You guys finally convinced me

 
zachary193
Member
Posts: 269
Joined: Tue. Jun. 21, 2022 4:10 pm
Location: South Western Pennsylvania
Hand Fed Coal Boiler: Ds machine energy max 160
Hand Fed Coal Stove: Ds energy max 160
Coal Size/Type: Blaschak nut
Other Heating: Oil/electric

Post by zachary193 » Sun. Jan. 22, 2023 6:46 pm

Since burning coal in the ds energymax 160 for about 2 months and 2 tons of coal . I noticed the days with wind I use more coal and days without I use less . I convinced myself to order a barometric dampener and Tee . And also a Dwyer manometer . I may also include a MPD just incase . I did get a cap as well so I can take it out and burn wood . The manual from DS says adjust barometric from .06-.08 if one is installed .

I just can’t get the stove top up that high with coal . 450-500 is max . When you have the bi-metallic up that high the flames do roar pretty well . Stove pipe is in the 150-175 range that high . I think I can keep a good bit more heat in the stove .


Lately this batch of coal convinced me . I seem to get a good bit of clinkers and I’m not really burning the stove that hot . So I assume I’m loosing heat up the chimney.

Needless to say with a manometer I won’t be flying blind either .


Any tips on shut down ? Things I should check out .

I plan on burning the bed down pretty far and shaking what’s left out . Disassembling the stove pipe , cleaning the fly ash out . Adding in the barometric and manometer .


I purchased a kit from The coal shop up in New York last night at work . The manometer came with a probe and pretty much ready to set up .


I don’t see it being a very long process .


Any tips would be appreciated.
Thanks

Attachments

F1BA1EC1-F473-4858-B2FE-EE27866F27DB.jpeg
.JPEG | 670KB | F1BA1EC1-F473-4858-B2FE-EE27866F27DB.jpeg


 
User avatar
Lightning
Site Moderator
Posts: 14658
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Sun. Jan. 22, 2023 6:55 pm

What model barometric damper and manometer did you get?

.06-.08 is high.
.04-.05 is better.

 
User avatar
ShawnLiNy
Member
Posts: 618
Joined: Fri. Nov. 30, 2018 12:28 am
Hand Fed Coal Stove: Waterford
Coal Size/Type: Nut

Post by ShawnLiNy » Sun. Jan. 22, 2023 7:09 pm

I’m with Lee , start at .04 and go lower if you are getting the heat you want , I ran .04 for years because that’s in the manual ( but what I missed was ( NO HIGHER than .04 this year I’m at a shade under.03 pretty much the lowest I can go without removing the weight , the difference between.04 and .03 is several hours burn

 
zachary193
Member
Posts: 269
Joined: Tue. Jun. 21, 2022 4:10 pm
Location: South Western Pennsylvania
Hand Fed Coal Boiler: Ds machine energy max 160
Hand Fed Coal Stove: Ds energy max 160
Coal Size/Type: Blaschak nut
Other Heating: Oil/electric

Post by zachary193 » Sun. Jan. 22, 2023 7:09 pm

Lightning wrote:
Sun. Jan. 22, 2023 6:55 pm
What model barometric damper and manometer did you get?

.06-.08 is high.
.04-.05 is better.

Attachments

4F881951-5210-4868-86D0-BF217360566A.png
.PNG | 1.4MB | 4F881951-5210-4868-86D0-BF217360566A.png

 
zachary193
Member
Posts: 269
Joined: Tue. Jun. 21, 2022 4:10 pm
Location: South Western Pennsylvania
Hand Fed Coal Boiler: Ds machine energy max 160
Hand Fed Coal Stove: Ds energy max 160
Coal Size/Type: Blaschak nut
Other Heating: Oil/electric

Post by zachary193 » Sun. Jan. 22, 2023 7:13 pm

zachary193 wrote:
Sun. Jan. 22, 2023 7:09 pm
Here’s a better picture

Attachments

C59B6D6F-6A3C-4045-8842-5C3F3A728F63.png
.PNG | 2MB | C59B6D6F-6A3C-4045-8842-5C3F3A728F63.png

 
zachary193
Member
Posts: 269
Joined: Tue. Jun. 21, 2022 4:10 pm
Location: South Western Pennsylvania
Hand Fed Coal Boiler: Ds machine energy max 160
Hand Fed Coal Stove: Ds energy max 160
Coal Size/Type: Blaschak nut
Other Heating: Oil/electric

