disconnect boxes, be it automatic using self starting generators, or manual start is the way to go. Two reasons, no burning up your generator when out line power comes back on. Second reason, you select what circuits you need.
- joethemechanic
- Member
- Posts: 369
- Joined: Sat. May. 23, 2015 12:26 pm
I've repaired a lot of big backup generators, and transfer switches. We used to have the Philadelphia Police, Fire, and Communications contract. Everything from little 2 cylinder natural gas Onans to a 900KW 16v92 Detroit Diesel powered Spectrum at the Roundhouse (Police HQ). All were installed by Local 98 guys working for big electrical contractors.
Sounds like your contractor is a Romex Roper
BTW, when testing that 900KW if you were in the enclosure, it made your teeth itch
Sounds like your contractor is a Romex Roper
BTW, when testing that 900KW if you were in the enclosure, it made your teeth itch
With the proper ATS you will never have any problems. You can wire to specificwilder11354 wrote: ↑Sun. Jan. 19, 2020 2:40 pmdisconnect boxes, be it automatic using self starting generators, or manual start is the way to go. Two reasons, no burning up your generator when out line power comes back on. Second reason, you select what circuits you need.
circuits or the whole box with enough generator power.
Never anything to burn up.
BigBarney
-
- Member
- Posts: 1442
- Joined: Sun. Oct. 14, 2012 7:52 pm
- Location: Mid Coast Maine
- Hand Fed Coal Boiler: New Yoker WC90
- Baseburners & Antiques: Woods and Bishop Antique Pot Bellied Stove
- Coal Size/Type: Stove/Nut/Pea Anthracite
- Other Heating: Munchkin LP Boiler/Englander Pellet Stove/Perkins 4.108 Cogeneration diesel
I just back-feed through my power panel too, and throw the main breaker so it does not go out on the grid.
Someone said that Maine passed a law where doing that is illegal, but who knows? Maine has a law about leaving Christmas lights up after January 15th too, and that is another law they do not enforce.
I do not think it is a huge safety concern with utility workers because by protocol they are supposed to ground the lines where they are working. They are supposed to assume all lines are generator back-fed and thus ground them.
Someone said that Maine passed a law where doing that is illegal, but who knows? Maine has a law about leaving Christmas lights up after January 15th too, and that is another law they do not enforce.
I do not think it is a huge safety concern with utility workers because by protocol they are supposed to ground the lines where they are working. They are supposed to assume all lines are generator back-fed and thus ground them.
- freetown fred
- Member
- Posts: 30300
- Joined: Thu. Dec. 31, 2009 12:33 pm
- Location: Freetown,NY 13803
- Hand Fed Coal Stove: HITZER 50-93
- Coal Size/Type: BLASCHAK Nut
When I was line trampin--(Kohler elec) my crew leader lost both his legs in Fl. when Andrew blew through--cause of people stupidity, assumption & iffiness==just sayin!
-
- New Member
- Posts: 7
- Joined: Wed. Jan. 22, 2014 1:31 pm
- Location: Central Pa
- Hand Fed Coal Stove: Not yet, looking
I know this post has been up for a while but I thought I would weigh in. I used to back feed through the panel also but their was no way I wanted my wife messing with it and I did not want to inadvertently hurt a lineman doing repair work.
I had my electrician install a small transfer switch a few months ago. I wanted something simple and inexpensive my wife could operate in case of power going out while I was away. I have a small propane powered 3500 watt generac portable generator which will handle a few of the critical circuits in the house. Heat, refrigerator, freezer, a few lights and computer.
Installation took about an hour, its safe and it was installed to code.
Transfer switch will handle 6 circuits and includes two, watt meters (one for each 110 volt leg.)
The transfer switch is fed from an outdoor weather resistant 220 v plug.
When power goes out I start up the generator and using the 220 outlet on the generator I plug into outside receptacle. Then going inside I switch each circuit from LINE to GEN that I need to power up.
When power comes back on it does not effect the circuits being powered by the generator, I manually switch them from GEN to LINE (It is impossible to back feed the line from my transfer switch)
Then I switch off the generator and put it away.
System works great. Transfer switch (protran brand) and dedicated heavy duty extension cord cost about $300 install wasn't much.
I had my electrician install a small transfer switch a few months ago. I wanted something simple and inexpensive my wife could operate in case of power going out while I was away. I have a small propane powered 3500 watt generac portable generator which will handle a few of the critical circuits in the house. Heat, refrigerator, freezer, a few lights and computer.
Installation took about an hour, its safe and it was installed to code.
Transfer switch will handle 6 circuits and includes two, watt meters (one for each 110 volt leg.)
The transfer switch is fed from an outdoor weather resistant 220 v plug.
When power goes out I start up the generator and using the 220 outlet on the generator I plug into outside receptacle. Then going inside I switch each circuit from LINE to GEN that I need to power up.
When power comes back on it does not effect the circuits being powered by the generator, I manually switch them from GEN to LINE (It is impossible to back feed the line from my transfer switch)
Then I switch off the generator and put it away.
System works great. Transfer switch (protran brand) and dedicated heavy duty extension cord cost about $300 install wasn't much.
