General Draft Question

Post Reply
 
User avatar
jpete
Member
Posts: 10829
Joined: Thu. Nov. 22, 2007 9:52 am
Location: Warwick, RI
Hand Fed Coal Stove: Harman Mk II
Coal Size/Type: Stove, Nut, Pea
Other Heating: Dino juice

Post by jpete » Sat. Jan. 02, 2010 9:23 pm

Are all solid fuel stoves supposed to run in the .04-.06 range?

A friend of mine has a Fire Chief FC1100 wood/coal furnace and he doesn't seem to be able to run it below "inferno".

I haven't seen the gage, but he claims it's reading "18".

Maybe he means 1.8?

I'm trying to diagnose this through text message so details are sketchy.

 
User avatar
SMITTY
Member
Posts: 12520
Joined: Sun. Dec. 11, 2005 12:43 pm
Location: West-Central Mass
Stoker Coal Boiler: EFM 520 Highboy
Coal Size/Type: Rice / Blaschak anthracite
Other Heating: Oil fired Burnham boiler

Post by SMITTY » Sat. Jan. 02, 2010 9:30 pm

Even .18 is MEGA draft!! :shock:

 
User avatar
jpete
Member
Posts: 10829
Joined: Thu. Nov. 22, 2007 9:52 am
Location: Warwick, RI
Hand Fed Coal Stove: Harman Mk II
Coal Size/Type: Stove, Nut, Pea
Other Heating: Dino juice

Post by jpete » Sat. Jan. 02, 2010 9:45 pm

Problem is, he's burning wood right now and I don't know if the draft reading is the same for coal. I'm trying to get him to just make the switch but he gets wood free from his 4+ acres of land.

 
User avatar
rockwood
Member
Posts: 1381
Joined: Sun. Sep. 21, 2008 7:37 pm
Location: Utah
Hot Air Coal Stoker Furnace: Stokermatic
Hand Fed Coal Stove: Rockwood Stoveworks Circulator
Baseburners & Antiques: Malleable/Monarch Range
Coal Size/Type: Lump and stoker + Blaschak-stove size

Post by rockwood » Sat. Jan. 02, 2010 9:51 pm

Is he using a manual pipe damper? What kind of gauge is he using to measure the draft?


 
User avatar
SMITTY
Member
Posts: 12520
Joined: Sun. Dec. 11, 2005 12:43 pm
Location: West-Central Mass
Stoker Coal Boiler: EFM 520 Highboy
Coal Size/Type: Rice / Blaschak anthracite
Other Heating: Oil fired Burnham boiler

Post by SMITTY » Sat. Jan. 02, 2010 9:51 pm

Ahhhh ... that will make a huge difference. Your looking at about a 500° minimum stack temp difference. Over .10 isn't out of the question with wood.

Coal will be a tough sell with free fuel available ....

 
User avatar
rockwood
Member
Posts: 1381
Joined: Sun. Sep. 21, 2008 7:37 pm
Location: Utah
Hot Air Coal Stoker Furnace: Stokermatic
Hand Fed Coal Stove: Rockwood Stoveworks Circulator
Baseburners & Antiques: Malleable/Monarch Range
Coal Size/Type: Lump and stoker + Blaschak-stove size

Post by rockwood » Sat. Jan. 02, 2010 9:58 pm

The FC1100 furnace has FD (forced draft) fan according to their website. That could be why the draft is so high.

 
User avatar
jpete
Member
Posts: 10829
Joined: Thu. Nov. 22, 2007 9:52 am
Location: Warwick, RI
Hand Fed Coal Stove: Harman Mk II
Coal Size/Type: Stove, Nut, Pea
Other Heating: Dino juice

Post by jpete » Sat. Jan. 02, 2010 10:50 pm

His manometer is the Dwyer Mk II so I knew an "18" seem unreal. But he confirmed it was "1.8"

He is running a manual pipe damper, closed down to about 45* to the pipe. Chimney is at least 25' of flexible stainless inside a masonry chimney that is in the center of the house.

He is not running the forced draft fan.

I told him to try to get it closer to 1 or he was going to clear out his land in one season. :D