Will Not Burn Coal Well

 
User avatar
windyhill4.2
Member
Posts: 6072
Joined: Fri. Nov. 22, 2013 2:17 pm
Location: Jonestown,Pa.17038
Stoker Coal Boiler: 1960 EFM520 installed in truck box
Hand Fed Coal Stove: Crane 404 with variable blower
Coal Size/Type: 404-nut, 520 rice ,anthracite for both

Post by windyhill4.2 » Mon. Nov. 13, 2017 6:42 am

windyhill4.2 wrote:
Sun. Nov. 12, 2017 7:45 pm
Try a 45* slope on that 4' horizontal run,with it level,the hot air gets into the horizontal & meets cold air & can't figure out which way is up.
This isn't guess work on my part...

This is based on REAL experience from many yrs ago when burning wood.


 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Mon. Nov. 13, 2017 6:49 am

No, there is no real chimney, the stove pipe just turns upwards and goes above the roof. No masonry or triple wall chimney, just single wall pipe.
That is why you have draft problems.

 
User avatar
CoalJockey
Verified Business Rep.
Posts: 1324
Joined: Sun. Mar. 09, 2008 11:18 am
Location: Loysburg, PA
Stoker Coal Boiler: Several EFM 520 refurbs...one 900, one 1300 mega-stoker
Hand Fed Coal Stove: (2) Warm Morning Stoves

Post by CoalJockey » Mon. Nov. 13, 2017 6:56 am

Can the single wall pipe on the exterior of the house be allowing the exhaust gasses to cool too quickly after leaving the stove? I would think that could kill your draft. The whole idea is to keep those gasses hot so they create the rise and pull more air from beneath. The higher the chimney = more draft.

I think that’s why when the old-timers built a stone fireplace and chimney, it was built out of the biggest fieldstones they could find...once stones are heated and draft established, the huge mass of the heated stones helps to maintain the proper draft.

I found this out quickly years ago on a stoker boiler in a shed. Once I went to double wall insulated pipe, it helped the draft very much. Likely the only thing that kept it going to begin with was the fan running on the stoker.

Would like to see a photo of the flue outside the house...

 
User avatar
CoalJockey
Verified Business Rep.
Posts: 1324
Joined: Sun. Mar. 09, 2008 11:18 am
Location: Loysburg, PA
Stoker Coal Boiler: Several EFM 520 refurbs...one 900, one 1300 mega-stoker
Hand Fed Coal Stove: (2) Warm Morning Stoves

Post by CoalJockey » Mon. Nov. 13, 2017 6:57 am

Missed Robs response as I was typing!

I think we’ve nailed it.

 
User avatar
Sunny Boy
Member
Posts: 25729
Joined: Mon. Nov. 11, 2013 1:40 pm
Location: Central NY
Hand Fed Coal Boiler: Anthracite Industrial, domestic hot water heater
Baseburners & Antiques: Glenwood range 208, # 6 base heater, 2 Modern Oak 118.
Coal Size/Type: Nuts !
Other Heating: Oil &electric plenum furnace

Post by Sunny Boy » Mon. Nov. 13, 2017 10:31 am

windyhill4.2 wrote:
Mon. Nov. 13, 2017 6:42 am
This isn't guess work on my part...

This is based on REAL experience from many yrs ago when burning wood.
Same here.

Had a 3 foot horizontal run on my small potbelly stove. Getting it to light without back drafting against the house's chimney affect took pre-heating that horizontal section of pipe with a pro-pain torch while the stove dampers were closed. Then once the hot and cold air inside the pipe figured out who's boss, quickly open the primary and light the kindling.

And I was also using single wall pipe outside. That was ok once a wood fire was going, but the single wall pipe lost so much heat and draft strength that running a coal fire slowly got tough to maintain enough draft to keep it from dying.

It's gotta be insulated pipe outside, or stick to burning with a high exhaust heat to maintain a safe draft.

Paul

 
User avatar
Logs
Member
Posts: 1819
Joined: Thu. Aug. 21, 2014 12:07 am
Location: White Oak Pa
Hand Fed Coal Stove: Chubby
Coal Size/Type: Nut anthracite
Other Heating: Fireplace and wood burner

Post by Logs » Mon. Nov. 13, 2017 10:49 am

I have single wall pipe on a small box stove I have in my garage. It works with much added difficulty. After exiting garage , it only sticks up 6 feet. Single wall, in order for me to get it burning really well, I heat the chimney with a piece of newspaper to get draft goin. Once lit , I have a small fan 6” on floor directed at air intake to keep the fire burning hot. I burn only wood and just use to take the chill off when working in there.
I guess what I’m trying to say is, you can make anything burn, may not be very safe though. Follow the advice of these guys and be safe. I hope you can get going good.

 
User avatar
Pancho
Member
Posts: 906
Joined: Sat. Feb. 01, 2014 4:00 pm
Location: Michigan
Baseburners & Antiques: Glenwood No. 8
Coal Size/Type: Stove
Other Heating: Jotul Firelight

Post by Pancho » Mon. Nov. 13, 2017 1:34 pm

NoSmoke wrote:
Mon. Nov. 13, 2017 6:34 am
No, there is no real chimney, the stove pipe just turns upwards and goes above the roof. No masonry or triple wall chimney, just single wall pipe.
Houston...there's a big part of your problem.

