all we're all here because ...well we're cheap,I know I am.Maybe thrifty is a better word but that's not what my wife calls me.

One more thing .The tank doesn't HAVE to be elevated it will work better that way but is not mandatory.If the tank and boiler were both on the floor the thermosipon will most likely produce 1/3 -1/2 gals /min(3/4" pipe).In a 40 gal. tank thats 1.5 hrs.for a full tank and that's faster that electric.
DON

 
User avatar
Freddy
Member
Posts: 7301
Joined: Fri. Apr. 11, 2008 2:54 pm
Location: Orrington, Maine
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Coal Size/Type: Pea size, Superior, deep mined

Post by Freddy » Mon. Sep. 15, 2008 10:06 pm

BIG BEAM wrote:What will make the water go into the tank if the hot coming out of the coil is connected to the hot on the tank and a tap (hot water) is open?
The water pressure coming in from the cold. Connecting it to the hot is no different than connecting it to the PRV as far as water flow is concerened. Either way when it's thermo siphoning, it makes the loop, when the tap water is opened water comes in from cold and out the hot. While the tap is being used the coil has equal pressure on both ends and the water in the coil does not move. (Unless you use Richards swing check to force it through the coil.)

Yup, the diagram in that link is a beauty, nice & simple & will work well.

I do like the idea of a second PRV very near the stove. When I first had my home made coil in my woodstove it had too much coil. The water would turn to steam and instantly collapse back below 220*. It would hammer! Ba-bang! I shortened my coil and had no issue after that, but I'll bet a PRV at the coil would have released a tiny bit of pressure and stopped the hammer.

 
BIG BEAM
Member
Posts: 712
Joined: Fri. Jan. 25, 2008 9:34 am
Location: upstate NY

Post by BIG BEAM » Mon. Sep. 15, 2008 10:17 pm

Not with that check valve system.The cold water goes to the coil first,gets heated,comes out the coil hot then gets tied into the hot on top of the tank.It won't go into the tank because if the hot water tap is open it will go right into the hot water line.So the hot water isn't coming from the tank it's coming from the coil.I'm not talking about the thermosipon part of the system I'm talking obout when you draw hot water.
DON

 
BIG BEAM
Member
Posts: 712
Joined: Fri. Jan. 25, 2008 9:34 am
Location: upstate NY

Post by BIG BEAM » Mon. Sep. 15, 2008 10:25 pm

I forgot
The coil I made for my wood stove did that hammer thing too.I had 10.5 ' of coil in my stove.That hammering just got things going.LOL Never hurt anything so I left it.
DON

Hey Freddy aint you supposed to be installing a boiler?How's it going?


 
User avatar
ceccil
Member
Posts: 1062
Joined: Sat. Mar. 15, 2008 11:33 pm
Location: Elmira, NY

Post by ceccil » Tue. Sep. 16, 2008 1:42 am

Ok, here we go. Can we agree this diagram will work? Still going to keep the 2nd PRV. I just like the added security, just in case. Should I just do away with the check valves? I'm still going to hold off on the mixing valve until I see how hot it gets. Draining the tank was a pain. Was going to drain it into sump pit but pump wouldn't work. Had to drain entire 40gal. into 2gal. buckets and carry over to washing machine to dump. Gotta get that pump fixed!!

Jeff

Attachments

Coil.jpg
.JPG | 16.7KB | Coil.jpg

 
User avatar
traderfjp
Member
Posts: 1801
Joined: Wed. Apr. 19, 2006 10:32 pm
Location: New York

Post by traderfjp » Tue. Sep. 16, 2008 6:47 am

I was going to plumb mine exactly as you have illustrated. I was told it would siphon but very slowly. I have no idea though.

 
User avatar
Adamiscold
Member
Posts: 1116
Joined: Fri. Feb. 29, 2008 7:09 am
Location: Winchendon,Ma

Post by Adamiscold » Tue. Sep. 16, 2008 6:48 am

BIG BEAM wrote:Not with that check valve system.The cold water goes to the coil first,gets heated,comes out the coil hot then gets tied into the hot on top of the tank.It won't go into the tank because if the hot water tap is open it will go right into the hot water line.So the hot water isn't coming from the tank it's coming from the coil.I'm not talking about the thermosiphon part of the system I'm talking about when you draw hot water.
DON
Since both hot water pipes (coil hot water and DHW feeds) are not connected inside the tank then some amount of mixing has to be going on. Wouldn't the amount of mixing be totally dependent on where the two hot water pipes end inside the tank? If the coil pipe ends right at the top of the tank and the DHW pipe starts in the middle of the tank then wouldn't that determine the amount of the mix? Check valve or not the water whether the tap is on or not is still going in the same direction.

