I bought a house and it’s prinary heat is a Baker Fireside Coal Insert. Having a problem getting a long burn that doesn’t overheat. Had temps on the door overnight just above 200, but did a shack down and reloaded it this morning and within an hour the door temp was pushing 600. This is the second day since firing up the stove and had this problem on three reloads. I didn’t make any changes from the overnight settings, the fire draft from one full turn and the secondary air
7AAF57E2-AC52-4FF4-9001-C7F1F3DB4611.jpeg
600 door temp
three turns. Outside temp 40. Any advise appreciated.

Rob R.
Site Moderator
Posts: 12932
Joined: Fri. Dec. 28, 2007 4:26 pm
Stoker Coal Boiler: EFM DF520
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Lehigh Rice
Other Heating: Dad's 1953 EFM Highboy
Location: Chazy, NY

Post By: Rob R. » Wed. Oct. 17, 2018 8:30 am

Welcome.

Looks like you need more coal and less air. Make sure the firebox is FULL of coal, and close the secondary air until it is barely cracked open.

Is there any kind of damper in the flue pipe?

DKBakerPA
New Member
Posts: 3
Joined: Wed. Oct. 17, 2018 7:34 am
Hand Fed Coal Stove: Baker Fireside Coal Insert
Coal Size/Type: Nut Coal

Post By: DKBakerPA » Wed. Oct. 17, 2018 8:34 am

So, add more coal and cut back on secondary air? I barely have any fire air draft, only 1/4 turn right now. Is that alright?

User avatar
McGiever
Member
Posts: 7129
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: RICE,PEA,NUT,STOVE /ANTHRACITE and EGG / BIT
Other Heating: Ground Source Heat Pump and some Solar
Location: Junction of PA-OH-WV

Post By: McGiever » Wed. Oct. 17, 2018 9:09 am

Dollar Bill test those door gaskets. With air leaks you lose finer fire control. Good Ash door seal is real important.

Air control is only way to thottle back a fire.
With anthracite it is the "under fire air" that counts the most for ultimate control. But, don't ignore those other air leaks.

Visit Hitzer Stoves

User avatar
Lightning
Member
Posts: 10011
Joined: Wed. Nov. 16, 2011 9:51 am
Hand Fed Coal Furnace: Overmodified/Bored out Clayton 1537
Coal Size/Type: Nut/Stove Size Mix
Location: Olean, NY

Post By: Lightning » Wed. Oct. 17, 2018 9:39 am

Rob asked if you have any sort of dampers on the stove pipe. A yo-yoing of heat output is usually indicative of fluctuating draft pressure. Does this stove have any sort of thermostat control on it? Look for a dial with a chain that moves a flap open and closed for regulating under fire air (primary combustion air).

DKBakerPA
New Member
Posts: 3
Joined: Wed. Oct. 17, 2018 7:34 am
Hand Fed Coal Stove: Baker Fireside Coal Insert
Coal Size/Type: Nut Coal

Post By: DKBakerPA » Wed. Oct. 17, 2018 9:48 am

Being it’s an insert, I have no flue control in the chimney or thermostat control. I will check the door seals again. Currently loaded with more coal, cut secondary air knobs to two turns and bottom air to 1/4 turn each. I have a hot bed of coals but no flames and the door temp is 300.

User avatar
Lightning
Member
Posts: 10011
Joined: Wed. Nov. 16, 2011 9:51 am
Hand Fed Coal Furnace: Overmodified/Bored out Clayton 1537
Coal Size/Type: Nut/Stove Size Mix
Location: Olean, NY

Post By: Lightning » Wed. Oct. 17, 2018 10:11 am

You could have conditions ripe for a puff back right now if there is no hot coals exposed. Open the secondary air controls wide open until the blue flames appear over the coal bed. You may also wanna have the ash door cracked open until that happens.