Stack Temperatures Hand Fired Stoves

Modern and vintage hand fired coal stove are similar to a wood stove and in some cases can burn either. They need to be regulated and fed by hand usually every 12 to 24 hours depending on your usage. They require no power to operate making them ideal for rural settings with long power outages.
User avatar
skobydog
Member
Posts: 238
Joined: Mon. Jun. 10, 2013 9:53 am
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Nut Anthracite
Location: Greenfield MA

Post Tue. Dec. 17, 2013 2:28 pm

Would it be abnormal to see a 600 degree (internal probe thermometer) temperature on a coal stove?

I ask because I noticed the other day (and today) that my stack temperatures shot up to 600 degrees (internal probe thermometer appr 24 inches above stove and MPD closed) when the stove was given some air. This is the Hitzer with the automatic damper on the back so it adjusts the air automatically. I could hear the flames going up the stove pipe. Maybe I just never noticed it because I'm not always here.

Normally my stack temp sits a bit under 200 degrees. Maybe I just never noticed the stack temp rising that high before as I'm not always home to see it.

Is this is a normal stack temp for a hand-fired stove? Thanks
Hitzer 50-93
Open Floor Plan
Stove is located on the first floor/living room
Heating appr 2,200 sq ft
House built 1976
Moderate Insulation

Visit Hitzer Stoves

User avatar
wsherrick
Member
Posts: 3731
Joined: Wed. Jun. 18, 2008 6:04 am
Hand Fed Coal Stove: Glenwood Base Heater, Crawford Base Heater
Baseburners & Antiques: Crawford Base Heater, Glenwood, Stanley Argand
Coal Size/Type: Chestnut, Stove Size
Location: High In The Poconos

Post Tue. Dec. 17, 2013 5:43 pm

A 600 degree stack temperature is really, really high.

User avatar
EarthWindandFire
Member
Posts: 1457
Joined: Sat. Dec. 18, 2010 12:02 pm
Hot Air Coal Stoker Furnace: Leisure Line Lil' Heater.
Other Heating: Oil Furnace and Kerosene Heaters.
Location: Connecticut

Post Tue. Dec. 17, 2013 5:56 pm

If everyone had a 600 degree stack temp, we would melt the polar ice caps and send Santa's workshop crashing into the Arctic Ocean. ;)

Anything above 350 degrees would be unacceptable.
Mark

Inflation is the Grim Reaper to prosperity.
Printing money without a gold standard is the crime of counterfeiting.
The bitterness of poor quality lingers long after the sweetness of low price is forgotten.
Mr. McGee, don't make me angry. You wouldn't like me when I'm angry.
Si vis paceum, parabellum.

User avatar
fastcat
Member
Posts: 443
Joined: Thu. Nov. 12, 2009 11:50 pm
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Blaschak Nut/Stove Mix
Location: CNY (McGraw)

Post Tue. Dec. 17, 2013 6:10 pm

That temp is normal to see with the Hitzer when running a little higher temps in the stove due to low outside temps. Mine has been doing the same thing. Myself I'm not worried about it because it is only for a short time till the flapper closes. :D
This is only my two cents
and sometimes it is not worth that

User avatar
mmcoal
Member
Posts: 139
Joined: Sat. Feb. 18, 2012 11:21 am
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: nut
Location: Northern NJ

Post Tue. Dec. 17, 2013 6:17 pm

My 50-93 does the same thing. It doesn't happen all the time, but I do get 500-600 degree stack temps after a shake down once in awhile. For me once it spikes, it usually calms down within about 15-20 minutes. It also doesn't matter whether I have my MPD is open or closed either. I think sometimes the new coal igniting right after a shake down starts to rage a little too much before the stove temperature raises enough for the bi-metal damper to respond and close. At least that's my thought on it.

User avatar
skobydog
Member
Posts: 238
Joined: Mon. Jun. 10, 2013 9:53 am
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Nut Anthracite
Location: Greenfield MA

Post Tue. Dec. 17, 2013 6:46 pm

mmcoal wrote: It doesn't happen all the time, but I do get 500-600 degree stack temps after a shake down once in awhile. For me once it spikes, it usually calms down within about 15-20 minutes. It also doesn't matter whether I have my MPD is open or closed either. I think sometimes the new coal igniting right after a shake down starts to rage a little too much before the stove temperature raises enough for the bi-metal damper to respond and close. At least that's my thought on it.