Jeff,
You shouldn't need a mixing valve between the stove and the hot water tank, but you should already have one setup between the hot water tank and the feed to the house.

 
User avatar
Adamiscold
Member
Posts: 1116
Joined: Fri. Feb. 29, 2008 7:09 am
Location: Winchendon,Ma

Post by Adamiscold » Tue. Sep. 16, 2008 7:55 am

Freddy,

Love the diagram, and agree it should be standard for people to see how things are done since it points everything out very clearly.

 
BIG BEAM
Member
Posts: 712
Joined: Fri. Jan. 25, 2008 9:34 am
Location: upstate NY

Post by BIG BEAM » Tue. Sep. 16, 2008 9:19 am

ceccill,
That's the way I would do it if it were my house.That's the way I did it 25 yrs.ago and it worked VERY well in a wood stove.
DON

Sorry,forget the check valves they're not needed.Rember to pitch the lines to and from the coil like you would a drain line at least.The more you pitch the lines the FASTER the system will work.
I bet by about now you're getting great at soldering :D
Last edited by BIG BEAM on Tue. Sep. 16, 2008 9:35 am, edited 1 time in total.

 
User avatar
Richard S.
Mayor
Posts: 15242
Joined: Fri. Oct. 01, 2004 8:35 pm
Location: NEPA
Stoker Coal Boiler: Van Wert VA1200
Coal Size/Type: Buckwheat/Anthracite

Post by Richard S. » Tue. Sep. 16, 2008 9:35 am

Don, I'll ask again why not send it through the coil first? Why use electric or gas to heat water when you're going to have excessive unused heat the coil can generate? In that setup you're only utilizing the thermo siphon action to heat the water. One other benefit I'll add to my setup is you have practically unlimited hot water. If you're using hot water it's all going through the coil first, if you deplete the volume of hot water in the hot water tank it's still hot because it went through the coil... :idea:

 
BIG BEAM
Member
Posts: 712
Joined: Fri. Jan. 25, 2008 9:34 am
Location: upstate NY

Post by BIG BEAM » Tue. Sep. 16, 2008 9:47 am

Richard,
I agree that system would be ideal.Much more so in a boiler than a stove.I just can't get my brain around it.I sat here last night drawing pictures and refering to you posts and I still can't see how the gravity part of the system works.I'm not saying it doesn't work but,with the simple science of your system I can't seem to figure it out.
DON

 
User avatar
LsFarm
Member
Posts: 7383
Joined: Sun. Nov. 20, 2005 8:02 pm
Location: Michigan
Stoker Coal Boiler: Axeman Anderson 260
Hand Fed Coal Boiler: Self-built 'Big Bertha' SS Boiler
Baseburners & Antiques: Keystone 11, Art Garland

Post by LsFarm » Tue. Sep. 16, 2008 11:59 am

Everyone need to remember that the simple 'U' coil in a stove is NOT the same as an 'instant hot water coil' in a boiler.. The long, finned 'instant' hot water coil in a boiler will raise 50* water to 140* water at the rate of about 5-10 gallons a minute, if the boiler is at 160-180*.

The HilKoil 'coil' in a stoker stove will barely raise 50* water to 70* water if you are running the water from the street through the 'coil' to the sink. These Hikoil 'coils' are meant to slowly heat a 40-50 gallon tank of water to 140*+ overnight or during the day,, over an 8 hour or more period of time..

This is why a thermosiphon system works,, it is slow, but steady, and will keep a tank of water hot or heat a tank of water 'for free' overnight.

I would never run well or street temperature water through a Hilkoil 'coil' in a stoker stove.. use the coil as an auxilary heater for your HWH. Or best, add a tempering tank prior to the cold water inlet to the HWH, and use the 'coil' to heat the tempering tank.. this way the HWH never gets street or well temperature water,,

Any way you plan on plumbing it, the small, in-stove coils do not turn the stove into a boiler,, there is just way too little heated surface.. I think SteveN told us that a HilKoil 'coil' was good for about 5K BTU per hour.. not a lot. [ my memory may be off on this number, but it was a small number]

Hook it up as a simple thermosiphon, if you are not happy, install a small circulator in the loop. Either way you are storing heated water for your morning showers, and afternoon/evening laundry... [at least that is how it would be in my household].

Greg L