Attachments
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
Nice!!!...
- joethemechanic
- Member
- Posts: 369
- Joined: Sat. May. 23, 2015 12:26 pm
I was at a municipal auction a few years back and bid 10 bucks on a big pile of old breaker panels and boxes on a pallet. There was a 100 amp single phase transfer switch on the bottom that was new. Some scratches but never installed. I have 3 phase here but there is a single phase panel for the office, my apartment, the heat, and some minimal lighting in the shop. I run everything on an older Kohler 4 cylinder 1800RPM 7.5 KW generator. Flathead engine, magneto ignition, all simple reliable manual stuff. The only thing I'd like to change is from gasoline to propane. Propane lasts forever in storage
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
I have 2 of the Vintage Kohler 10kW gen-sets with 4 cylinder @1800 rpm Waukesha engine w/ magneto plus they're already set up for propane...they didn't even bother to remove the gasoline carb...just mount a big adjustable brass jet into the elbow between the air cleaner and the choke side of carb and govenor works carb thottle the same. The motor oil never even gets dark...no fuel stabilizer ever...The starter is built into the generator rotor...24 volt battery spins whole generator and the propain lights right up quick...
Dang dem old boys were smart!!!
Dang dem old boys were smart!!!
-
- Member
- Posts: 1442
- Joined: Sun. Oct. 14, 2012 7:52 pm
- Location: Mid Coast Maine
- Hand Fed Coal Boiler: New Yoker WC90
- Baseburners & Antiques: Woods and Bishop Antique Pot Bellied Stove
- Coal Size/Type: Stove/Nut/Pea Anthracite
- Other Heating: Munchkin LP Boiler/Englander Pellet Stove/Perkins 4.108 Cogeneration diesel
I got one of those as well! Mine is a little different in that it is a 12 volt start. Can yours change from single to 3 phase power too?McGiever wrote: ↑Tue. Feb. 18, 2020 2:30 amI have 2 of the Vintage Kohler 10kW gen-sets with 4 cylinder @1800 rpm Waukesha engine w/ magneto plus they're already set up for propane...they didn't even bother to remove the gasoline carb...just mount a big adjustable brass jet into the elbow between the air cleaner and the choke side of carb and govenor works carb thottle the same. The motor oil never even gets dark...no fuel stabilizer ever...The starter is built into the generator rotor...24 volt battery spins whole generator and the propain lights right up quick...
Dang dem old boys were smart!!!
Attachments
-
- Member
- Posts: 1442
- Joined: Sun. Oct. 14, 2012 7:52 pm
- Location: Mid Coast Maine
- Hand Fed Coal Boiler: New Yoker WC90
- Baseburners & Antiques: Woods and Bishop Antique Pot Bellied Stove
- Coal Size/Type: Stove/Nut/Pea Anthracite
- Other Heating: Munchkin LP Boiler/Englander Pellet Stove/Perkins 4.108 Cogeneration diesel
If the breaker panels had breaks in them, then that would have been a nice score unto its own. We got old breaker boxes here, but they no longer make breakers to fit inside them, so it means adding a circuit can get expensive and complicated fast. Just having an old breaker that fits would save a lot of work.joethemechanic wrote: ↑Mon. Feb. 17, 2020 11:49 pmI was at a municipal auction a few years back and bid 10 bucks on a big pile of old breaker panels and boxes on a pallet. There was a 100 amp single phase transfer switch on the bottom that was new. Some scratches but never installed. I have 3 phase here but there is a single phase panel for the office, my apartment, the heat, and some minimal lighting in the shop. I run everything on an older Kohler 4 cylinder 1800RPM 7.5 KW generator. Flathead engine, magneto ignition, all simple reliable manual stuff. The only thing I'd like to change is from gasoline to propane. Propane lasts forever in storage
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
- franpipeman
- Member
- Posts: 692
- Joined: Fri. Jan. 11, 2008 4:27 pm
- Location: Wernersville pa
- Stoker Coal Boiler: efm 520 stoker fitzgibbons pressure vessel
- Hand Fed Coal Stove: harman, russo
- Coal Size/Type: rice
- Other Heating: alpine propane condensing boiler radiant floor
Here is my generator story not mine at my house but at a public school i was working at. We were working on a renovation at the school and they had a generator but old and small. A power failure occurred the generator tried to start but just cranked for 15 seconds never started, the grid power returned, generator stopped trying then tried dropped out again after 10 seconds the old generator tried to start again it didnt . The power returned and shut off again and the generators battery eventually failed...... no grid power , no generator power . I guess they didnt exercise their system, i think it was natural gas fuel but obvious no exercise this was 1979 no digital solid sate controller for automatic exercise .
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
Thanks for sharing Fran, you reminded me that I need to replace my 2 batteries for my 24 volt starter on my old generator. Got it while working renovations at a public school in 1999.
Replaced those included battries in 2007 and now they're due again. It is a vintage tri-fuel Kohler genset, I run it off 2-100 gallon propane tanks, and it serves me well .
Replaced those included battries in 2007 and now they're due again. It is a vintage tri-fuel Kohler genset, I run it off 2-100 gallon propane tanks, and it serves me well .