Looks like you and fastcat have had the same experience with this stove.

What you described is exactly what happened today. I shook down the stove. A short time later (not sure how long) the stack temp spiked for a number of minutes until the back flapper closed. Then within 20-30 mins the stack temp dropped back to around 200 degrees and stayed in that range.

When I opened the flapper again shortly after there was on spike in the stack temp. Like you said, I guess it's just the new coal being introduced at that time.

I suppose it doesn't happen all the time because the back flapper isn't always open after shaking. 8-)
Hitzer 50-93
Open Floor Plan
Stove is located on the first floor/living room
Heating appr 2,200 sq ft
House built 1976
Moderate Insulation

JohnnyV
Member
Posts: 102
Joined: Wed. Dec. 08, 2010 8:41 pm
Hand Fed Coal Stove: hitzer 254
Coal Size/Type: Nut
Other Heating: Pellet stove far end of house
Stove/Furnace Make: Hitzer
Stove/Furnace Model: 254
Location: Houtzdale, PA

Post Tue. Dec. 17, 2013 6:53 pm

I believe that is normal. It is only temporary, until the flap closes.

User avatar
skobydog
Member
Posts: 238
Joined: Mon. Jun. 10, 2013 9:53 am
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Nut Anthracite
Location: Greenfield MA

Post Tue. Dec. 17, 2013 7:10 pm

JohnnyV wrote:I believe that is normal. It is only temporary, until the flap closes.
I'll have to experiment over the next couple shake downs. If I can replicate it then I'll know. I'll purposely keep the flapper open and then closed to see.

I'm still with this stove and would like to make sure for piece of mind while I'm at work.
Hitzer 50-93
Open Floor Plan
Stove is located on the first floor/living room
Heating appr 2,200 sq ft
House built 1976
Moderate Insulation

Visit Hitzer Stoves

User avatar
Keepaeyeonit
Member
Posts: 1036
Joined: Wed. Mar. 24, 2010 7:18 pm
Baseburners & Antiques: Glenwood #8
Coal Size/Type: Direnzo nut, Lehigh stove
Other Heating: 45 year old oil furnace,and a crappy 24 year old heat pump
Location: Northeast Ohio.

Post Tue. Dec. 17, 2013 7:30 pm

Skobydog,I have a thermometer 2" above the stove outlet and a thermocouple at the same level to check flue gas temp and at shake down/reload I see 500* pipe and 700* to 800*(1000* was the max I ever saw but the pipe never got above 550*) gas temp but thats for a very short amount of time.During normal use with the stove above 500* the pipe is 350* or so and the gas temp is 400*, the pipe is 145* 6' from the stove and after the baro.Keepaeyeonit
Keepaeyeonit
Northeast,Ohio

User avatar
skobydog
Member
Posts: 238
Joined: Mon. Jun. 10, 2013 9:53 am
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Nut Anthracite
Location: Greenfield MA

Post Tue. Dec. 17, 2013 9:43 pm

Keepaeyeonit wrote:Skobydog,I have a thermometer 2" above the stove outlet and a thermocouple at the same level to check flue gas temp and at shake down/reload I see 500* pipe and 700* to 800*(1000* was the max I ever saw but the pipe never got above 550*) gas temp but thats for a very short amount of time.During normal use with the stove above 500* the pipe is 350* or so and the gas temp is 400*, the pipe is 145* 6' from the stove and after the baro.Keepaeyeonit
Because I am using double-wall stove pipe I am using a probe thermometer.

Would I be correct in assuming a probe thermometer would be closer to the thermocouple vs a magnetic stick-on stove pipe thermometer?
Hitzer 50-93
Open Floor Plan
Stove is located on the first floor/living room
Heating appr 2,200 sq ft
House built 1976
Moderate Insulation

User avatar
2001Sierra
Member
Posts: 1845
Joined: Wed. May. 20, 2009 8:09 am
Hot Air Coal Stoker Stove: Keystoker 90 Chimney vent
Coal Size/Type: Rice
Other Heating: Buderus Oil Boiler 3115-34
Stove/Furnace Model: Keystoker 90 Chimney Vent
Location: Wynantskill NY, 10 miles from Albany

Post Tue. Dec. 17, 2013 9:51 pm

My old Buderus never exceeded 300 degrees, 59000 BTU stove rated.

