Stack Temperature

Post Reply
 
drujinin
Member
Posts: 87
Joined: Wed. Dec. 06, 2006 4:00 pm
Location: Elkhorn, Wisconsin
Hand Fed Coal Stove: Hearth-Mate Series 2480
Coal Size/Type: Nut

Post by drujinin » Tue. Nov. 06, 2007 1:27 pm

I have a mid-80's Coal/Wood combo Stove. Someone else has posted about having the same model (slips my mind). The question is after reading tons of posts about 135, 250, 375 degree "F" stack temperatures. What would be "typical" for a temperature to see on a stack for a vintage stove like this? There is no high tech here, I crack the below grate air to allow the fire to burn relying on the natural draft of a 35 foot chimney to draw. My pipe is too hot to touch. If I was to open the air wide open, 3/4 open, half open or even 1/4 open the heat will drive you out of the room. I want to improve my efficiency and reduce my consumption which is 2 five gallon pails a per 24 hours. I am thinking about putting a shell around the stove to put a blower system in it so I can keep the fire turned down and get more heat out of it.
I am borrowing a temp gun from work this work and will know more by next post.
drujinin


 
User avatar
coaledsweat
Site Moderator
Posts: 13766
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Tue. Nov. 06, 2007 1:41 pm

The temperatures can vary widely, even with the same model unit. Sounds like you need a barometric damper if you don't have one, a 35" chimney can pull a serious draft. A handfired unit should stop drafting at about .060, anymore and you are sucking up heat and coal.

 
drujinin
Member
Posts: 87
Joined: Wed. Dec. 06, 2006 4:00 pm
Location: Elkhorn, Wisconsin
Hand Fed Coal Stove: Hearth-Mate Series 2480
Coal Size/Type: Nut

Post by drujinin » Wed. Nov. 07, 2007 11:30 am

0.06"? Are you sure you didn't mean 0.6"
I would have to walk over to the LAB and look at an inclined water manometer but I didn't think they would read down that low.
Anyways I choked it down some more last night to see if the fire would go out and it doesn't so I am running cool enough to touch the pipe for a second or two. I am going to drill some probe holes in it just to get some readings on temp and suction.
Its warm outside today which isn't agreeing with the weather forecast which makes it hard to get good stack draw values.
The only reason I have been hesitant to put a barometric damper on it is because I can't deal with the fact that would suck warm air out of the house. Of course when I am burning wood it should help with that also.
I do suppose the reasoning is suck air through the fire and use more fuel in return for a small degree of warmth or suck out of the warm room an equivalent amount of air in return for a fuel savings.
Is this a correct assumption??
drujinin

 
User avatar
coaledsweat
Site Moderator
Posts: 13766
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Wed. Nov. 07, 2007 11:38 am

drujinin wrote:0.06"? Are you sure you didn't mean 0.6"

The only reason I have been hesitant to put a barometric damper on it is because I can't deal with the fact that would suck warm air out of the house.
Actually, the reading is -.06 as the draft you read is lower than room pressure.

You are saving the 70* air from your room and sacrificing several hundred * air to the chimney and outdoors. GET A BARO.

 
drujinin
Member
Posts: 87
Joined: Wed. Dec. 06, 2006 4:00 pm
Location: Elkhorn, Wisconsin
Hand Fed Coal Stove: Hearth-Mate Series 2480
Coal Size/Type: Nut

Post by drujinin » Wed. Nov. 07, 2007 1:48 pm

OK! :)
I need to upgrade the pipe quality and do an inside chimney inspection anyways.
drujinin

 
Mastiffman
Member
Posts: 36
Joined: Wed. Oct. 11, 2006 9:38 am
Location: Sch. County

Post by Mastiffman » Thu. Nov. 08, 2007 7:29 pm

Where is everybody taking their readings? Right now I have a magnetic Rutland gauge on my Harman Mark II's stack about 12" above the stove, which is 1/2 way to the barometric damper.
It's 32 outside, and my 6" stack goes up maybe 6' before turning then 2' into a, 8X8" brick chimney that is probably about 30' tall.
The stove is burning good, approx. 3/4 full of pea, with 2-3" dancing blue flames over 80% orange coals. Circualting blower is off.

Moving the magnetic guage around, the temps are:
Side of stove near the top - 490
Stack 12" above stove - 280
Stack 12" above barometric damper - 155

The only ballpark numbers I could find online are from Hearth.com's Q&A where they say a coal stove at 450-475 degrees should have a stack temp of 225-250, but where do they take those readings?

I think I'm probably running a little on the hot side, so I'm going to cut the air back 1/4 turn for now.

Any thoughts or suggestions?

Thanks,
Steve

 
User avatar
CoalHeat
Member
Posts: 8862
Joined: Sat. Feb. 10, 2007 9:48 pm
Location: Stillwater, New Jersey
Stoker Coal Boiler: 1959 EFM 350
Hand Fed Coal Stove: Harman Magnafire Mark I
Baseburners & Antiques: Sears Signal Oak 15 & Andes Kitchen Range
Coal Size/Type: Rice and Chestnut
Other Heating: Fisher Fireplace Insert

Post by CoalHeat » Thu. Nov. 08, 2007 9:27 pm

Mastiffman wrote:Where is everybody taking their readings? Right now I have a magnetic Rutland gauge on my Harman Mark II's stack about 12" above the stove, which is 1/2 way to the barometric damper.
It's 32 outside, and my 6" stack goes up maybe 6' before turning then 2' into a, 8X8" brick chimney that is probably about 30' tall.
The stove is burning good, approx. 3/4 full of pea, with 2-3" dancing blue flames over 80% orange coals. Circualting blower is off.

