Hilkoil to heat exchanger info needed

urhstry
Member
Posts: 22
Joined: Wed. Nov. 04, 2015 4:27 pm
Stoker Coal Boiler: Harman Verti-flow
Hand Fed Coal Boiler: Harman Mark III
Coal Size/Type: pea and nut
Other Heating: OWB
Location: Elysburg, PA
Contact:

Post By: urhstry » Tue. Aug. 28, 2018 9:32 am

I am going to put a Hilkoil in my Harman Magnum and just need it to run about twelve feet to a new heat exchanger (with fan). My question is will I need a relief valve inline or anything else? This is for a garage setup and I do not want a tank inline. Thanks!

Visit Hitzer Stoves

User avatar
McGiever
Member
Posts: 7013
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hot Air Coal Stoker Furnace: Converted Riteway into a Stoker Fed
Hot Air Coal Stoker Stove: Harman Magnum
Hand Fed Coal Stove: Warm Morning 414A
Baseburners & Antiques: Our Glenwood 111 ; Art Garland 130 ; Favorite 513
Coal Size/Type: RICE,PEA,NUT,STOVE /ANTHRACITE and EGG / BIT
Other Heating: Ground Source Heat Pump and some Solar
Location: Junction of PA-OH-WV

Post By: McGiever » Tue. Aug. 28, 2018 9:39 am

yes, releif valve required as always on closed loop system...very dangerous w/o releif if fan, pump or power were to fail.

urhstry
Member
Posts: 22
Joined: Wed. Nov. 04, 2015 4:27 pm
Stoker Coal Boiler: Harman Verti-flow
Hand Fed Coal Boiler: Harman Mark III
Coal Size/Type: pea and nut
Other Heating: OWB
Location: Elysburg, PA
Contact:

Post By: urhstry » Tue. Aug. 28, 2018 9:50 am

Can you suggest a valve for this project?

User avatar
McGiever
Member
Posts: 7013
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hot Air Coal Stoker Furnace: Converted Riteway into a Stoker Fed
Hot Air Coal Stoker Stove: Harman Magnum
Hand Fed Coal Stove: Warm Morning 414A
Baseburners & Antiques: Our Glenwood 111 ; Art Garland 130 ; Favorite 513
Coal Size/Type: RICE,PEA,NUT,STOVE /ANTHRACITE and EGG / BIT
Other Heating: Ground Source Heat Pump and some Solar
Location: Junction of PA-OH-WV

Post By: McGiever » Tue. Aug. 28, 2018 10:02 am

urhstry wrote:
Tue. Aug. 28, 2018 9:50 am
Can you suggest a valve for this project?
I'll direct you to Hilkoil for that...they list their's there.

User avatar
Lightning
Member
Posts: 9848
Joined: Wed. Nov. 16, 2011 9:51 am
Hand Fed Coal Furnace: Overmodified/Bored out Clayton 1537
Coal Size/Type: Anthracite/Awesome Size
Location: Olean, NY

Post By: Lightning » Tue. Aug. 28, 2018 3:02 pm

How big is the coil? I don't wanna rain on anyone's parade but those coils don't pick up very much heat. I'd be surprised if they will transfer more than a 1500 BTUs per hour.

urhstry
Member
Posts: 22
Joined: Wed. Nov. 04, 2015 4:27 pm
Stoker Coal Boiler: Harman Verti-flow
Hand Fed Coal Boiler: Harman Mark III
Coal Size/Type: pea and nut
Other Heating: OWB
Location: Elysburg, PA
Contact:

Post By: urhstry » Tue. Aug. 28, 2018 3:08 pm

I would most likely be going with the 18" U coil.

User avatar
Lightning
Member
Posts: 9848
Joined: Wed. Nov. 16, 2011 9:51 am
Hand Fed Coal Furnace: Overmodified/Bored out Clayton 1537
Coal Size/Type: Anthracite/Awesome Size
Location: Olean, NY

Post By: Lightning » Tue. Aug. 28, 2018 3:23 pm

Hmmm. I use two 24 inch U shaped coils in my hand fed. One preheats domestic hot water, the other keeps my outside hot tub warm all winter.

It takes about 12 hours to lift my 40 gallon temper tank roughly 50 degrees during a high burn. So,

40 × 8.34 = 334 BTU/degree

334 × 50 degrees = 16,700

16,700 ÷ 12 hours = 1391

So if I did that right, one 24 inch coil at a high burn absorbs only 1391 BTUs per hour. That's not very much. There's just not enough surface area around a coil to absorb heat to make it do what your wanting. You'll need a lot more than that to heat a garage.

That's my view on it, with my experience on water coils. Your mileage may vary.

urhstry
Member
Posts: 22
Joined: Wed. Nov. 04, 2015 4:27 pm
Stoker Coal Boiler: Harman Verti-flow
Hand Fed Coal Boiler: Harman Mark III
Coal Size/Type: pea and nut
Other Heating: OWB
Location: Elysburg, PA
Contact:

Post By: urhstry » Tue. Aug. 28, 2018 3:35 pm

Interesting.... so in order for my project to work I would neeed a bigger coil AND a water tank, correct?