User avatar
oliver power
Member
Posts: 2266
Joined: Sun. Apr. 16, 2006 9:28 am
Stoker Coal Boiler: KEYSTOKER Kaa-2
Hand Fed Coal Stove: Hitzer 50-93 & 30-95, Vigilant (pre-Vigilant-II), D.S. 1600 Circulator
Baseburners & Antiques: MANY (Mostly when burning wood)
Location: Near Dansville, NY

Post Wed. Dec. 18, 2013 4:29 am

OK, here's what's happening; If you have a good hot fire at tending time, no problems. Your stack temp may, or may not rise. If it does rise, it wouldn't be much (Example: 25* - 50*) ,then settles back down. Now, if your fire is low at tending time, the first thing you need to do is shut the fan off. You don't want the fan taking any heat off the mass of the stove. As you loose heat off the mass of the stove, the back flapper door will open wider, and wider. Once the fire gets going, it has to heat the entire mass of the stove back up, till the flapper door closes again. By that time, you have a roaring fire, and way higher stack temps than you should. The flapper door acts like a mini ash pan door being left open. The stove runs away on you. Stack temps surge. You loose control (not good). I wouldn't except these high spikes in stack temps as "Normal". The secret is not to loose the stoves heat mass. Also, should the fire be low; it should be built up a little to a time (as if starting a fresh fire), till you have a good hot bed of coals to start with. Because the fan is off, the mass of the stove is heated back up. Or at least rapidly heading in that direction. Only then, the hopper should be topped off. And yes, you're correct about many people not seeing this happen, as off to work they go. All the while, never knowing how close they are to having a house fire Every Day.

User avatar
Keepaeyeonit
Member
Posts: 1036
Joined: Wed. Mar. 24, 2010 7:18 pm
Baseburners & Antiques: Glenwood #8
Coal Size/Type: Direnzo nut, Lehigh stove
Other Heating: 45 year old oil furnace,and a crappy 24 year old heat pump
Location: Northeast Ohio.

Post Wed. Dec. 18, 2013 7:02 am

Skobydog,OP brings up something I forgot your stove has dial-a-temp so your tending routine is going to be different then mine.The other thing is not tending the stove and running out the door, I leave myself 25 to 30 minutes after a reload to make sure that everything settles down before I leave the house.Keepaeyeonit
Keepaeyeonit
Northeast,Ohio

User avatar
coalkirk
Member
Posts: 4682
Joined: Wed. May. 17, 2006 8:12 pm
Stoker Coal Boiler: 1981 EFM DF520
Coal Size/Type: anthracite/rice coal
Location: Forest Hill MD

Post Wed. Dec. 18, 2013 7:25 am

If you are using an internal probe thermometer you need to make sure the probe cannot "see" the fire in the stove. If it does you are getting a radiant effect on the probe instead of measuring the stack temp.
You have enemies? Good. That means you've stood up for something, sometime in your life. Winston Churchill

"I would rather have a German division in front of me than a French one behind me." —General George S. Patton

Burning rice coal in a 1981 EFM DF520, nut coal in a hand fired Jotul 507.

bksaun
Member
Posts: 966
Joined: Sat. Oct. 28, 2006 9:24 am
Stoker Coal Boiler: Hybrid, Gentleman Janitor GJ-6RSU/ EFM 700
Hand Fed Coal Stove: Hitzer 503
Coal Size/Type: Pea Stoker/Bit, Pea or Nut Anthracite
Stove/Furnace Make: Hitzer/ EFM-Gentleman Janitor
Stove/Furnace Model: 503 Insert/ 700/GJ-62
Location: Hustonville, Ky

Post Wed. Dec. 18, 2013 7:33 am

Big difference between an internal temp and an external magnet temp, 600 was normal for my hitzer, I used a grill thermometer so it measured the internal temp, also had a magnet type beside it and the temps were 175-200 degrees different when running on high.

We need to compare apples to apples here.

Bk
"Corn Stoves", It is morally wrong to burn something you can make into Whiskey!

BK

Visit Hitzer Stoves