Options for my stove pipe clearance??

 
Coal country
Member
Posts: 86
Joined: Sat. Oct. 08, 2016 6:53 pm
Hand Fed Coal Stove: Gibraltar lcc

Post by Coal country » Sun. Oct. 14, 2018 10:07 pm

So with how low my basement ceiling is I only have about 7 inches from old beams of my first floor to the stove pipe on my stove it's a gibralter lcc with 8inch stove pipe I think it's around 120k btu. What are my options here will a heat shield work what's the best material to use.. looks are not important it's it an old 5ft dirt floor basement. Also could I potientionally buy or make a double heat shield for better results.. I'll try to attach a picture.

Attachments

20181014_205853.jpg
.JPG | 290.9KB | 20181014_205853.jpg
20181014_205905.jpg
.JPG | 237.5KB | 20181014_205905.jpg


 
User avatar
oliver power
Member
Posts: 2970
Joined: Sun. Apr. 16, 2006 9:28 am
Location: Near Dansville, NY
Stoker Coal Boiler: KEYSTOKER Kaa-2
Hand Fed Coal Stove: Hitzer 50-93 & 30-95, Vigilant (pre-2310), D.S. 1600 Circulator, Hitzer 254

Post by oliver power » Sun. Oct. 14, 2018 11:02 pm

Wrap the pipe with insulation. Use double heat shield. Take a piece of rectangular duct work, and run it from the floor up, and over the top of stove pipe. Leave a gap at the bottom for cooler air to enter. Hang a cheap aluminum basting pan over the stove pipe. Put a little water in it. Lots of options..........

 
NoSmoke
Member
Posts: 1442
Joined: Sun. Oct. 14, 2012 7:52 pm
Location: Mid Coast Maine
Hand Fed Coal Boiler: New Yoker WC90
Baseburners & Antiques: Woods and Bishop Antique Pot Bellied Stove
Coal Size/Type: Stove/Nut/Pea Anthracite
Other Heating: Munchkin LP Boiler/Englander Pellet Stove/Perkins 4.108 Cogeneration diesel

Post by NoSmoke » Mon. Oct. 15, 2018 7:41 am

I would just buy a couple of glass electric fence insulators which can be still bought at farm supply centers, then use a piece of steel roofing and put long screws through the tin, through the glass insulators, and then into the beams. That would allow for a 1 inch or so stand-off from the wooden beams and allow air to flow all around the chimney pipe. You would be amazed at how cool it is on the other side.

But that is just how I would do it...as others have said, a lot of options.

 
User avatar
freetown fred
Member
Posts: 30293
Joined: Thu. Dec. 31, 2009 12:33 pm
Location: Freetown,NY 13803
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut

Post by freetown fred » Mon. Oct. 15, 2018 7:57 am

Orrrrrrr, a piece of crete board (2'X4')??? with fence insulators.

 
Coal country
Member
Posts: 86
Joined: Sat. Oct. 08, 2016 6:53 pm
Hand Fed Coal Stove: Gibraltar lcc

Post by Coal country » Mon. Oct. 15, 2018 8:09 am

Thanks guys I didnt think about the fence insulators that's a good idea my father has leftover tin metal from his pole barn to so as long as that would suffeicentlly block the heat it shouldn't be much of a project

 
User avatar
Lightning
Site Moderator
Posts: 14658
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Mon. Oct. 15, 2018 8:13 am

I would just hang some tin over it, keep air spaces above and below. Check it frequently to see if anything is getting hot until you are confident it's safe.

 
User avatar
Rob R.
Site Moderator
Posts: 17977
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Mon. Oct. 15, 2018 8:15 am

NoSmoke wrote:
Mon. Oct. 15, 2018 7:41 am
I would just buy a couple of glass electric fence insulators which can be still bought at farm supply centers, then use a piece of steel roofing and put long screws through the tin, through the glass insulators, and then into the beams. That would allow for a 1 inch or so stand-off from the wooden beams and allow air to flow all around the chimney pipe. You would be amazed at how cool it is on the other side.

But that is just how I would do it...as others have said, a lot of options.
x2. I have done this and it works very well. As Fred mentioned, some cement board would work well also.