With a wood fire, you "might" be able to overcome the single wall as your exhaust gasses are very high....BUT....I wouldn't burn wood in that setup, it's begging for creosote issues and chimney fires take the fun out of everything.

Go triple wall out and up and you should see a big improvement.


 
User avatar
joeq
Member
Posts: 5743
Joined: Sat. Feb. 11, 2012 11:53 am
Location: Northern CT
Hand Fed Coal Stove: G111, Southard Robertson

Post by joeq » Mon. Nov. 13, 2017 1:58 pm

He mentioned his chimney pipe totals 17' high, (not counting the 4' horizontal run.) and is 6" diameter. Sounds like plenty of run for drafting, no? Or are you guys saying because it's not "insulated" the outside temperature of the pipe is affecting the draft?

 
User avatar
CoalJockey
Verified Business Rep.
Posts: 1324
Joined: Sun. Mar. 09, 2008 11:18 am
Location: Loysburg, PA
Stoker Coal Boiler: Several EFM 520 refurbs...one 900, one 1300 mega-stoker
Hand Fed Coal Stove: (2) Warm Morning Stoves

Post by CoalJockey » Mon. Nov. 13, 2017 3:00 pm

joeq wrote:
Mon. Nov. 13, 2017 1:58 pm
He mentioned his chimney pipe totals 17' high, (not counting the 4' horizontal run.) and is 6" diameter. Sounds like plenty of run for drafting, no? Or are you guys saying because it's not "insulated" the outside temperature of the pipe is affecting the draft?
That's what I think. Seems like the gasses would cool immediately after exiting the house. You could probably have a pipe 30 feet high with the same stove setup and if the gasses are not hot enough it still would not create any "lift".

The double and triple walk pipes has the insulating value to keep the heat in the pipe where it belongs... no immediate cooling effect.

 
franco b
Site Moderator
Posts: 11417
Joined: Wed. Nov. 05, 2008 5:11 pm
Location: Kent CT
Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
Baseburners & Antiques: Glenwood Modern Oak 114
Coal Size/Type: nut and pea

Post by franco b » Mon. Nov. 13, 2017 3:05 pm

Unless I misunderstand the triple wall pipes are designed to cool the gas to prevent overheating. That third layer is open for circulation through the length of the pipe.

I would only use double wall insulated.

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Mon. Nov. 13, 2017 3:07 pm

franco b wrote:
Mon. Nov. 13, 2017 3:05 pm
Unless I misunderstand the triple wall pipes are designed to cool the gas to prevent overheating. That third layer is open for circulation through the length of the pipe.

I would only use double wall insulated.
You are correct.

 
User avatar
Sunny Boy
Member
Posts: 25729
Joined: Mon. Nov. 11, 2013 1:40 pm
Location: Central NY
Hand Fed Coal Boiler: Anthracite Industrial, domestic hot water heater
Baseburners & Antiques: Glenwood range 208, # 6 base heater, 2 Modern Oak 118.
Coal Size/Type: Nuts !
Other Heating: Oil &electric plenum furnace

Post by Sunny Boy » Mon. Nov. 13, 2017 3:39 pm

joeq wrote:
Mon. Nov. 13, 2017 1:58 pm
He mentioned his chimney pipe totals 17' high, (not counting the 4' horizontal run.) and is 6" diameter. Sounds like plenty of run for drafting, no? Or are you guys saying because it's not "insulated" the outside temperature of the pipe is affecting the draft?
Too much heat is lost through the outdoors single pipe wall. By the time the exhaust reaches the top there's hardly any pressure difference to give a strong enough draft.

It's kinda like sticking a potato in the tail pipe ! I know that you know what that means. :D

Paul

 
User avatar
oliver power
Member
Posts: 2970
Joined: Sun. Apr. 16, 2006 9:28 am
Location: Near Dansville, NY
Stoker Coal Boiler: KEYSTOKER Kaa-2
Hand Fed Coal Stove: Hitzer 50-93 & 30-95, Vigilant (pre-2310), D.S. 1600 Circulator, Hitzer 254

Post by oliver power » Mon. Nov. 13, 2017 9:14 pm

Yes Mam, There's your problem. No chimney..........

 
User avatar
joeq
Member
Posts: 5743
Joined: Sat. Feb. 11, 2012 11:53 am
Location: Northern CT
Hand Fed Coal Stove: G111, Southard Robertson

Post by joeq » Mon. Nov. 13, 2017 11:07 pm

Sunny Boy wrote:
Mon. Nov. 13, 2017 3:39 pm
It's kinda like sticking a potato in the tail pipe ! I know that you know what that means. :D

Paul
Good analogy Paul. I'ld prefer a spark plug in the tailpipe. :yes:

 
User avatar
Lightning
Site Moderator
Posts: 14669
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Thu. Nov. 16, 2017 4:53 am

Oh yeah, I did the stove pipe chimney thing my first year. It was funny cuz while the sun was hitting it in the evening it would draft like mad. Once the sun fell under the hill it struggled to draft at all, that's how touchy it was. It kept things pretty exciting lol.