Visit Hitzer Stoves

User avatar
Lightning
Member
Posts: 9848
Joined: Wed. Nov. 16, 2011 9:51 am
Hand Fed Coal Furnace: Overmodified/Bored out Clayton 1537
Coal Size/Type: Anthracite/Awesome Size
Location: Olean, NY

Post By: Lightning » Tue. Aug. 28, 2018 4:56 pm

Well, you are attempting to make your hot air/convection unit act like a boiler. This subject has come up before and as one forum member once said, "a stove can't even play a boiler on TV" lol. But yes, you are right. Although it would take a significant network of many coils inside the fire chamber of a hand fed or stoker fed furnace to have enough surface area to absorb the amount of heat you need to heat a garage. Even if you used the one coil and heated a tank, then used that stored heat to heat your garage, the tank of water would go cold rather quickly and it would need a huge amount of time (like a full day) to recover so that your could heat the garage for two hours again. It's all about heat transfer at the source of heat. The water circles back to the coil which can't absorb heat fast enough for the demand needed.

User avatar
StokerDon
Site Moderator
Posts: 4111
Joined: Mon. Nov. 11, 2013 11:17 am
Stoker Coal Boiler: 1959Axeman Anderson130M, 1991Axeman Anderson130M, BairMatic BMC-500/Van Wert VA400 Stoker, Gentleman Janitor GJ-671SU/EFM S-15 stoker, 2xVan Wert VA-600
Hand Fed Coal Furnace: Harman SF3500
Coal Size/Type: Rice, Pea, Chestnut
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood
Location: PA, Southern York County!

Post By: StokerDon » Tue. Aug. 28, 2018 5:10 pm

urhstry wrote:
Tue. Aug. 28, 2018 3:35 pm
Interesting.... so in order for my project to work I would neeed a bigger coil AND a water tank, correct?
No, what you really need is a boiler. There is no way for a small coil in a stove to absorb enough heat to power house sized a water to air heat exchanger. There is just not enough surface area. Sounds like you are trying to reinvent the wheel when it was already perfected 100 years ago.

Used coal boilers can be fairly cheap because, unlike a stove, they are not easy to move.

-Don

User avatar
Lightning
Member
Posts: 9848
Joined: Wed. Nov. 16, 2011 9:51 am
Hand Fed Coal Furnace: Overmodified/Bored out Clayton 1537
Coal Size/Type: Anthracite/Awesome Size
Location: Olean, NY

Post By: Lightning » Tue. Aug. 28, 2018 6:33 pm

Mr. Don is right. Just to put things in perspective, you would want at least 30,000 BTUs per hour on hand (during really cold weather) for your garage. And 30,000 is probably a conservative figure.

franco b
Site Moderator
Posts: 9299
Joined: Wed. Nov. 05, 2008 5:11 pm
Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
Baseburners & Antiques: Glenwood Modern Oak 114
Coal Size/Type: nut and pea
Location: Kent CT

Post By: franco b » Wed. Aug. 29, 2018 8:24 pm

I would suggest trying a 5000 BTU electric heater to observe the heating effect in your garage. It will give you an idea of what you need.

xmanjeff
Member
Posts: 32
Joined: Thu. Apr. 09, 2015 7:41 pm
Hot Air Coal Stoker Stove: keystoker 90 dv
Location: niagara falls new york

Post By: xmanjeff » Mon. Sep. 17, 2018 8:26 pm

i had a hilcoil single u in my keystoker 90 and worked ok , I had a w made up and it works perfectly , on hot burns it will dump hot water , so those are the days where I take an extra shower or do laundry

User avatar
KLook
Member
Posts: 3996
Joined: Sun. Feb. 17, 2008 1:08 pm
Stoker Coal Boiler: Harman VF 3000
Coal Size/Type: rice, bagged, Blaschak
Other Heating: Gas boiler backup/main
Stove/Furnace Model: VF 3000
Location: Harrison, Tenn

Post By: KLook » Mon. Sep. 17, 2018 9:12 pm

The heat loss of an entire garage over a 24 hr period is much more then a shower or wash....the coil for domestic HW in my Harman boiler was many ft long. And it had fins on the outside to pick up the heat from the boiler water. I am guessing it was 10ft or more stretched out.
Listen to the guys that have advised, they have practical experience.


Kevin

Good old Sting would not be so kind....

User avatar
StokerDon
Site Moderator
Posts: 4111
Joined: Mon. Nov. 11, 2013 11:17 am
Stoker Coal Boiler: 1959Axeman Anderson130M, 1991Axeman Anderson130M, BairMatic BMC-500/Van Wert VA400 Stoker, Gentleman Janitor GJ-671SU/EFM S-15 stoker, 2xVan Wert VA-600
Hand Fed Coal Furnace: Harman SF3500
Coal Size/Type: Rice, Pea, Chestnut
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood
Location: PA, Southern York County!

Post By: StokerDon » Tue. Sep. 18, 2018 7:25 pm

xmanjeff wrote:
Mon. Sep. 17, 2018 8:26 pm
i had a hilcoil single u in my keystoker 90 and worked ok , I had a w made up and it works perfectly , on hot burns it will dump hot water , so those are the days where I take an extra shower or do laundry
He's not trying to heat domestic water. He wants to heat his house with a Hilcoil.

-Don

Visit Hitzer Stoves