Harmon MKII Backdrafting

 
doctorclean
New Member
Posts: 4
Joined: Fri. Oct. 26, 2012 3:14 pm
Location: Homer, Alaska

Post by doctorclean » Sat. Oct. 27, 2012 6:50 pm

Hello Gentlemen,

I hope you can give me some advice on my Harman MKII setup. I purchased this house a year ago, I have been burning sub-bituminous coal from Healy in Alaska. The problem I have is that the stove backdrafts when the wind blows from the side of the house that the stove is mounted in. I did install a downdraft preventer that is shaped like an H. It doesn't move in the wind but is supposed to create a vacuum in the stove pipe, This addition did not help. I believe my next course of action should be to make the stack taller according to what I have read here. One Thing I am curious about is the size of the pipe. The hole on the back of the stove is a 6" the previous owner has chosen to immediately adapt the stack size up to 8" for the rest of stack. Should I remove all of the 8" pipe and replace it with 6"(expensive). I am concerned about Carbon Monoxide poisoning. We do have 3 CO detecters in the house. I will post pics of the downdraft preventer soon. I do have a manual damper and no manometer at this time.

Attachments

photo_1[1].JPG

inside

.JPG | 87.7KB | photo_1[1].JPG
photo_2[1].JPG

6 to 8 reducer

.JPG | 160.5KB | photo_2[1].JPG
photo_3[2].JPG

House side front

.JPG | 131.2KB | photo_3[2].JPG
photo_5[1].JPG

house side back

.JPG | 35.9KB | photo_5[1].JPG


 
User avatar
freetown fred
Member
Posts: 30293
Joined: Thu. Dec. 31, 2009 12:33 pm
Location: Freetown,NY 13803
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut

Post by freetown fred » Sat. Oct. 27, 2012 8:04 pm

DC, that chimney height looks good in the pix-(sometimes deceiving) as long as you are a couple foot above that higest roof line, you're good. NOW, just an old farmers thoughts--lose the 8" pipe, sorry buddy, expensive or not, I'm pretty sure that will be your fix.Fancy cap or not, that 8" is a lot of pipe--I have a hand fired & have only an MPD--no mano, no baro--I think on these more complex set-ups they might be a great idea. My draft test consists of lighting a piece of paper & sticking it near my exit vent--if it draws it's good. I too am on top of a hill with no trees around the house as wind break--I'm a firm beleiver in the KISS concept. SAFETY is the rule--with 3 CO alarms, you're set--I do new batteries every year, needed or not. Nice place by the way.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sat. Oct. 27, 2012 8:35 pm

Looking at that roof pitch...I'd say you need more height.

And that 8" pipe is just fine for your sub-bit Alaskan Coal. :)

 
doctorclean
New Member
Posts: 4
Joined: Fri. Oct. 26, 2012 3:14 pm
Location: Homer, Alaska

Post by doctorclean » Sat. Oct. 27, 2012 8:49 pm

Here is a pic of the new top

Attachments

photo 3.JPG
.JPG | 87KB | photo 3.JPG

 
User avatar
freetown fred
Member
Posts: 30293
Joined: Thu. Dec. 31, 2009 12:33 pm
Location: Freetown,NY 13803
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut

Post by freetown fred » Sat. Oct. 27, 2012 10:57 pm

Looks like it should work in theory. Hopin it does.

 
User avatar
Rob R.
Site Moderator
Posts: 17979
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sat. Oct. 27, 2012 11:03 pm

Any chance the backdraft occurs when you are running the clothes dryer or something else competing for air with the stove?

 
doctorclean
New Member
Posts: 4
Joined: Fri. Oct. 26, 2012 3:14 pm
Location: Homer, Alaska

Post by doctorclean » Sun. Oct. 28, 2012 12:10 am

The backdraft only occurs when the wind is blowing from the west.Bathroom fans being on do not change the draft problem. The new cap also did not help.


 
doctorclean
New Member
Posts: 4
Joined: Fri. Oct. 26, 2012 3:14 pm
Location: Homer, Alaska

Post by doctorclean » Sun. Oct. 28, 2012 12:42 am

Here are some more pics from various angles :)

Attachments

IMG_2389.JPG
.JPG | 152.1KB | IMG_2389.JPG
IMG_2675.JPG
.JPG | 116.3KB | IMG_2675.JPG
IMG_3704.JPG
.JPG | 183.9KB | IMG_3704.JPG

 
User avatar
Freddy
Member
Posts: 7293
Joined: Fri. Apr. 11, 2008 2:54 pm
Location: Orrington, Maine
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Coal Size/Type: Pea size, Superior, deep mined

Post by Freddy » Sun. Oct. 28, 2012 6:07 am

Beautiful place!

