Post Mon. Nov. 13, 2017 4:57 pm

Installed Dwyer mano set the 2 zeros fire is 450 in stove an flue pipe is 235 .Drilled the hole in flue My Reading Is .07 .Now what .Please your comments

User avatar
coaledsweat
Site Moderator
Posts: 10018
Joined: Fri. Oct. 27, 2006 2:05 pm
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea
Location: Guilford, Connecticut

Post Mon. Nov. 13, 2017 5:18 pm

Do you have a barometric damper? If so, adjust it back to -.05 and see what happens. That's a strong draft, probably more than you need.

Den034071
Member
Posts: 510
Joined: Sat. Jun. 25, 2011 4:30 pm
Hand Fed Coal Stove: Hitzer, 3095

Post Mon. Nov. 13, 2017 6:28 pm

Yes hace a baro the R C unit .

Visit Hitzer Stoves

KingCoal
Member
Posts: 3278
Joined: Wed. Apr. 03, 2013 1:24 pm
Hand Fed Coal Stove: 3-Locke Warm Morning #120, 1-Locke Warm Morning #524B
Baseburners & Antiques: 2014 DTS C17 Base Burner
Coal Size/Type: Nut Anth.
Other Heating: none
Location: Elkhart county, IN.

Post Mon. Nov. 13, 2017 7:12 pm

jack did you install an MPD in the flue along with the Baro ?

Den034071
Member
Posts: 510
Joined: Sat. Jun. 25, 2011 4:30 pm
Hand Fed Coal Stove: Hitzer, 3095

Post Mon. Nov. 13, 2017 9:06 pm

Yep have both .All new to me a batch fed stove . jack

User avatar
warminmn
Member
Posts: 2619
Joined: Tue. Feb. 08, 2011 5:59 pm
Hand Fed Coal Stove: Chubby Junior, Efel Nestor Martin, Frankenstove
Coal Size/Type: nut and stove anthracite
Other Heating: wood and a little LP
Location: Land of 11,842 lakes

Post Mon. Nov. 13, 2017 9:27 pm

No pictures so I just want to make sure your baro is above your MPD. Its dangerous the other way.

Visit Hitzer Stoves

User avatar
corey
Member
Posts: 852
Joined: Fri. Nov. 14, 2014 11:14 am
Hand Fed Coal Stove: USS Ashley coal stove
Coal Size/Type: Eastern KY bituminous
Location: Southwest VA

Post Sat. Nov. 25, 2017 3:03 pm

I like to run mine .03 to .05 tuned with my mpd. When mine hits .07 it's usually going to cook me out the house from the heat.

User avatar
Sunny Boy
Member
Posts: 13165
Joined: Mon. Nov. 11, 2013 1:40 pm
Hand Fed Coal Boiler: Anthracite Industrial, domestic hot water heater
Baseburners & Antiques: Glenwood range 208, # 6 base heater, 2 Modern Oak 118.
Coal Size/Type: Nuts !
Other Heating: Oil &electric plenum furnace
Location: Central NY

Post Sun. Nov. 26, 2017 6:54 am

Every stove and chimney system draft ability varies. Plus, where you install the mano probe can show different readings than someone with the exact same stove and their probe in a different place. But what's common amongst them all is that you want the lowest mano reading that gives you the warmth you need.

The mano numbers are an indication of draft strength that is sending heat up the chimney. More heat causes a stronger draft, therefore higher mano numbers. Obviously, you want to keep as much heat in the house as possible, but you still need to give some heat to the chimney system to maintain a enough draft to keep a steady fire.

Try adjusting the baro to get the lowest mano reading, without the stove slowing down. That's a baseline that tells you that any less draft and the stove wants to run too slow. Then experiment with increasing the mano readings to where it's consistently putting out the amount of heat you want. That's the draft "sweet spot" for your stove and chimney system.

From that sweet spot point you can fine tune the heat output using just the primary and MPD to bump the mano readings up or down if you need heat changes, and the baro will maintain that.

Paul