Help on Plumbing for Thermosiphon

Modern and vintage hand fired coal stove are similar to a wood stove and in some cases can burn either. They need to be regulated and fed by hand usually every 12 to 24 hours depending on your usage. They require no power to operate making them ideal for rural settings with long power outages.
User avatar
ceccil
Member
Posts: 1062
Joined: Sat. Mar. 15, 2008 11:33 pm
Stove/Furnace Make: Keystoker, Harman
Stove/Furnace Model: 90K, Mark III
Location: Elmira, NY

Post Sat. Sep. 13, 2008 11:49 pm

Got coil installed and had some questions on plumbing. I'm running my water out of the drain on the tank into the bottom side of the coil. I plan on raising the tank using blocks. The outlet on the tank will still be about 2" lower than the inlet on the coil. Is this acceptable? I'm also installing a 2nd PRV (one on the tank and one between outlet of coil and inlet on the tank) and going to tie them into each other down the line and vent to the outside. Last question I have is, if I start making to much heat can this be dumped using one of the finned baseboard units using the thermo method or is this only an option using a pump? Any other suggestions or comments? Let e'm fly. Thanks.

Jeff
Attachments
DSC00001.JPG
Coil installed
DSC00003.JPG
start of dry fitting
Jeff
Loyalty to the country always. Loyalty to the government when it deserves it. - Mark Twain

Visit Hitzer Stoves

User avatar
Freddy
Member
Posts: 6606
Joined: Fri. Apr. 11, 2008 2:54 pm
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Hot Air Coal Stoker Stove: Reading piece o' junk in the barn (rice)
Coal Size/Type: Pea size, Superior, deep mined
Location: Orrington, Maine

Post Sun. Sep. 14, 2008 6:11 am

No need to raise the tank. As long as it's within 10 feet (which it is) and on the same level it''ll thermo just fine. What you're doing looks good so far. Make sure that there are no valves between the PRV's and the pipes or tanks (looks like you're good so far). If all valves are shut off, the PRV's must still work. I think you may plumb the PRV's together and out.I don't think code talk about two PRVs together. Again, no valves. I might plumb them seperatly, and do it with as few elbows and as short a run as you can. The idea is to make it an easy path to blow off.

The overheat... I wouldn't worry about it. From what I've read they are designed well and rarely give a problem. If it does, then cross that bridge. I'm not sure how you'd make a dump zone. If you made a thermo siphon one, it would be hot all the time, not just when it overheats. If you put a pump on it, you'd need an aquastat. Kinda complicated for something that'll probably never get used. Maybe someone else has better words for a dump zone.
Orrington, Maine
Fred

"If you can't say something nice, don't say anything at all".

CoaLen
Member
Posts: 565
Joined: Wed. Apr. 09, 2008 7:05 am
Hot Air Coal Stoker Furnace: Keystoker Koker
Coal Size/Type: rice
Location: Northeast Ohio

Post Sun. Sep. 14, 2008 8:14 am

I had some of these same questions and this thread may be of some help to you:

Thermosiphon Question for Coil

-Len
“The trouble with quotes on the Internet is you never know if they are genuine.” —Abraham Lincoln

BIG BEAM
Member
Posts: 714
Joined: Fri. Jan. 25, 2008 9:34 am
Stove/Furnace Make: USS Hot blast
Stove/Furnace Model: 1557M
Location: upstate NY

Post Sun. Sep. 14, 2008 8:55 am

Looks good.I don't think you'll have to worry about a dump zone.You're using a gas water heater and should have ample heat loss(stand by loss) up the chimney.Try it without insul on the siphon lines if you need or want more hot water insulate them.
DON

One more thing the top line off your coil(hot) should be hooked to your hot line on the water heater pitching up slightly.The bottom off your coil (cold) should be pitching slightly down toward the tank.

Here I go again.Don't keep that boiler drain upside down on the tank. The line will fill up with lime and crud.

