Hilkoil to heat exchanger info needed

 
urhstry
Member
Posts: 44
Joined: Wed. Nov. 04, 2015 4:27 pm
Location: Elysburg, PA
Stoker Coal Boiler: Harman Verti-flow
Hand Fed Coal Boiler: Harman Mark III
Coal Size/Type: pea and nut
Other Heating: OWB

Post by urhstry » Tue. Aug. 28, 2018 9:32 am

I am going to put a Hilkoil in my Harman Magnum and just need it to run about twelve feet to a new heat exchanger (with fan). My question is will I need a relief valve inline or anything else? This is for a garage setup and I do not want a tank inline. Thanks!


 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Tue. Aug. 28, 2018 9:39 am

yes, releif valve required as always on closed loop system...very dangerous w/o releif if fan, pump or power were to fail.

 
urhstry
Member
Posts: 44
Joined: Wed. Nov. 04, 2015 4:27 pm
Location: Elysburg, PA
Stoker Coal Boiler: Harman Verti-flow
Hand Fed Coal Boiler: Harman Mark III
Coal Size/Type: pea and nut
Other Heating: OWB

Post by urhstry » Tue. Aug. 28, 2018 9:50 am

Can you suggest a valve for this project?

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Tue. Aug. 28, 2018 10:02 am

urhstry wrote:
Tue. Aug. 28, 2018 9:50 am
Can you suggest a valve for this project?
I'll direct you to Hilkoil for that...they list their's there.

 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Tue. Aug. 28, 2018 3:02 pm

How big is the coil? I don't wanna rain on anyone's parade but those coils don't pick up very much heat. I'd be surprised if they will transfer more than a 1500 BTUs per hour.

 
urhstry
Member
Posts: 44
Joined: Wed. Nov. 04, 2015 4:27 pm
Location: Elysburg, PA
Stoker Coal Boiler: Harman Verti-flow
Hand Fed Coal Boiler: Harman Mark III
Coal Size/Type: pea and nut
Other Heating: OWB

Post by urhstry » Tue. Aug. 28, 2018 3:08 pm

I would most likely be going with the 18" U coil.

 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Tue. Aug. 28, 2018 3:23 pm

Hmmm. I use two 24 inch U shaped coils in my hand fed. One preheats domestic hot water, the other keeps my outside hot tub warm all winter.

It takes about 12 hours to lift my 40 gallon temper tank roughly 50 degrees during a high burn. So,

40 × 8.34 = 334 BTU/degree

334 × 50 degrees = 16,700

16,700 ÷ 12 hours = 1391

So if I did that right, one 24 inch coil at a high burn absorbs only 1391 BTUs per hour. That's not very much. There's just not enough surface area around a coil to absorb heat to make it do what your wanting. You'll need a lot more than that to heat a garage.

That's my view on it, with my experience on water coils. Your mileage may vary.


 
urhstry
Member
Posts: 44
Joined: Wed. Nov. 04, 2015 4:27 pm
Location: Elysburg, PA
Stoker Coal Boiler: Harman Verti-flow
Hand Fed Coal Boiler: Harman Mark III
Coal Size/Type: pea and nut
Other Heating: OWB

Post by urhstry » Tue. Aug. 28, 2018 3:35 pm

Interesting.... so in order for my project to work I would neeed a bigger coil AND a water tank, correct?

 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Tue. Aug. 28, 2018 4:56 pm

Well, you are attempting to make your hot air/convection unit act like a boiler. This subject has come up before and as one forum member once said, "a stove can't even play a boiler on TV" lol. But yes, you are right. Although it would take a significant network of many coils inside the fire chamber of a hand fed or stoker fed furnace to have enough surface area to absorb the amount of heat you need to heat a garage. Even if you used the one coil and heated a tank, then used that stored heat to heat your garage, the tank of water would go cold rather quickly and it would need a huge amount of time (like a full day) to recover so that your could heat the garage for two hours again. It's all about heat transfer at the source of heat. The water circles back to the coil which can't absorb heat fast enough for the demand needed.

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Tue. Aug. 28, 2018 5:10 pm

urhstry wrote:
Tue. Aug. 28, 2018 3:35 pm
Interesting.... so in order for my project to work I would neeed a bigger coil AND a water tank, correct?
No, what you really need is a boiler. There is no way for a small coil in a stove to absorb enough heat to power house sized a water to air heat exchanger. There is just not enough surface area. Sounds like you are trying to reinvent the wheel when it was already perfected 100 years ago.

Used coal boilers can be fairly cheap because, unlike a stove, they are not easy to move.

-Don

 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Tue. Aug. 28, 2018 6:33 pm

Mr. Don is right. Just to put things in perspective, you would want at least 30,000 BTUs per hour on hand (during really cold weather) for your garage. And 30,000 is probably a conservative figure.

 
franco b
Site Moderator
Posts: 11416
Joined: Wed. Nov. 05, 2008 5:11 pm
Location: Kent CT
Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
Baseburners & Antiques: Glenwood Modern Oak 114
Coal Size/Type: nut and pea

Post by franco b » Wed. Aug. 29, 2018 8:24 pm

I would suggest trying a 5000 BTU electric heater to observe the heating effect in your garage. It will give you an idea of what you need.

 
xmanjeff
Member
Posts: 52
Joined: Thu. Apr. 09, 2015 7:41 pm
Location: niagara falls new york
Hot Air Coal Stoker Stove: keystoker 90 dv

Post by xmanjeff » Mon. Sep. 17, 2018 8:26 pm

i had a hilcoil single u in my keystoker 90 and worked ok , I had a w made up and it works perfectly , on hot burns it will dump hot water , so those are the days where I take an extra shower or do laundry

 
KLook
Member
Posts: 5791
Joined: Sun. Feb. 17, 2008 1:08 pm
Location: Harrison, Tenn
Other Heating: Wishing it was cold enough for coal here....not really

Post by KLook » Mon. Sep. 17, 2018 9:12 pm

The heat loss of an entire garage over a 24 hr period is much more then a shower or wash....the coil for domestic HW in my Harman boiler was many ft long. And it had fins on the outside to pick up the heat from the boiler water. I am guessing it was 10ft or more stretched out.
Listen to the guys that have advised, they have practical experience.


Kevin

Good old Sting would not be so kind....

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Tue. Sep. 18, 2018 7:25 pm

xmanjeff wrote:
Mon. Sep. 17, 2018 8:26 pm
i had a hilcoil single u in my keystoker 90 and worked ok , I had a w made up and it works perfectly , on hot burns it will dump hot water , so those are the days where I take an extra shower or do laundry
He's not trying to heat domestic water. He wants to heat his house with a Hilcoil.

-Don