Post by zachary193 » Sun. Jan. 22, 2023 7:21 pm

ShawnLiNy wrote:
Sun. Jan. 22, 2023 7:09 pm
I’m with Lee , start at .04 and go lower if you are getting the heat you want , I ran .04 for years because that’s in the manual ( but what I missed was ( NO HIGHER than .04 this year I’m at a shade under.03 pretty much the lowest I can go without removing the weight , the difference between.04 and .03 is several hours burn
Well , also too I’m kind of flying blind . I know I have draft . I just don’t know how much yet. We’ll keep that in mind .

 
Hoytman
Member
Posts: 5990
Joined: Wed. Jan. 18, 2017 11:30 pm
Location: swOH near a little town where the homes are mobile and the cars aren’t
Hand Fed Coal Stove: Hitzer 354
Coal Size/Type: nut coal
Other Heating: electric, wood, oil

Post by Hoytman » Sun. Jan. 22, 2023 7:57 pm

Check draft with manometer first for a baseline.

Install Manometer first and take reading before installing anything else.

Record it all on paper.

I wouldn’t be surprised if you’re already running lower than the manual states.


 
zachary193
Member
Posts: 269
Joined: Tue. Jun. 21, 2022 4:10 pm
Location: South Western Pennsylvania
Hand Fed Coal Boiler: Ds machine energy max 160
Hand Fed Coal Stove: Ds energy max 160
Coal Size/Type: Blaschak nut
Other Heating: Oil/electric

Post by zachary193 » Sun. Jan. 22, 2023 8:16 pm

Hoytman wrote:
Sun. Jan. 22, 2023 7:57 pm
Check draft with manometer first for a baseline.

Install Manometer first and take reading before installing anything else.

Record it all on paper.

I wouldn’t be surprised if you’re already running lower than the manual states.

Any suggestions on how to do this without shutting the stove down twice ? I would have to drill a hole to Insert the manometer probe . I’m trying to avoid tearing down 2 times . Or could I check this at the stove , through the gap around the shaker handle ?

 
Hoytman
Member
Posts: 5990
Joined: Wed. Jan. 18, 2017 11:30 pm
Location: swOH near a little town where the homes are mobile and the cars aren’t
Hand Fed Coal Stove: Hitzer 354
Coal Size/Type: nut coal
Other Heating: electric, wood, oil

Post by Hoytman » Sun. Jan. 22, 2023 8:31 pm

I doubt you have a gap big enough to fit the probe or copper tubing. You can install on the stove pipe, on the load door, or on the ash pan door and likely won’t see a lot of difference in your readings. The door installs will require a set screw. Me…I didn’t want to drill my stove so I went with the stove pipe install.

Here’s a thread I made when I installed my manometer. I’m pretty sure I detailed the entire install with pictures and maybe even links to the supplies I used. I elected to not install fittings in my stove pipe. I just drilled a hole for a stove pipe screw and my copper line slides right in. If I want to take it out I just remove it and use a stove pipe screw to close the hole.

Manometer install parts list
Last edited by Hoytman on Sun. Jan. 22, 2023 9:44 pm, edited 2 times in total.

 
fig
Member
Posts: 1137
Joined: Fri. Feb. 12, 2016 2:36 pm
Hand Fed Coal Boiler: Harman SF360
Hand Fed Coal Stove: T.O.M (Warm Morning converted to baseburner by Steve) Round Oak 1917 Door model O-3, Warm Morning 400, Warm Morning 524, Warm Morning 414,Florence No.77, Warm Morning 523-b
Hand Fed Coal Furnace: Clayton 7.1/DS Machine basement stove/ Harman SF1500
Baseburners & Antiques: Renown Parlor stove 87B
Coal Size/Type: Bituminous/anthracite
Other Heating: Harman Accentra, enviro omega, Vermont Ironworks Elm stove, Quadrafire Mt Vernon, Logwood stove, Sotz barrel stove,

Post by fig » Sun. Jan. 22, 2023 8:44 pm

I just drilled a hole in the pipe with the stove going. Made sure the drill bit I used was only slightly larger than some brake line I had for a snug fit. Then slipped about 8” long piece of brake line into it. Attached the rubber hose that came with the mano to that and ran with it. Just had to keep the hose away from the stove.