User avatar
ceccil
Member
Posts: 1062
Joined: Sat. Mar. 15, 2008 11:33 pm
Stove/Furnace Make: Keystoker, Harman
Stove/Furnace Model: 90K, Mark III
Location: Elmira, NY

Post Sun. Sep. 14, 2008 10:43 am

Looks like i'm doing ok so far then. The tank is going to stay about where it sits now. It's going to be plumbed like the drawing below that traderflp drew up. The only thing different will be the drain, and another PRV in line between coil and tank.
Attachments
boiler2.jpg
Jeff
Loyalty to the country always. Loyalty to the government when it deserves it. - Mark Twain

User avatar
Freddy
Member
Posts: 6606
Joined: Fri. Apr. 11, 2008 2:54 pm
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Hot Air Coal Stoker Stove: Reading piece o' junk in the barn (rice)
Coal Size/Type: Pea size, Superior, deep mined
Location: Orrington, Maine

Post Sun. Sep. 14, 2008 1:59 pm

That diagram isn't going to work.... the top of the coil need to go to the top of the tank. The bottom of the coil needs to go to the bottom of the tank. I see no need for a swing check, but one wouldn't hurt. I didn't put the drain(s) or valves in the sketch.

One other thing.... You'll probably want to have a mixing valve so water coming from the tank to your domestic use is not too hot. If you get the water up to 170 or 180 degrees in the tank you'll be taking skin off in the shower.

I don't think it's make a big difference if the cold water coming in goes through the coil first or directly to the tank. When you turn on a faucet the water wouldn't be in the coil for more than a couple of seconds.
Attachments
SIPHON.jpg
Orrington, Maine
Fred

"If you can't say something nice, don't say anything at all".

BIG BEAM
Member
Posts: 714
Joined: Fri. Jan. 25, 2008 9:34 am
Stove/Furnace Make: USS Hot blast
Stove/Furnace Model: 1557M
Location: upstate NY

Post Sun. Sep. 14, 2008 3:39 pm

Shouldn't the hot from the coil go to the hot on the tank?
I've never hooked a coil to a regular tank just to a range boiler.They have separate tappings for a coil.

User avatar
Freddy
Member
Posts: 6606
Joined: Fri. Apr. 11, 2008 2:54 pm
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Hot Air Coal Stoker Stove: Reading piece o' junk in the barn (rice)
Coal Size/Type: Pea size, Superior, deep mined
Location: Orrington, Maine

Post Sun. Sep. 14, 2008 4:39 pm

Yup, good point, and that's why the check valve is needed!
Attachments
SIPHON.jpg
Orrington, Maine
Fred

"If you can't say something nice, don't say anything at all".

Visit Hitzer Stoves

User avatar
traderfjp
Member
Posts: 1799
Joined: Wed. Apr. 19, 2006 10:32 pm
Stove/Furnace Make: Alaska
Stove/Furnace Model: Channing 3
Location: New York

Post Sun. Sep. 14, 2008 6:20 pm

The drawing I made above was to help me sort out the thermosiphon sketch that Richard posted. In the end, I decided to use a small circulator. Here is a pic of the coil. You can see the relief valve which is to the right of the valve on the coil. I think I need to add a PRV on the coil too. Not sure.
Attachments
coil.jpg
Disclaimer: I'm not an expert in any coal or plumbing related field. I only post my own experiences, research and common sense. If you choose to use any of the information in this post or any other post you do so at your own risk.