You say it happens when the wind blows from the right? Usually this type of thing happens when it blows from the direction that I have pictured. Perhaps the shed roof makes your geometry different than most. Nonetheless, a couple of comments.... one, they say you should have a minimum of 10 feet from the chimney top horizontally to the roof. It looks like you might be a bit close and more height would help. Also, I do think a 6" pipe might help. Logic says a 6" pipe would have to have more flu gas speed and it seems that could only be a good thing. It would certainly be a weekend killer, but with some luck it wouldn't cost you a penny. Find out how much a new 6" would be. Then put an add on Craigs list (internet) and try to sell your 8" for that price. If it sells, voila, you got a 6" for nothing.

Again...beautiful place! If you want a different solution to your problem, just trade your place for mine. <grin>

Attachments

Alaska Chimney.jpg
.JPG | 102.5KB | Alaska Chimney.jpg
Alaska Chimney 2.jpg
.JPG | 37.2KB | Alaska Chimney 2.jpg

 
User avatar
Rob R.
Site Moderator
Posts: 17979
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sun. Oct. 28, 2012 7:14 am

Most of the buys that burn bituminous coal recommend 8"...it tolerates soot better. I think the chimney needs to be higher.

Most people would say that the chimney on my house is too large and won't draft properly, but it is about 32' high and works fine.

 
User avatar
freetown fred
Member
Posts: 30293
Joined: Thu. Dec. 31, 2009 12:33 pm
Location: Freetown,NY 13803
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut

Post by freetown fred » Sun. Oct. 28, 2012 7:30 am

So much for theory--I'm probably just an old fool, but when something is designed to accomodate a 6" pipe, I gotta kinda figure that the designers aren't idiots no matter what the rocket scientists think, and think about it--what options do you have left. Freddy's advice on the pipe venture sure looks good in my book.

 
User avatar
blrman07
Member
Posts: 2383
Joined: Mon. Sep. 27, 2010 3:39 pm
Location: Tupelo Mississippi

Post by blrman07 » Sun. Oct. 28, 2012 7:34 am

Much quicker solution. Install a motorized draft inducer. picture from ebay You can get them on the internet for between $100 and $150. One is currently on ebay for $90.
Last edited by blrman07 on Mon. Oct. 29, 2012 6:51 am, edited 1 time in total.

 
User avatar
Rob R.
Site Moderator
Posts: 17979
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sun. Oct. 28, 2012 7:37 am

Sub-bit coal is a different beast, I expect it would clog that draft inducer up in no time.

 
User avatar
freetown fred
Member
Posts: 30293
Joined: Thu. Dec. 31, 2009 12:33 pm
Location: Freetown,NY 13803
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut

Post by freetown fred » Sun. Oct. 28, 2012 7:43 am

What Rob R. said :)

 
User avatar
SteveZee
Member
Posts: 2512
Joined: Wed. May. 11, 2011 10:45 am
Location: Downeast , Maine
Hand Fed Coal Stove: Glenwood Modern Oak 116 & Glenwood 208 C Range

Post by SteveZee » Sun. Oct. 28, 2012 8:08 am

I'm with Rob on this one. I'd stick with the 8" pipe (for the moment) and extend it at least a section (4') first off. That's the easiest and most practical thing to try. If it works, your off to the races. If not, then you may have to spend the bucks and convert to 6". I understand what that (wily) old farmer Fred is saying about design, but in the past many stoves were designed with a standard 5" or 6" ( some furnaces up to 8") pipe outlets that exhausted into larger masonry chimneys well before the advent of matching sized stainless chimney.
Is a matching flue to the size of the stove outlet better? Probably it is, but you have 8" which isn't out of the question larger, and putting an extention on to test, is the easiest way to find out if it solves the problem. JMHO. ;)