 
Coal country
Member
Posts: 86
Joined: Sat. Oct. 08, 2016 6:53 pm
Hand Fed Coal Stove: Gibraltar lcc

Post by Coal country » Mon. Oct. 15, 2018 11:55 am

I may be going overboard but I have the sheet metal would it be worth while to fasten two together with 1/2 dia pipe that are 1\2 long and run a bolt with nut and washers to make a double shield with 1\2 inch space between them and and 1" space from the beams would doubling the sheets make a noticeable gain in heat shielding or is there something I'm missing in the logic. I may be being extra cautious but the 6 inch or so gap from extremely hot stove pipe to 100 year old dried hemlock beams has me pretty nervous

 
Coal country
Member
Posts: 86
Joined: Sat. Oct. 08, 2016 6:53 pm
Hand Fed Coal Stove: Gibraltar lcc

Post by Coal country » Mon. Oct. 15, 2018 11:57 am

Also on not the metal roofing/ siding I have is painted would that be an issue as in would the paint be considered combustible

 
CapeCoaler
Member
Posts: 6515
Joined: Sun. Feb. 10, 2008 3:48 pm
Location: Cape Cod, MA
Stoker Coal Boiler: want AA130
Hand Fed Coal Stove: DS Machine BS#4, Harman MKII, Hitzer 503,...
Coal Size/Type: Pea/Nut/Stove

Post by CapeCoaler » Mon. Oct. 15, 2018 12:09 pm

Double heat shield is better...
Silver or bare metal towards stove...
Dark colors black, red, green will absorb heat and transfer to next layer...
If you can make it 12-24 inches wider than the stove all the way around..
Radiant and convective heat will dry those beans out fast...
How far is the top of stove to those beams?...

 
Coal country
Member
Posts: 86
Joined: Sat. Oct. 08, 2016 6:53 pm
Hand Fed Coal Stove: Gibraltar lcc

Post by Coal country » Mon. Oct. 15, 2018 4:06 pm

It's about 7 inch from that beam

 
User avatar
freetown fred
Member
Posts: 30293
Joined: Thu. Dec. 31, 2009 12:33 pm
Location: Freetown,NY 13803
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut

Post by freetown fred » Mon. Oct. 15, 2018 4:45 pm

Then---any of the above suggestions will work well---KISS C

 
CapeCoaler
Member
Posts: 6515
Joined: Sun. Feb. 10, 2008 3:48 pm
Location: Cape Cod, MA
Stoker Coal Boiler: want AA130
Hand Fed Coal Stove: DS Machine BS#4, Harman MKII, Hitzer 503,...
Coal Size/Type: Pea/Nut/Stove

Post by CapeCoaler » Mon. Oct. 15, 2018 7:55 pm

The actual stove not the pipe...
if it is just a 5 foot dirt floor basement...
Then the top of the stove might be only 30 inches to the beam...
And you will nee a heat shield to protect the beams from the stove too...
Continuous heat soaking from the stove will lower the combustion point of the beams...

 
archangel_cpj
Member
Posts: 214
Joined: Sat. Dec. 06, 2008 10:51 pm

Post by archangel_cpj » Mon. Oct. 15, 2018 11:36 pm

Best stuff I've used is the corregated galvanized steel sheeting from Home depot its 12 bucks for an 8 foot long by 2ftish wide piece and it reflects heat nicely... my set up is the wall a 1.25 in air gap and the silver corrugated steel... The metal is cold to the touch while pipe is pretty near 200 degrees...

Attachments

20181015_233333.jpg
.JPG | 248KB | 20181015_233333.jpg

 
Coal country
Member
Posts: 86
Joined: Sat. Oct. 08, 2016 6:53 pm
Hand Fed Coal Stove: Gibraltar lcc

Post by Coal country » Tue. Oct. 16, 2018 8:03 am

Hey thanks for the picture of one in use... and I checked the stove to beam is 34 inch but while I'm making it I had planned to make it long enough to cover everything


Post Reply

Return to “Hand Fired Coal Stoves & Furnaces Using Anthracite”