User avatar
ceccil
Member
Posts: 1062
Joined: Sat. Mar. 15, 2008 11:33 pm
Stove/Furnace Make: Keystoker, Harman
Stove/Furnace Model: 90K, Mark III
Location: Elmira, NY

Post Sun. Sep. 14, 2008 9:21 pm

Please tell me this will work!! I worked on this a good part of the day and it's how I have it plumbed. Also found out just how much to tighten down the pex fitting on top of the tank (about a 1/2 lb less than I tightened it) cracked the fitting :mad: and had to run all the way back up to Lowes to get another. Got all done, filled system and bled air. No leaks as of now. Thanks to all for your input. Makes life easier. I didn't add a mixing valve as of yet. Talked to a few people about my setup and they say it may not get as hot because the coil is off to the side of the grate instead of being over top. Also going to leave pipes uninsulated. Will see how hot it gets. Will add mixer later if needed.

Jeff
Attachments
Coil.jpg
DSC00001.JPG
DSC00003.JPG
DSC00004.JPG
Jeff
Loyalty to the country always. Loyalty to the government when it deserves it. - Mark Twain

User avatar
Razzler
Member
Posts: 434
Joined: Wed. Dec. 19, 2007 7:56 pm
Stoker Coal Boiler: EFM DF520
Coal Size/Type: rice
Location: Northampton Pa.

Post Sun. Sep. 14, 2008 10:23 pm

ceccil, A swing check valve will only works in the vertical position if the water is running up-wards. :what:

User avatar
ceccil
Member
Posts: 1062
Joined: Sat. Mar. 15, 2008 11:33 pm
Stove/Furnace Make: Keystoker, Harman
Stove/Furnace Model: 90K, Mark III
Location: Elmira, NY

Post Mon. Sep. 15, 2008 12:21 am

Very good point :oops: Don't know why I didn't realize that. The bottom one is flowing in the right direction but using thermo the water probobly isn't moving fast enough to open it. Well, back at it tomorrow. Thanks.

Jeff
Jeff
Loyalty to the country always. Loyalty to the government when it deserves it. - Mark Twain

User avatar
Freddy
Member
Posts: 6606
Joined: Fri. Apr. 11, 2008 2:54 pm
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Hot Air Coal Stoker Stove: Reading piece o' junk in the barn (rice)
Coal Size/Type: Pea size, Superior, deep mined
Location: Orrington, Maine

Post Mon. Sep. 15, 2008 6:29 am

You mayhave made the mistake I made in my first sketch. The hot from the coil shold go to the hot of the tank. The reason is that the cold from the tank has an internal pipe that goes to the bottom of the tank. With the hot from the coil going to the cold of the tank it will not "turn the water over" in the tank. It will tend to just make a mini circle at the bottom.

I'm not sure if a swing check will work vertical on the other pipe either unless it's pumped. Horizonal will work fine.
Orrington, Maine
Fred

"If you can't say something nice, don't say anything at all".

BIG BEAM
Member
Posts: 714
Joined: Fri. Jan. 25, 2008 9:34 am
Stove/Furnace Make: USS Hot blast
Stove/Furnace Model: 1557M
Location: upstate NY

Post Mon. Sep. 15, 2008 7:51 pm

I would have left the hot and cold water lines hooked up to the tank the way it was with a mixing valve of coarse.What you did on the bottom of the tank was fine(connecting the bottom of the tank to the coil like it is)I would connect the hot(top) of the coil to the relief valve port and put the relief valve in the run of the tee right next to the tank.This way the 1 relief valve would take care of both the coil and tank.Connect the bull of the tee in the relief valve port to the hot(top) side of the coil.No need for any check valves.But that's just me.
DON

BIG BEAM
Member
Posts: 714
Joined: Fri. Jan. 25, 2008 9:34 am
Stove/Furnace Make: USS Hot blast
Stove/Furnace Model: 1557M
Location: upstate NY

Post Mon. Sep. 15, 2008 8:04 pm

Freddy,
After thinking about this last night if you hook the hot from the coil to the hot on the tank when a tap is opened the hot from the coil will go right into the hot water line bypassing the tank.
If you hook it to the cold at the top of the tank I don't know if it will thermosphon because of the drip tube in the tank.
DON

Visit Hitzer Stoves

Post Reply