 
zachary193
Member
Posts: 269
Joined: Tue. Jun. 21, 2022 4:10 pm
Location: South Western Pennsylvania
Hand Fed Coal Boiler: Ds machine energy max 160
Hand Fed Coal Stove: Ds energy max 160
Coal Size/Type: Blaschak nut
Other Heating: Oil/electric

Post by zachary193 » Sun. Jan. 22, 2023 8:50 pm

Hoytman wrote:
Sun. Jan. 22, 2023 8:31 pm
I doubt you have a gap big enough to fit the probe or copper tubing. You can install on the stove pipe, on the load door, or on the ash pan door and likely won’t see a lot of difference in your readings. The door installs will require a set screw. Me…I didn’t want to drill my stove so I went with the stove pipe install.

Here’s a thread I made when I installed my manometer. I’m pretty sure I detailed the entire install with pictures and maybe even links to the supplies I used. I elected to not install fittings in my stove pipe. I just drilled a hole for a stove pipe screw and my copper line slides right in. If I want to take it out I just remove it and use a stove pipe screw to close the hole.

Post by Hoytman - Manometer install parts list

The manometer I ordered already came with a 8” probe . I thought I had the photo in the above with the baro . Must not have loaded .

Attachments

CCFFA9B7-AC93-49EE-82DA-3ED6475EBE8F.png
.PNG | 2MB | CCFFA9B7-AC93-49EE-82DA-3ED6475EBE8F.png

 
User avatar
Sunny Boy
Member
Posts: 25547
Joined: Mon. Nov. 11, 2013 1:40 pm
Location: Central NY
Hand Fed Coal Boiler: Anthracite Industrial, domestic hot water heater
Baseburners & Antiques: Glenwood range 208, # 6 base heater, 2 Modern Oak 118.
Coal Size/Type: Nuts !
Other Heating: Oil &electric plenum furnace

Post by Sunny Boy » Sun. Jan. 22, 2023 9:07 pm

Must be a new thing for Dwyer. The Mark II kits I bought didn't come with a probe. Just the tubing and bottle of liquid. :cry:

Paul

 
Hoytman
Member
Posts: 5990
Joined: Wed. Jan. 18, 2017 11:30 pm
Location: swOH near a little town where the homes are mobile and the cars aren’t
Hand Fed Coal Stove: Hitzer 354
Coal Size/Type: nut coal
Other Heating: electric, wood, oil

Post by Hoytman » Sun. Jan. 22, 2023 9:07 pm

Mine never came with a probe. I wouldn’t have used it anyway and I also never used the red/gray hose.

You’ll see what I did in my thread. Just disregard all the other comments in that thread and only pay attention to my posts for what “I” did. Obviously, other folks installed theirs differently and that it ok too. I just felt my install was easiest for me.

 
Hoytman
Member
Posts: 5990
Joined: Wed. Jan. 18, 2017 11:30 pm
Location: swOH near a little town where the homes are mobile and the cars aren’t
Hand Fed Coal Stove: Hitzer 354
Coal Size/Type: nut coal
Other Heating: electric, wood, oil

Post by Hoytman » Sun. Jan. 22, 2023 9:33 pm

I edited the post above. The first posts I’m that thread show what I used to install my manometer.

No brake line for my style install and no brake line fittings. Copper line slips in and slips out of stove pipe. Stove pipe screw can be used to plug hole if you ever want to remove it all…make it look like it wasn’t even there.

Here is the correct link…
Manometer install parts list

 
zachary193
Member
Posts: 269
Joined: Tue. Jun. 21, 2022 4:10 pm
Location: South Western Pennsylvania
Hand Fed Coal Boiler: Ds machine energy max 160
Hand Fed Coal Stove: Ds energy max 160
Coal Size/Type: Blaschak nut
Other Heating: Oil/electric

Post by zachary193 » Mon. Jan. 23, 2023 1:36 am

fig wrote:
Sun. Jan. 22, 2023 8:44 pm
I just drilled a hole in the pipe with the stove going. Made sure the drill bit I used was only slightly larger than some brake line I had for a snug fit. Then slipped about 8” long piece of brake line into it. Attached the rubber hose that came with the mano to that and ran with it. Just had to keep the hose away from the stove.

Drilled with the stove running ? No sonic boom ?