Moving the magnetic guage around, the temps are:
Side of stove near the top - 490
Stack 12" above stove - 280
Stack 12" above barometric damper - 155

The only ballpark numbers I could find online are from Hearth.com's Q&A where they say a coal stove at 450-475 degrees should have a stack temp of 225-250, but where do they take those readings?

I think I'm probably running a little on the hot side, so I'm going to cut the air back 1/4 turn for now.

Any thoughts or suggestions?

Thanks,
Steve
My Harman is currently running at 225 degrees stack temp. The gauge is on the vertical pipe between the outlet and the tee where the baro is. My draft is running at -.06 WC, the chimney is about 30' tall, masonry, on the outside of the house. Draft vent is open 2 turns, stove 3/4 full of pea coal. At 1 turn it runs about 150 degrees. Before I installed the baro the pipe temps were much higher, the paint on pipes would start to smoke and I would get a combustion odor, I think the pipe connections expanded so much that the seams opened up a little.

29 degrees outside now.

Attachments

HARMAN 03-21 #2.JPG

You can just about see the thermometer on the front of the pipe.

.JPG | 100.8KB | HARMAN 03-21 #2.JPG


 
User avatar
stoker-man
Verified Business Rep.
Posts: 2071
Joined: Mon. Nov. 19, 2007 9:33 pm
Location: Lehigh Valley, PA
Hand Fed Coal Boiler: 1981 efm wcb-24 in use 365 days a year
Coal Size/Type: Anthracite/Chestnut
Other Heating: Hearthstone wood stove

Post by stoker-man » Wed. Nov. 21, 2007 9:22 pm

It's recommended to keep the stack temperature at or above 350 degrees to prevent condensation in an uninsulated chimney. My wood/coal boiler using dried wood varies widely in temperature. Even with a hot fire, my stack temperature is around 150 degrees once it settles down. I had a terrible time with creosote last year before I tore out the clay liner and installed a stainless liner wrapped with ceramic fiber and foil.

 
User avatar
europachris
Member
Posts: 1017
Joined: Sat. Dec. 09, 2006 5:54 pm
Location: N. Central Illinois

Post by europachris » Wed. Nov. 21, 2007 9:28 pm

That's the beauty of coal, though! No condensation issues to worry about, and hence - no creosote! We only need enough heat in the exhaust to develop the required draft (or in my case, I have a direct vent stove - no heat needed at all). But yeah, with wood, on a cool fire and long chimney, you can get GALLONS of creosote liquid running out everywhere. Been there, done that. What a smelly mess.

 
User avatar
Cyber36
Member
Posts: 480
Joined: Mon. Oct. 29, 2007 1:53 pm
Location: Byron NY
Hand Fed Coal Stove: Marathon/Logwood

Post by Cyber36 » Thu. Nov. 22, 2007 1:37 pm

So, if coal causes no condensation, is a 350 stack temp. too high??

 
User avatar
LsFarm
Member
Posts: 7383
Joined: Sun. Nov. 20, 2005 8:02 pm
Location: Michigan
Stoker Coal Boiler: Axeman Anderson 260
Hand Fed Coal Boiler: Self-built 'Big Bertha' SS Boiler
Baseburners & Antiques: Keystone 11, Art Garland

Post by LsFarm » Thu. Nov. 22, 2007 2:08 pm

A stack temp of 350* is pretty hot for a coal stove. Around 200-250* is wasting a lot less heat up the flue. If you need to have your fire burning so hot that the flue is above 3-350* , then maybe you should look into trying to get more heat off the stove body with a fan or a better fan. A stack temp of 3-350* is going to have the stove at 500*-600*+ . If some of the stove heat is washed off with a fan, the stack temp will drop, the room temp will rise. and that is what we are looking for, a warm room.

Greg L

 
User avatar
Rex
Member
Posts: 224
Joined: Thu. Apr. 12, 2007 11:25 pm
Location: Indiana

Post by Rex » Fri. Nov. 23, 2007 2:45 pm

Right now my stack temps shows 115 with stove top at 250. Our big pot of chilly sure is enjoying it going into the 5th hour of cooking.

 
User avatar
stoker-man
Verified Business Rep.
Posts: 2071
Joined: Mon. Nov. 19, 2007 9:33 pm
Location: Lehigh Valley, PA
Hand Fed Coal Boiler: 1981 efm wcb-24 in use 365 days a year
Coal Size/Type: Anthracite/Chestnut
Other Heating: Hearthstone wood stove

Post by stoker-man » Sat. Nov. 24, 2007 6:20 am

When I say 350 degrees stack temp, I mean at the breech of the unit.

 
drujinin
Member
Posts: 87
Joined: Wed. Dec. 06, 2006 4:00 pm
Location: Elkhorn, Wisconsin
Hand Fed Coal Stove: Hearth-Mate Series 2480
Coal Size/Type: Nut

Post by drujinin » Tue. Nov. 27, 2007 1:25 pm

I'm sorry for asking but what or where is the breach of the unit?

By the way there is an add on the website or in the wisconsin farmer paper for bagged nut coal in a 920 area code.

 
User avatar
stoker-man
Verified Business Rep.
Posts: 2071
Joined: Mon. Nov. 19, 2007 9:33 pm
Location: Lehigh Valley, PA
Hand Fed Coal Boiler: 1981 efm wcb-24 in use 365 days a year
Coal Size/Type: Anthracite/Chestnut
Other Heating: Hearthstone wood stove

Post by stoker-man » Tue. Nov. 27, 2007 5:29 pm

The breach is where the heat exits the stove or where the flue pipes begin.


Post Reply

Return to “Hand Fired Coal Stoves & Furnaces Using Anthracite”