Manometer question
-
- Member
- Posts: 28
- Joined: Thu. Sep. 03, 2015 7:49 am
- Baseburners & Antiques: Home Herald Oak #18
Just installed one , the question I have and forget since my last stove hook up is it the low side or the high side of the meter? I’m running a Harman Mark 2 and what’s a good reading on it? Thanks guys...
- Lightning
- Site Moderator
- Posts: 14659
- Joined: Wed. Nov. 16, 2011 9:51 am
- Location: Olean, NY
- Stoker Coal Boiler: Modified AA 130
- Coal Size/Type: Pea Size - Anthracite
Dwyer Mark II model 25 - use the low side to show a negative value on the positive side of the scale. A good operating range is -.03 to -.05
The hose connected to the high side is only 4 inches long and open to the room. It helps keep dust from getting into the unit.